Is a DOB relay at the condenser recommended for a residential split system?

gagecalman

Well-known member
Joined
Feb 5, 2020
Messages
217
Location
MD
Is a DOB relay like the ICM206 at the condenser recommended for a residential split system?

I was also wondering if there's a produce that will help if the furnace is 120-volts because if the leg not supplying it is lost the 120-volt transformer will keep the DOB energized as well as the contactor but the compressor will stop. If the leg is energized quickly the compressor will start right back up which is not good and it could also rotate backwards.
 
To avoid these ads, REGISTER NOW!

fitter30

Well-known member
Joined
Jun 23, 2019
Messages
3,022
Location
Peace Valley,mo
Most if not all electronic termostats have in their program a setting for 5 minute timer compressor off. Most scroll style compressors start unloaded. 5 minute dob relay if the thermostat doesn't have a timer is a good idea.
 

manwithtools

ALLIANCE MEMBER
Joined
Aug 24, 2015
Messages
14,683
Location
Lebanon, TN
Don't most modern compressor units have it built into the control board? In addition new thermostats have compressor delays built into their functionality.
 
OP
G

gagecalman

Well-known member
Joined
Feb 5, 2020
Messages
217
Location
MD
I understand if the transformer is on an air handler and is 240VAC. If only one leg drops the 24VAC is lost and the DOB start the delay.


But if the transformer is on a 120VAC furnace and the leg not supplying it is lost the 120VAC transformer will keep the thermostat and DOB energized as well as the contactor but the compressor will stop. If the leg is energized quickly the compressor will start right back up.


Is there a product that will fix this?
 

PoorUB

Well-known member
Joined
Mar 29, 2021
Messages
11,889
Location
Fargo, ND
I understand if the transformer is on an air handler and is 240VAC. If only one leg drops the 24VAC is lost and the DOB start the delay.


But if the transformer is on a 120VAC furnace and the leg not supplying it is lost the 120VAC transformer will keep the thermostat and DOB energized as well as the contactor but the compressor will stop. If the leg is energized quickly the compressor will start right back up.


Is there a product that will fix this?
https://www.icmcontrols.com/product/icm492/
 
To avoid these ads, REGISTER NOW!

98ssuck

Well-known member
Joined
Oct 21, 2012
Messages
350
Location
British columbia
Hypothetically those things could happen with losing phases and what phase energizes the control transformer. But what problem are you trying to solve?
 

pcmeiners

Well-known member
Joined
Aug 13, 2009
Messages
8,054
Location
In the only town in Pennsylvania, Bloomsburg.
. If the leg is energized quickly the compressor will start right back up which is not good and it could also rotate backwards.
How is the compressor going to rotate backwards, utility AC comes into the unit and converted to DC, then back again in modern VFD mini splits. The control board is controlling rotation, not the utility power legs.
 
OP
G

gagecalman

Well-known member
Joined
Feb 5, 2020
Messages
217
Location
MD
How is the compressor going to rotate backwards, utility AC comes into the unit and converted to DC, then back again in modern VFD mini splits. The control board is controlling rotation, not the utility power legs.
Residential split system. I never mentioned mini split.
 

bob smith1

Well-known member
Joined
Jul 2, 2026
Messages
138
DOB is delay-on-break, you want DOM, delay-on-make, or otherwise usually called time delay. You don't need 5min, and I like adjustable. what you need to watch for is overlapped circuits where the stat serves a delay, then a relay. but you need to ensure that in any scenario, the compressor won't attempt a hot restart. What is common is power glitches. You want that compressor to take a break.
 