Yes, to make it a proper 4 wire feed, you need to add an insulated ground wire back to the main panel. The local ground rods are for a different purposeHere is the panel after moving some of the wires out of the way for clarity.
The copper ground is going to two ground rods spaced several feet apart, It is not going back to the main panel. It has (3) aluminum wires coming from the main panel at the house about 65'.
Bought a 100 Amp load center today.
Assuming i still need to run a ground from the main panel?
View attachment 2232626![]()
GE 100 Amp 20-Space 20-Circuit Main Breaker Indoor Load Center Contractor Kit TM2010CCUBK1 - The Home Depot
Save money and space at your workspace with the addition of this excellent GE Main Breaker Indoor Load Center Contractor Kit.www.homedepot.com
I dont believe the panel swap is enough to trigger a requirement that you update to 4 wire, but it would be a good idea. Not a small project