simpler=better
Well-known member
You guys want to double check my work? This is for the 2nd floor & attic in an old farmhouse. First floor is going to be mini splits. Current system looks like it was designed & installed by drunk raccoons.
The house has no real insulation, single pane windows, balloon framed, etc. Yes I need to fix that stuff, but right now I want to get the ducts sorted.
J-calculation says 30kBTU cooling, the current 3ton unit should be adequate.
Air handler is rated at 1,400cfm unrestricted.
The rooms are 10x10x8=800 cubic feet. 800cuft*10 air changes=8,000/60mins= 133CFM per room.
The attic is 20x20x8 (vaulted ceiling)=2,000cuft*6 air changes=12,000/60mins=200CFM to the attic.
So that's 1,000CFM total-the handler can do that.
To keep the velocity under 500fpm for noise, duct drag calculator gave me a minimum duct diameter of 6.6". I rounded that up to 8".
I'll be replacing the 20x20x1 pleated filter with a Honeywell F100 20x25x4 media filter.
To get air back into the attic, I'm planning on cutting straight down through the floor to put in a 20" grate. The air handler will pull from the top of the room. This is the 20" round hole near the center of the drawing.
These are the rough plans:
I plan on running spiral duct and insulating to R8. The rectangular bends will have vanes in them. All drops will get dampers.
I'll be getting all my parts from Phoenix Metals
Do you guys think my ducts are too big:?
The house has no real insulation, single pane windows, balloon framed, etc. Yes I need to fix that stuff, but right now I want to get the ducts sorted.
J-calculation says 30kBTU cooling, the current 3ton unit should be adequate.
Air handler is rated at 1,400cfm unrestricted.
The rooms are 10x10x8=800 cubic feet. 800cuft*10 air changes=8,000/60mins= 133CFM per room.
The attic is 20x20x8 (vaulted ceiling)=2,000cuft*6 air changes=12,000/60mins=200CFM to the attic.
So that's 1,000CFM total-the handler can do that.
To keep the velocity under 500fpm for noise, duct drag calculator gave me a minimum duct diameter of 6.6". I rounded that up to 8".
I'll be replacing the 20x20x1 pleated filter with a Honeywell F100 20x25x4 media filter.
To get air back into the attic, I'm planning on cutting straight down through the floor to put in a 20" grate. The air handler will pull from the top of the room. This is the 20" round hole near the center of the drawing.
These are the rough plans:
I plan on running spiral duct and insulating to R8. The rectangular bends will have vanes in them. All drops will get dampers.
I'll be getting all my parts from Phoenix Metals
Do you guys think my ducts are too big:?