Long time lurker, first time poster. I'm trying to run a sub panel 125' to my newly built shop. I plan on using 2-2-2-4 alum URD in 1 1/4 pvc conduit. My question is my main panel is on a interior wall around 15' from the exterior wall that the feed line will come in at, so can I run the URD in conduit the 15' in the attic to the main panel or do I have to switch to SER ?
 
To avoid these ads, REGISTER NOW!

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
make sure this URD is dual marked with a listed wire type (XHHW for example)
 
OP
X

xavier+09

New member
Joined
Jan 24, 2011
Messages
3
Thanks for the reply, excuse my ignorance but what is XHHW type wire? Can I run this type of URD indoors in conduit?
 

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
URD is not a listed wire type and may not be used. XHHW, RHHW, THWN are all listed wire types and may be used in an NEC installation. XLPE is not. Most of this 'mobile home feeder' is listed, but there is some out there that is not. The stuff the power companies use is not.

If its a listed wire type you can use it in conduit

someone more familiar with the applicable code section can tell you if the conduit has to be sized based on the overall diameter of the cable or if you can size based on the individual conductors since it doesnt have an outer jacket. im not sure.

practically speaking, if you are running 125ft through conduit underground you should consider getting individual conductors. i think pulling 125ft of 4 al conductors twisted together would not be fun. you may want to increase the size of the conduit a bit as well.
 

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
Basically, it has to have markings other than or in addition to the URD on it. If URD alone, you cannot enter the building with it.

Break the bank and use 2" conduit, you will be much happier pulling thru it.

Charles
 

fefarms

Well-known member
Joined
Jan 25, 2007
Messages
186
Fifteen feet is often not considered "nearest the point of entry" by the AHJ, meaning a separate disconnect is required anyway. If you used an outdoor disconnect you could terminate the URD there, and continue through the attic with a wire type suitable for indoor use.
 
To avoid these ads, REGISTER NOW!

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
Fifteen feet is often not considered "nearest the point of entry" by the AHJ, meaning a separate disconnect is required anyway. If you used an outdoor disconnect you could terminate the URD there, and continue through the attic with a wire type suitable for indoor use.

He has to run through the house 15' to get to the panel, is what I think he's saying. If he had to run 15' through the building to get to his subpanel, he'd most likely need an outside disconnect.

I also agree with using 2" pvc. Pipe's cheap when you factor in the frustration of trying to pull through a small conduit. Multiconductor cable doesn't pull as easy as individual wires IMO, so it'd definitely be worth it to upsize. Plus the insulation isn't as smooth as THHN THWN so it'll want to drag a little more. Use lube.
 

green.bubbly

Well-known member
Joined
Dec 14, 2008
Messages
2,156
Location
Lafayette, LA
He has to run through the house 15' to get to the panel, is what I think he's saying. If he had to run 15' through the building to get to his subpanel, he'd most likely need an outside disconnect.

I also agree with using 2" pvc. Pipe's cheap when you factor in the frustration of trying to pull through a small conduit. Multiconductor cable doesn't pull as easy as individual wires IMO, so it'd definitely be worth it to upsize. Plus the insulation isn't as smooth as THHN THWN so it'll want to drag a little more. Use lube.



What would be used for lube? I will be pulling some wire through pvc pretty soon.
 
OP
X

xavier+09

New member
Joined
Jan 24, 2011
Messages
3
Will take the advice and use 2" pvc conduit, I just wanted to make sure I can run the URD indoors but it sounds like there is different types of URD. Great forum, lots of good advice.
 

Kriilin

Well-known member
Joined
Oct 2, 2009
Messages
69
I don't know if your setup and code allow, but have you thought of using a dual-lug meter hub? That way you keep the wiring outside, and don't put a load on your main panel.
 