You've got a short somewhere, either in a wire or a component.
Go to the condensing unit, open the side panel (disconnect off), and pull one of the wires on the contactor off. Replace the fuse in the furnace, turn the AC on again. If it blows, that's a short in the wiring. If it doesn't blow, ohm out the coil on the contactor. If it's less the say 5 ohms, it's bad. Replace it. The newer Chines made components **** at QC.
If the short's in the wiring it'll be a bit more involved to find