Happy Easter to all. I have a Champion 5 hp 3 phase compressor. Using a RPC and a disconnect I can run the compressor just fine. Do I need a Mag starter? Thank You 930.
 
To avoid these ads, REGISTER NOW!

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
Does the motor have a thermal overload reset button on it, usually on the end opposite the pulley? If not, the motor does not have any overload protection and for that reason alone, you probably should have a starter, as they, when set up with the proper overload heat element in them, provide that protection. Beyond that, 5 hp is alot for the pressure switch, much easier on the pressure switch contacts to have a starter.

Charles
 

GeorgiaHybrid

Well-known member
Joined
Sep 9, 2008
Messages
3,763
Location
Extreme NW Georgia
Most people use a starter when the HP gets to 5 or more. like Charles mentioned, it is easier on the pressure switch contacts. Also read his comment about thermal overload protection. If your motor does not have an overload reset, you should have a starter with the correct heater installed.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,772
Some type of overload protection is required for 1 HP & larger cont. duty motors per 430.32 (NEC 2005), this can be debated if compressor is cont. duty though...

That being said, I would have a starter on a compressor.
 
OP
9

930dreamer

Super Moderator
Staff member
Joined
Oct 7, 2009
Messages
23,016
Location
Amarillo,TX and Stinnett,TX
Thanks for the comments. Earlier this year I tried to install a mag starter but failed, I posted my questions here but wasn't in town enough to mess with it. I have some time now and will post a picture of the mag starter. Thanks
 
OP
9

930dreamer

Super Moderator
Staff member
Joined
Oct 7, 2009
Messages
23,016
Location
Amarillo,TX and Stinnett,TX
This is the Furnas motor control, I'm trying to wire the pressure switch also.
It shows LINE to L1, MOTOR,MOTOR and LINE L2. The motor control box only has a reset on the cover, do I need a on/off switch also. Thanks 930
 

Attachments

  • 032710 003.jpg
    032710 003.jpg
    137.1 KB · Views: 25
  • 032710 004.jpg
    032710 004.jpg
    144.7 KB · Views: 34
  • 032710 005.jpg
    032710 005.jpg
    137.2 KB · Views: 26
  • 032710 006.jpg
    032710 006.jpg
    133.9 KB · Views: 20
Last edited:

W-Cummins

Well-known member
Joined
Jan 9, 2006
Messages
1,642
Location
Iowa
That motor starter will work BUT, as far as I know it's no longer allowed under the later NEC codes as it only has the overloads on 2 of the three phases.....

William....
 

JBurgess

Well-known member
Joined
Mar 1, 2008
Messages
372
Location
Arizona
I circled the parts of the label that apply to what you want to do. I also circled teminals 1 and 3 on the drawing.

If you want a on off switch wire it in series with the pressure switch.

I circled the directions for single phase in case you are using a RPC. The manufactured phase would go in the middle on L2 but you don't want to use it to power the coil. This change will correct that. It may cause the coil to chatter on start up if it is powered by the manufactured phase.

03271020003A.jpg
 

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
You need a manual disconnect within view of and within 50 ft of the compressor. If you cannot meet those requirements using the circuit breaker, you need a disconnect of some sort. It will need to break all three hot legs.

Charles
 
To avoid these ads, REGISTER NOW!

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,772
In the 1st post it was said the compressor was 3Ø , & that starter has been prohibited for a 3 Ø applications since the 1971 NEC was adopted, one overload per phase is required.
 
OP
9

930dreamer

Super Moderator
Staff member
Joined
Oct 7, 2009
Messages
23,016
Location
Amarillo,TX and Stinnett,TX
I have a 30 amp disconnect next to the compressor,with 3 -30 amp fuses. I'm running 3 phase from a RPC.

One question is, does the wiring from the motor go into the pressure switch. From there out to the disconnect and then to the starter?
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,772
I have a 30 amp disconnect next to the compressor,with 3 -30 amp fuses. I'm running 3 phase from a RPC.

One question is, does the wiring from the motor go into the pressure switch. From there out to the disconnect and then to the starter?

No, the pressure switch leads go to the mag starter.
 

JBurgess

Well-known member
Joined
Mar 1, 2008
Messages
372
Location
Arizona
The presure switch goes where I circled where it says "remote 2 wire control". From terminals 1 to 3.

03271020003A.jpg
 

JBurgess

Well-known member
Joined
Mar 1, 2008
Messages
372
Location
Arizona
If I remember right you still need to change the heaters to the correct ones for your motor.

You might want to trim the ends on those wires ties before the wire tie police catch up with you.:)
 