mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
you can only backfeed a panel to a total of 120% of the rated bus capacity (this applies to solar or other grid tie sources, not backup generators which are switched with the main) so for example if you have a 200amp panel with a 200a main feeding it, the breaker backfed by the grid tie inverter can only be 40a
 

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
That is true for residential under 2005, however in this case we using service entrance conductor taps instead of back feeding a panel.

oh yeah....probably would have helped if i looked at the picture :rolleyes:
 