...to use 14 ga. wire with a 20 amp breaker?
For normal branch circuits, absolutely not, in NEC art. 430 & 440 it's allowed to use table 310.16 & then 14 AWG is rated 20A & 12AWG is 25A, but there are a # rules to be followed first.....
The short answer is yes since the question is "ever", not only 20 but is some cases 30, but that would be specialized equipment and not part of a general use circuit.Is it ever okay....
It's not uncommon for a hair dryer to draw ~1500 watts. Add 15 bulbs @ say 15 watts =225 watts for a total of ~1775w.
1775/110volts =16 amps.
Time to add another circuit.