Hoping someone here might have some insight before I have to call a service company to look.
Bryant gas furnace, circa 1988. Has worked well until yesterday, when the blower started to run continuously. The heat cycle will otherwise work like normal, except the blower does not stop after its normal few minutes after the end of running the burners. If I power down the furnace and start back up the blower starts immediately.
The thermostat has the fan set to auto, not continuous. The blower will even still run with the thermostat disconnected, so I do not think the thermostat is the issue.
I checked the limit switches in the furnace. Both had very low voltage drop across their contacts, and measured ~20ohm. When I jumpered the limit switches on the circuit board, same behavior, blower kept running. Interestingly, when I disconnected the limit switches from the circuit board also the same behavior, blower kept running.
My thinking now is the relay that runs the fan is stuck. I gave it a few light taps but nothing changed. If I power down the furnace and start it back up, I do not see any movement in the relay (it has a transparent housing).
Am I on the right track, or is there anything else to check?
Thanks!
Bryant gas furnace, circa 1988. Has worked well until yesterday, when the blower started to run continuously. The heat cycle will otherwise work like normal, except the blower does not stop after its normal few minutes after the end of running the burners. If I power down the furnace and start back up the blower starts immediately.
The thermostat has the fan set to auto, not continuous. The blower will even still run with the thermostat disconnected, so I do not think the thermostat is the issue.
I checked the limit switches in the furnace. Both had very low voltage drop across their contacts, and measured ~20ohm. When I jumpered the limit switches on the circuit board, same behavior, blower kept running. Interestingly, when I disconnected the limit switches from the circuit board also the same behavior, blower kept running.
My thinking now is the relay that runs the fan is stuck. I gave it a few light taps but nothing changed. If I power down the furnace and start it back up, I do not see any movement in the relay (it has a transparent housing).
Am I on the right track, or is there anything else to check?
Thanks!