To avoid these ads, REGISTER NOW!

Installing 220V for Welder Question

padronanniversary

Well-known member
Joined
Jul 11, 2010
Messages
1,367
Location
Minesooooooota
I plan on running a Miller 252 in my garage. Looks like I'll need roughly 40-45 Amps.

I assume this puts me in the 6-3 Romex range for copper with a 50 Amp breaker ?

Is this correct, or can I run 8 gauge ? Just want to make sure I have it sized appropriately.

Run will be about 30 feet from panel to outlet.
 
To avoid these ads, REGISTER NOW!

lametec

Well-known member
Joined
May 5, 2008
Messages
2,099
Location
Michigan
As long as the circuit is used for (and labeled as such) the welder only you can use 8 ga wire. Use a 60 amp breaker.

Edit: I should add that this circuit will be okay for your current welder. If you upgrade to one higher current requirement and/or higher duty cycle, the circuit may no longer be adequate.
 
Last edited:

nate379

Banned
Joined
Feb 2, 2009
Messages
7,279
Location
Palmer, AK
Can actually use 10 gauge for 50 amp on a welder outlet. Sorry I can't can quote the NEC as to where off the top of head, just remember reading it.

I still wired my outlets with #6 wire and the 2 outlets are about 3ft from my panel.
 

Buckgnarly

Well-known member
Joined
Oct 8, 2010
Messages
7,660
Location
VT
Can actually use 10 gauge for 50 amp on a welder outlet. Sorry I can't can quote the NEC as to where off the top of head, just remember reading it.

I still wired my outlets with #6 wire and the 2 outlets are about 3ft from my panel.

I may be wrong, but I think you are right. I think it has to do with the length of time the welder will be pulling that current. Short runs unlike a dryer, appliances, etc.
I think I used 8 for about a 1' run anyway.
 
To avoid these ads, REGISTER NOW!

lametec

Well-known member
Joined
May 5, 2008
Messages
2,099
Location
Michigan
For your reference:

weldercode.gif
 

Keep

Well-known member
Joined
Jan 1, 2009
Messages
1,398
Location
Oshawa, Ontario
Save some cash. Put the outlet as close to the box as you can, then go buy a 50ft welder extension cord. Should run you about $65 for the extension. Makes it easy to move the welder around.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
Can actually use 10 gauge for 50 amp on a welder outlet.
This is actually dependent on the machine connected to it, the 252 calls for 8. Technically if using Romex it may even be 6 but a small garage will never crank it up hard enough to make it an issue. I think it will spray arc 045 wire, would probably melt the factory stinger off,,, ha.
 
Last edited:
To avoid these ads, REGISTER NOW!
Top Bottom