To avoid these ads, REGISTER NOW!

Insane prices for additional concrete

globalmax

Well-known member
Joined
Jun 17, 2023
Messages
57
Location
Greensboro, NC
I had a thread a while back to prep the garage floor for a two post lift. Thanks for everyone's input.


General consensus was to go from 4" to 6" thick concrete floor for the entire 25x 30 garage. Additional 2 inches which will be 4.63 yards of concrete.
I was thinking that approximate $150 or so per cubic yard for concreate which could be a total of approximate $600 to $700 maximum.

Garage is part of the overall home build considering 4" concrete garage floors. The quote I got for additional 2 inches of concrete is $2500 !!!. Does additional 2" of concreate involve so much additional labor, what am I missing? Guess he is mixing gold hence this price :mad:
 
To avoid these ads, REGISTER NOW!

luvtheheat

Well-known member
Joined
Jan 28, 2017
Messages
489
Location
Tucson AZ
I recently built a 24' X 44' detached garage. Garage door was to be 8' high. Got concrete floor work estimated at that. 4" pour. Changed my mind and went with 10' garage door.

That change forced a change in the rebar work (to what they called an "engineered footer") and a 5" pour, and slab work alone went up by probably $10-12K. The brickwork also increased sharply, which is easier to understand as walls height went up 25%.
 

The Cobbler

Super Moderator
Staff member
Joined
Oct 24, 2013
Messages
25,802
Location
Niagara Region, Ontario, Canada
If it takes 2 trucks for the total pour the second truck would be a short load and that gets expensive
not here, maybe a regional thing. if we need 1 meter over a truck load, the second truck has no under load if you order it at the same time. but if you end up short on your calculations and need another meter without asking for plus, you're going to pay an under load .
if you're close to a full truck and order 9meters plus , you can order more with no underload... but the you're going to wait for the next load & that's not good maybe
 

Rusted Nut

Well-known member
Joined
Dec 11, 2022
Messages
1,800
Location
PNW
No short load on a second truck here the PNW. If no other work required (forming, grading, etc..), then cost should really only about $300 for concrete. No real added labor for pouring 6” vs. 4”.
 

C-S-H

Well-known member
Joined
Jan 18, 2024
Messages
144
A 6" slab is pitifully thin for use under your 2-post lift, and overkill for the rest of the slab for light vehicle loads. Why not just thicken the slab where it needs the strength? This practice is commonplace in civil construction. Reinforce the thickened portion of the slab correctly using the 2-post lift manufacturers' literature for guidance.
 

bb29510

Well-known member
Joined
Dec 27, 2022
Messages
1,216
four all you need and required for most lifts, get a four post and dont worry about it
 

pcmeiners

Well-known member
Joined
Aug 13, 2009
Messages
7,825
Location
In the only town in Pennsylvania, Bloomsburg.
"Does additional 2" of concrete involve so much additional labor, what am I missing?"

Your not missing anything. But the contractor would be missing a chance at making a nice bit of profit on 2" of concrete.
As is the slab will need 9.2 yards at 4", that is with NO spare/waste concrete, so he really needs 10 yards, a second truck anyway. $1300 at most,considering an extra hour for the pour, and a smaller profit; $2500 if he is mixing some gold leaf sprinkles so that you concrete has tiny sparkles with the lights on.

Then again your into the season where contractors are booked solid, so highway robbery is legal.
 
OP
G

globalmax

Well-known member
Joined
Jun 17, 2023
Messages
57
Location
Greensboro, NC
Not too sure about additional truck for this extra 2 inches is driving up the cost.
To give some more context, contractor is building the whole house and I am sure he is not bringing the truck for putting concrete on just garage only. Agree that I just can't consider the cost for 4.63 cubic yard of concrete and everyone needs mark up.... but this is something I don't understand
 

BombShelter

Well-known member
Joined
Nov 16, 2015
Messages
541
Location
State of Hockey
I haven't sold concrete flatwork for over 10 years but back when I quoted it the boss just wanted me to go a little over the yard pricing for the extra thickness. We typically went 5" on anything with vehicles and 4" on sidewalks.
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
22,186
Location
VT
Not too sure about additional truck for this extra 2 inches is driving up the cost.
To give some more context, contractor is building the whole house and I am sure he is not bringing the truck for putting concrete on just garage only. Agree that I just can't consider the cost for 4.63 cubic yard of concrete and everyone needs mark up.... but this is something I don't understand
He sure as hell isn't bringing in the truck for footings, walls and slabs on the same day.

