The "ductwork fix" is only within the rated operating range (TESP and CFM) of the motor. In order to keep the amp draw down, the TESP has to be around 0.5" water column and certainly no more than 0.8" wc. That requires that the system (equipment/blower, coil, filter and ductwork) needs to be chosen properly. Bad ductwork can also mean fittings that have bad airflow characteristics, even though the physical size may be OK.One interesting thing about the VS stuff is in some situations it will "fix" bad ductwork .... not leaking and wacky stuff with flex all over the place. But -- there are many houses with undersize ductwork. Modern VS equipment can be zoned very easy ... and by doing so you can often change the main runs in the basement and zone off areas of a house.
You just have to make sure that the smallest zone has a CFM about 25% above the lowest CFM of the equipment. Carriers infinity zoning system is really slick ... it goes through a test of each zone and knows the CFM/ static pressure of the run. When you fire it up it knows what each zone needs and where it has that zones damper. So a hot/ cold second floor can be easily fixed .... same with a great room.
The Carrier equipment you describe is top shelf. The percentage of customers that will choose that level is small, then there is the additional work.
Not so sure on fixing a hot/cold floor or area without some diagnostics first. I certainly wouldn't promise it.
Ductwork problems could be easily fixed if the stuff was installed right in the first place...