Thanks Rick, you made me call Goodman.
You got me thinking, is it possible Ive been wrong about something so basic for sooooo long? The answer was no. But you are not wrong either. I have a lot of GMP furnaces in the area I work on, so I know there is only one fan relay on the board. It is energized by G or Y. So the fan cannot be brought on manually with "fan on" if the relay fails. Goodman confirmed this. This is not the case with a lot of furnaces, particularly newer stuff. G and Y each have there own relay so you can choose a speed for just fan on. In that case if the fan cooling relay fails, switching the fan switch to fan on will bring the fan on. But not if "Y" is also energized. In that case the cooling relay overrides the fan relay, and if the cooling relay is bad.....No fan.
You got me thinking, is it possible Ive been wrong about something so basic for sooooo long? The answer was no. But you are not wrong either. I have a lot of GMP furnaces in the area I work on, so I know there is only one fan relay on the board. It is energized by G or Y. So the fan cannot be brought on manually with "fan on" if the relay fails. Goodman confirmed this. This is not the case with a lot of furnaces, particularly newer stuff. G and Y each have there own relay so you can choose a speed for just fan on. In that case if the fan cooling relay fails, switching the fan switch to fan on will bring the fan on. But not if "Y" is also energized. In that case the cooling relay overrides the fan relay, and if the cooling relay is bad.....No fan.