He's probably breaking up the pours into footings, walls and slabs, possibly separating out the garage due to size and finishing.

Maybe ask him why it's so much?
 
OP
G

globalmax

Well-known member
Joined
Jun 17, 2023
Messages
57
Location
Greensboro, NC
Purely from concrete cost standpoint for 4.63 cubic yards ( say $150 per cubic yard) and whatever additional labor involved to pour down this 2 additional inches, don't think it should be more than $1K even with some mark ups?
 

Chaznsc

Well-known member
Joined
Apr 9, 2013
Messages
6,526
Location
SC
I had a thread a while back to prep the garage floor for a two post lift. Thanks for everyone's input.


General consensus was to go from 4" to 6" thick concrete floor for the entire 25x 30 garage. Additional 2 inches which will be 4.63 yards of concrete.
I was thinking that approximate $150 or so per cubic yard for concreate which could be a total of approximate $600 to $700 maximum.

Garage is part of the overall home build considering 4" concrete garage floors. The quote I got for additional 2 inches of concrete is $2500 !!!. Does additional 2" of concreate involve so much additional labor, what am I missing? Guess he is mixing gold hence this price :mad:
It’s excessive. I’d just talk with the guy.
 
To avoid these ads, REGISTER NOW!

Beemer

Well-known member
Joined
Jun 21, 2020
Messages
1,388
Location
Northeast
Over forty years in building construction design industry and if there is one set thing learned is that once the contract is signed "additions" to the job are priced like gold.
Most contractors I saw on jobs in the last ten years go in with a low price to get in the door but more than make it up in the coarse of the job. Pricing gets ridiculous.
You might ask for justification of the requote but that might not get you far.
You might look into an independent contractor to come in for the slab but guaranteed you'd get a very small credit for taking the slab out of the original contractors scope. That's how the game is played!
 

ItsNemo

Well-known member
Joined
Mar 5, 2016
Messages
4,805
Location
Canada
A 6" slab is pitifully thin for use under your 2-post lift, and overkill for the rest of the slab for light vehicle loads. Why not just thicken the slab where it needs the strength? This practice is commonplace in civil construction. Reinforce the thickened portion of the slab correctly using the 2-post lift manufacturers' literature for guidance.

6" is PLENTY for under a 2 post lift, it's more than most manufacturers ask for in fact.
 

Sumboodie

Well-known member
Joined
Mar 20, 2021
Messages
10,647
Location
AK
Wow,
Around here an easy estimate for flatwork is 2x $/cuyd
That's cheap!

I've gotten quotes for a 30x30 in the 16-18k area.
Concrete is around $160/yard.

That would be around $2600 and 5100 labor. Maybe another $1500 in rebar, forms, etc, that's barely over 9k.
 

C-S-H

Well-known member
Joined
Jan 18, 2024
Messages
144
6" is PLENTY for under a 2 post lift, it's more than most manufacturers ask for in fact.
No it is not plenty. The manufacturers allow the thinner pre-existing slabs only if reinforced with a highly unprobable amount of reinforcement. So the retrofit slab design is required in every case for 2-post lifts. Having run the design computations on 2-post lifts myself, there is no way the thickened areas of the slab are going to be less than about 8" or 9". Manufacturers require 12".
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
22,186
Location
VT
No it is not plenty. The manufacturers allow the thinner pre-existing slabs only if reinforced with a highly unprobable amount of reinforcement. So the retrofit slab design is required in every case for 2-post lifts. Having run the design computations on 2-post lifts myself, there is no way the thickened areas of the slab are going to be less than about 8" or 9". Manufacturers require 12".

Source?
 

bb29510

Well-known member
Joined
Dec 27, 2022
Messages
1,216
even with the extra, labor is really minimumal because finisher onlt deal with the top 1/4 inch
 

Dig Doug

Well-known member
Joined
Apr 16, 2018
Messages
1,078
Adding 2 inches to your slab thickness seems fairly easy & simple

but
depending on build conditions & build plans there could be extra hidden costs that are not visible at 1st -
like grading, & sub grade moving handling materials, extra labor for placing and finishing and possibly pumping, could also be a sub contractor ….

