Ignition failure lockout

bluedog225

Well-known member
Joined
Jan 31, 2012
Messages
3,276
Location
Texas
I was in the attic anyway, and I turned off my gas line because winter is over.

Turns out it’s getting a little chilly. I tried to turn the heater back on and it didn’t work. I crawl back up in the attic and realize my mistake and turn the gas back on.

Still doesn’t work. Opened it up and saw the code “ignition failure lockout”. The plate says it’s a three hour lockout. That’s fine.

I was curious if I shut the power and turn it back on will that reset the lockout? Future reference mostly. Thanks.
 
To avoid these ads, REGISTER NOW!

Walkers

Well-known member
Joined
May 17, 2021
Messages
3,912
Location
Cave Creek Az
I was in the attic anyway, and I turned off my gas line because winter is over.

Turns out it’s getting a little chilly. I tried to turn the heater back on and it didn’t work. I crawl back up in the attic and realize my mistake and turn the gas back on.

Still doesn’t work. Opened it up and saw the code “ignition failure lockout”. The plate says it’s a three hour lockout. That’s fine.

I was curious if I shut the power and turn it back on will that reset the lockout? Future reference mostly. Thanks.
It should reset and retry immediately.
 
OP
B

bluedog225

Well-known member
Joined
Jan 31, 2012
Messages
3,276
Location
Texas
Great. Thanks. I’ve been here since 1991 and haven’t quite gotten around to labeling the breakers…..
 

ramchill

Member
Joined
Nov 27, 2022
Messages
7
I was in the attic anyway, and I turned off my gas line because winter is over.

Turns out it’s getting a little chilly. I tried to turn the heater back on and it didn’t work. I crawl back up in the attic and realize my mistake and turn the gas back on.

Still doesn’t work. Opened it up and saw the code “ignition failure lockout”. The plate says it’s a three hour lockout. That’s fine.

I was curious if I shut the power and turn it back on will that reset the lockout? Future reference mostly. Thanks.
There will be a cutout right next to the furnace. You don't have to go looking for the breaker.
 
To avoid these ads, REGISTER NOW!

ramchill

Member
Joined
Nov 27, 2022
Messages
7
There is a well document startup sequence for a furnace. Once you get familiar with you, you can watch it go through the sequence and spot where it fails. Starts with the inducer motor.. And the final one is once the furnace starts up give it another couple minutes to ensure that the flame sensor tells the controller that all is good.
 

fitter30

Well-known member
Joined
Jun 23, 2019
Messages
2,968
Location
Peace Valley,mo
If you have a hot surface igniter ( has two 14 gauge wires ) needs to be replaced even if it lights the burner burner control is looking for a certain amps. Remove it take it to appliance parts house.
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
22,598
Location
VT
There is a well document startup sequence for a furnace. Once you get familiar with you, you can watch it go through the sequence and spot where it fails. Starts with the inducer motor.. And the final one is once the furnace starts up give it another couple minutes to ensure that the flame sensor tells the controller that all is good.
I'm guessing part of the startup sequence either directly or indirectly checks for gas flow....

With the gas line OFF it would never ignite and should lock out.
 