Idea's for connection to house?

leeklm

Well-known member
Joined
Jul 15, 2011
Messages
72
Location
Minneapolis
Garage is about done with the 100amp service install, now getting ready to run the lines into the house. May be a little fun as there is not much room to work above the panel where the service lines come in. My 200amp house panel is plenty busy with lines!

Question... I am running three lines w/3ga and a 6ga gw. through 1.5" pvc up to the house. Is conduit typically needed once you are inside the wall ? (it is about 12-18" from entrance to the panel.)

If yes, what is the recommended type, and smallest conduit I could get by with for these 4 wires?

Thanks!
 
To avoid these ads, REGISTER NOW!

Stuart in MN

Well-known member
Joined
Sep 8, 2005
Messages
23,112
Location
Minneapolis
Individual wires need to be in a conduit or some type of approved raceway. I don't have my cheat sheets handy but I believe you can get by with 1 1/4" conduit for three #3 and one #6 THHN/THWN wires.
 