Talk to your builder to see what’s all involved

Keep in mind you’ll have a few of these “ extras/ changes “ during the build process
sometimes you can get a credit back and most times cost a little extra
a give and take so to say



Important part is to maintain a good relationship with the contractor as the slab is in the beginning of the project and there will be a long road until completion
 

Dig Doug

Well-known member
Joined
Apr 16, 2018
Messages
1,078
Another option would be to go 5 inch Slab

If 6 inch is $2500
would the cost only be $1250 up charge for 50% less concrete than the 6inch slab…..


hmmmm
 

C-S-H

Well-known member
Joined
Jan 18, 2024
Messages
144
That is when you're retro-fitting an existing slab with a cutout and inset pour, not a new monolithic pour....pre-existing floors 6" is plenty (unless you're doing a 12k+ lift, which rarely people do at home, that's for heavy duty shops), per YOUR links:
Why are you ignoring the rebar requirement? Nobody is going to have a pre-existing 4" or 6" slab with #6's at 10" or 12". And no knowledgeable person would cast that design in a new structure. They would hire an engineer to calculate an efficient and reasonable reinforced slab that is strengthened around the lift bases. The 2-post lift industry needs to hire another engineer to calculate their standard concrete requirement sheets. What they have is poor.
 

Smoker

Well-known member
Joined
Sep 4, 2009
Messages
167
Location
San Antonio
Why are you ignoring the rebar requirement? Nobody is going to have a pre-existing 4" or 6" slab with #6's at 10" or 12". And no knowledgeable person would cast that design in a new structure. They would hire an engineer to calculate an efficient and reasonable reinforced slab that is strengthened around the lift bases. The 2-post lift industry needs to hire another engineer to calculate their standard concrete requirement sheets. What they have is poor.
I do. I had them pour the slab to those specs (actually ~5-6" deep to allow for slight changes in fill level) with that rebar on that spacing.
 

Firebrick43

Well-known member
Joined
May 12, 2015
Messages
13,971
Location
West central Indiana
Why are you ignoring the rebar requirement? Nobody is going to have a pre-existing 4" or 6" slab with #6's at 10" or 12". And no knowledgeable person would cast that design in a new structure. They would hire an engineer to calculate an efficient and reasonable reinforced slab that is strengthened around the lift bases. The 2-post lift industry needs to hire another engineer to calculate their standard concrete requirement sheets. What they have is poor.
Because we are not talking about a pre existing slab, we are talking about a new pour
 
OP
G

globalmax

Well-known member
Joined
Jun 17, 2023
Messages
57
Location
Greensboro, NC
Another option would be to go 5 inch Slab

If 6 inch is $2500
would the cost only be $1250 up charge for 50% less concrete than the 6inch slab…..


hmmmm
It is 30 length x25 feet wide 2 bay garage. Lift is going to be on one bay only. Having additional 2 inches of concrete only in one bay is a possibility?
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
22,186
Location
VT
It is 30 length x25 feet wide 2 bay garage. Lift is going to be on one bay only. Having additional 2 inches of concrete only in one bay is a possibility?
They just dig the grade deeper on that side.

You could also roughly plan out where the lift is going to be, and pour those areas deeper.
 

finn

Well-known member
Joined
Mar 27, 2005
Messages
16,175
Location
The UP, God's country
No it is not plenty. The manufacturers allow the thinner pre-existing slabs only if reinforced with a highly unprobable amount of reinforcement. So the retrofit slab design is required in every case for 2-post lifts. Having run the design computations on 2-post lifts myself, there is no way the thickened areas of the slab are going to be less than about 8" or 9". Manufacturers require 12".


I call ******** on this one. The compressive strength of typical 4” thick concrete is 3500 psi, or 504, 000 lb/sf. So double that if you have a two post lift with one square foot pads on each post. Then add normal rebar reinforcement.

Then consider that the slab isn’t hanging in the air like a bridge, but is supported underneath by a compacted gravel base.
 
Last edited:
To avoid these ads, REGISTER NOW!