Indoor unit piping direction

aone

Active member
Joined
May 21, 2014
Messages
35
Location
Queens
Fujitsu ASU9RLS2

For this unit can the piping go up to run in a drop ceiling? The drain hose will go out.

The unit will be mounted four inches below the drop ceiling. The piping (except the drain hose) will go up the wall into the ceiling then run to back of the house in the drop ceiling. The manual says horizontal and down only. I remember different. I attached a snippet of the manual. Any thoughts?
 

Attachments

  • indoor piping.pdf
    35.3 KB · Views: 18
Last edited:
To avoid these ads, REGISTER NOW!

justinjoyal

Well-known member
Joined
Apr 30, 2015
Messages
888
Location
Quebec
You can go up once you're past the unit.

What the manual does is show possible exit locations using factory "pre-cut" holes.
 
OP
A

aone

Active member
Joined
May 21, 2014
Messages
35
Location
Queens
Thank you for clearing that up. I am glad I can now get the piping run up in the ceiling. It will be easier and neater. Thank again.
 
To avoid these ads, REGISTER NOW!

acmikee

Well-known member
Joined
Feb 2, 2005
Messages
301
Location
olympia, wa
they make a small condensate pump that fits inside the unit so you can run the condensate with the refrigerant piping.
 

justinjoyal

Well-known member
Joined
Apr 30, 2015
Messages
888
Location
Quebec
^^ Not a fan of those... One more thing that can break and if it does it makes a nice mess...
 
OP
A

aone

Active member
Joined
May 21, 2014
Messages
35
Location
Queens
If it comes to it, I now know that option is available. Mess indeed to let you know it failed.
 