I found in my box of salvaged junk an indicator light that looks to mount in place of a standard switch. It is marked 220-270V and has two wire connections on it. If I jump the two connections to 240V power it lights up, it also lights up if I put one connection on 120V and one to neutral. I would like to install this next to the exit door of my shop so I will have a visual clue that I have left my compressor on. The compressor is in another part of the shop and wired through a wall mount fused disconnect. My thoughts are to run a single wire (of the same gauge?) off one leg of the 240V after the fuse to the light, and connect the other side of the light to a neutral leg located near where the light would be. Is this a no-no? Would it be better to run two wires? Do they have to be the same gauge as the equipment on the circuit? - The circuit is as follows: 30 amp two pole breaker --> 10 gauge wire --> fused knife switch/disconnect ---> 15 amp fuses ---> 12 gauge wire ---> 2 hp motor. If I wire the lights in after the fuses as it is now I should be fine with a lighter gauge wire - but... should I ever upgrade the compressor and use larger fuses in the disconnect will I need larger wire for the light?

Long winded I know. :bounce: Thanks in advance.
 
To avoid these ads, REGISTER NOW!

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
first, you cannot take a hot off the disco and the neutral from somewhere else. All conductors of the circuit must be in the same cable or conduit.

The wire running to the light must be protected at its rated ampacity. This is easily solved by fusing down to 15 amps and running #14 over to the light.

That said, what I would do is get ahold of a small 240vac to 24vac control transformer (cheap on ebay) and then run a piece of doorbell wire from that to a 24v indicator light. Heres a picture of some I have, these are 22mm control panel indicator lights, they have LEDs inside behind the lens.

attachment.php
 

Attachments

  • ind-bl-rd-on.jpg
    ind-bl-rd-on.jpg
    30 KB · Views: 471

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
how far away from compressor are you putting that light? you might just want to use a 120v light. (same light I posted comes in 120v also)
 

1Garageman

Well-known member
Joined
May 12, 2009
Messages
4,417
Location
Columbus, Ohio
I was just thinking of putting it within 5 ft or so of it. I am going to box in the compress eventually to cut down on the damn noise it makes and that would be nice. Out side switch for on and off and a light with it.
 
OP
P

Possum

Well-known member
Joined
Dec 10, 2008
Messages
302
Location
KS
Thanks for the response mrb. I would like to just utilize the switch I already have since fits in a standard electrical box and the light fits through a cover plate made for the switch. The wire run from the compressor would be about 40' one way. I will just run two wires to it, probably 10 gauge in case I upgrade the compressor - like the Saylor Beall 705 I found today - and need to use larger fuses requiring larger wires to the light correct?
 

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
Thanks for the response mrb. I would like to just utilize the switch I already have since fits in a standard electrical box and the light fits through a cover plate made for the switch. The wire run from the compressor would be about 40' one way. I will just run two wires to it, probably 10 gauge in case I upgrade the compressor - like the Saylor Beall 705 I found today - and need to use larger fuses requiring larger wires to the light correct?

ok. seemed like it would be better to use a $8 transformer and a $3 light plus some cat5, phone wire, doorbell wire, or whatever than to install a 40ft run of #10 to use a light you already have....
 
OP
P

Possum

Well-known member
Joined
Dec 10, 2008
Messages
302
Location
KS
That is cheap. What would I need to operate the compressor at the door location with a setup like that?
 
To avoid these ads, REGISTER NOW!

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
operate the compressor? as in turn it on an off?
 

scuba0459

Well-known member
Joined
Mar 27, 2010
Messages
114
Location
The Fundy shore off Nova Scotia
You would need a starter contactor. I have my compressor hooked up to such a circuit. Mine has a 24V remote switch and if I ran a third wire I would also have a light. My compressor is in my other garage and I can remotely turn it on from my workshop.
 

Underdog

Well-known member
Joined
Sep 24, 2007
Messages
1,135
Location
Treasure Coast, Florida
I tried to wire in a indicator light (115V) on my compressor (230V single phase w/starter, 230V coil. Wired as I thought it should work but it made the coil buzz from back feed thru the light bulb.???:headscrat
 

gmhill33

Well-known member
Joined
Oct 5, 2009
Messages
539
Location
Ohio
I hooked up a regular light to a double pole 230v switch so that I would know that I left the air compressor turned on.

Gary
 

2LTim

Well-known member
Joined
Nov 9, 2008
Messages
143
Location
Central Iowa
You could do as I have done in my shop, control a contactor with the lighting circuit switch. If you can remember to turn off the lights, you never have to wonder if you left the air on.
 