Ok, guys. I need your help again.
You may recall this thread from a couple of weeks back.
https://www.garagejournal.com/forum/showthread.php?t=375414
I have a Goodman GMS80453ANA that's mounted horizontally in the rafters of my 780 sq/ft detached garage. I though I had that no-heat issue solved, but went back out there yesterday morning and found that shop temp had fallen below the thermostat setting of 60 degrees F.
I climbed up there and found that the cycle would start as normal and the hot surface igniter glowed bright for 4 to 7 seconds, but there was no call for gas (no flame). It would repeat this three times before the status light would flash once indicating a lockout condition. I reset the unit and found the issue recurring.
I used my voltmeter to check for AC current at the gas valve. It's believe it's a simple two-wire switch. I found no current jump to 24V (or so) while the hot surface igniter was cycling.
Considering that I had an intermittent operation last winter and now intermittent operation this year with what I though was a real pressure switch issue and now a gas valve issue, it is time to simply replace the control board? Or is there something else I should be checking first?
You may recall this thread from a couple of weeks back.
https://www.garagejournal.com/forum/showthread.php?t=375414
I have a Goodman GMS80453ANA that's mounted horizontally in the rafters of my 780 sq/ft detached garage. I though I had that no-heat issue solved, but went back out there yesterday morning and found that shop temp had fallen below the thermostat setting of 60 degrees F.
I climbed up there and found that the cycle would start as normal and the hot surface igniter glowed bright for 4 to 7 seconds, but there was no call for gas (no flame). It would repeat this three times before the status light would flash once indicating a lockout condition. I reset the unit and found the issue recurring.
I used my voltmeter to check for AC current at the gas valve. It's believe it's a simple two-wire switch. I found no current jump to 24V (or so) while the hot surface igniter was cycling.
Considering that I had an intermittent operation last winter and now intermittent operation this year with what I though was a real pressure switch issue and now a gas valve issue, it is time to simply replace the control board? Or is there something else I should be checking first?