ketas47
Well-known member
Just started my system Thurs. for my 26x38x10 fully insulated garage.Use a lochinvar copper fin non-condensing, 84% eff. boiler.(45000btu).Use a ball valve to recirculate water to boiler. I have a heat exchanger(fan off) before water goes to floor to lower my water temp.(drops about 30 degrees). Also can shut-off water going into floor and just run through heat exchanger and turn fan on to warm up garage quickly if needed. I leave pump on all the time to get all the heat into floor(was told it cost about $20 to run pump for the season).When boiler starts up water is approx. 60*, as boiler water temp comes up return water is approx. 20*-30* cooler. Takes about 8-10 min. to get return water to 125-135* range.Then boiler settles out to about 150-160* going out to 135-145*return. Runs for about 10 min more before room thermostat shuts down boiler(Total 16-23 min cycle).(Water going into floor starts @ 60* and goes as high as 120*by the time boiler stops.) Boiler runs every 2-4 hours depending on outside temp.I know the return temp should probably come up quicker so I dont possible harm boiler but during the warm up time the boiler is running most eff.( paid $200 for boiler) When and if boiler fails I plan on buying condensing boiler. This was fairly cheap route! Comments are appreciated. THANKS P.S. Live in central Wi.