Firebrick43
Well-known member
So the other night at work they had an a chiller that cools on open glycol tank that cools a 1.5KW laser. There is a glycol loop from an outside water evaporator tower that runs through a plate type heat exchanger (condenser) and then the glycol tank/loop to the laser runs through another heat exchanger(evaporator) Excellent flows on both loops. It is a 20 ton compressor, R407C gas and TXV valve system and it was throwing low pressure faults on the proprietary PID controller. Checked most everything elese first, nothing else was malfunctioning. Any way I was charging it by sub cooling, only had about 1 degree as found. It stopped faulting almost immediately as I added freon.. It was a german machine, with a german manual, that as best as my google translation could surmise, If any faults, problems, or even a fart, call the manufacture.
Any who, for the actual question. This system had a 6mm pressure line coming off the directly after the output of the compressor and down through a solenoid valve(controlled) by the PID and dumped between the TXV and the heat exchanger the heat exchanger (evaporator). It had an odd capped off ball valve to regulate flow. If I pulled the DIN connector off the solinoid (Normally Closed) I actually had cooling(before adding a charge) but with it open it added enough heat to cancel out any cooling, hence the 1 degree of sub cooling.
Having no specs I was going to originally shoot for 10 degrees of sub cooling, and things were cooling real well even with that solenoid valve open at about 8.5 degrees but when that valve would close(for what ever reason????) it would jump up to 15 degrees of sub cooling for 30 seconds or so before settling down.
What is the purpose of adding hot freon out of the pump to after the TXV Valve???? Would you take the measurement while it was open(most of the time) or closed?
Thank you
Any who, for the actual question. This system had a 6mm pressure line coming off the directly after the output of the compressor and down through a solenoid valve(controlled) by the PID and dumped between the TXV and the heat exchanger the heat exchanger (evaporator). It had an odd capped off ball valve to regulate flow. If I pulled the DIN connector off the solinoid (Normally Closed) I actually had cooling(before adding a charge) but with it open it added enough heat to cancel out any cooling, hence the 1 degree of sub cooling.
Having no specs I was going to originally shoot for 10 degrees of sub cooling, and things were cooling real well even with that solenoid valve open at about 8.5 degrees but when that valve would close(for what ever reason????) it would jump up to 15 degrees of sub cooling for 30 seconds or so before settling down.
What is the purpose of adding hot freon out of the pump to after the TXV Valve???? Would you take the measurement while it was open(most of the time) or closed?
Thank you