Is my Well pressure switch wired right?

JOE.G

Well-known member
Joined
Feb 4, 2013
Messages
765
Location
Eastern ( Catskills ) NY
Hi, Today I decided to clean out the tube that the Well pressure switch is connected to ( Completely clogged not sure how it was working ) and I cleaned up the switch.
I have a Sta - Rite SK 2 switch which I adjusted to be a 40/60. I also have a 1/2 HP 230 Volt well pump.

Now I have had no problems but my wiring does not seem to be like anything I have seen on the net.

The first pic is of my cover
2nd is my switch
3 and 4 are samples off the Net.
Mine is wired 2 out side posts to a 2 pole 20 amp breaker and the middle wires go to my Pump.
I did attach wires better when I put it back together.

Thanks
 

Attachments

  • Cover.jpg
    Cover.jpg
    88.2 KB · Views: 97
  • Mine.jpg
    Mine.jpg
    77.9 KB · Views: 144
  • Sample.jpg
    Sample.jpg
    103.8 KB · Views: 122
  • Sample 2.jpg
    Sample 2.jpg
    99.3 KB · Views: 94
Last edited:
To avoid these ads, REGISTER NOW!

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,733
Location
NW Iowa
Black and white don't matter. This is 240v so it's not a neutral. If you want to be technical the white wire should be colored black. Then you wouldn't even know the difference.
 
OP
J

JOE.G

Well-known member
Joined
Feb 4, 2013
Messages
765
Location
Eastern ( Catskills ) NY
Okay so mine is right? I could switch the two power wires ( White and black from breaker box ) with each other and also switch the two motor wires ( White and Black center wires ) with each other and it would be fine?

Why do the pictures I took from the net have black with black and white with white? It appears they dont have the motor hooked to both center screws which the label says they are for the motor.

I am trying to learn and I thank you guys for the help
 
Last edited:

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,733
Location
NW Iowa
Why do the pictures I took from the net have black with black and white with white? It appears they dont have the motor hooked to both center screws which the label says they are for the motor.

I am trying to learn and I thank you guys for the help

Because they don't know any better and think it matters.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,019
Location
Modesto, CA
The order doesnt matter.

If you ran THWN to the switch and used all black it still wouldnt matter. The hot legs from single phase 240v can go any way.
 

walta

Well-known member
Joined
Jan 13, 2017
Messages
2,311
Location
Dutzow Missouri
There is nothing wrong with the way you wired the switch.

The only possible danger is the next time you disconnect the wires and switch you could put the wires back slightly differently and short the circuit making the breaker trip and maybe damage the switch. If you keep the whites and blacks together you can’t make that mistake.


Walta
 

Junkman

Well-known member
Joined
Dec 18, 2006
Messages
6,626
Location
Northeastern CT
My only suggestion is to change out your switch for a new Square D switch with low pressure cut off. If you left your home, and a pipe broke, the pump would shut off because the broken pipe would be pulling more water out of the tank than the pump could recover. We had a ruptured water hose on the washing machine, that started flooding the laundry room, until the pump shut down. Now, I have hoses on the washing machine that also shut off the flow should one rupture.
They sell in the $25 range at Home Depot.. Cheap Insurance....
 

Attachments

  • square-d-pump-switche.jpg
    square-d-pump-switche.jpg
    53.2 KB · Views: 23

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,174
Location
SE MI
Okay so mine is right? I could switch the two power wires ( White and black from breaker box ) with each other and also switch the two motor wires ( White and Black center wires ) with each other and it would be fine?
As stated, it does not matter, but if it makes you feel better, switch either the motor wire OR the power wires, BUT NOT BOTH.

That is, make the colors line up like the other picture. (It does look a bit odd, like the first time you see a white wire going to one of the legs on a 240V breaker.)
 
OP
J

JOE.G

Well-known member
Joined
Feb 4, 2013
Messages
765
Location
Eastern ( Catskills ) NY
I get it now, I can swap 1 and 4 or 2and 3 with each other and have colors matched. Ill leave it for now and if and when i replace switch I ll do it then. Just wasn't 100 % sure.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,756
One thing I see wrong is the NM cable “Romex” being used. Doubt anyone could say it’s protected from physical damage or in a dry location.
 

s14kev

Well-known member
Joined
Dec 12, 2008
Messages
245
One thing I see wrong is the NM cable “Romex” being used. Doubt anyone could say it’s protected from physical damage or in a dry location.

That should be fine if in a well house. My pressure switch is outdoors in a valve box and I wired it with UF cable.
 
OP
J

JOE.G

Well-known member
Joined
Feb 4, 2013
Messages
765
Location
Eastern ( Catskills ) NY
I fixed up the connections, I did not use Romex as this passed inspection in 2010, It is in the basement of my home. I have seen a few wired like this with no romex.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,019
Location
Modesto, CA
I fixed up the connections, I did not use Romex as this passed inspection in 2010, It is in the basement of my home. I have seen a few wired like this with no romex.

The well is in your basement? That would make it impossible for a derrick truck to change it out.

how deep is the well and what type of drop pipe does it use?
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,733
Location
NW Iowa
The well is in your basement? That would make it impossible for a derrick truck to change it out.

how deep is the well and what type of drop pipe does it use?

Pretty hard to put a pressure switch, tank and pump control in a 6" casing...

I'm sure the well is in the yard somewhere. It's pretty common to put the rest in the house basement. And yes I've wired them with Romex.
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,019
Location
Modesto, CA
Pretty hard to put a pressure switch, tank and pump control in a 6" casing...

I'm sure the well is in the yard somewhere. It's pretty common to put the rest in the house basement. And yes I've wired them with Romex.

most of the wells ive serviced out here have had everything right next to the casing so I didnt think of a divorced setup
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,733
Location
NW Iowa
most of the wells ive serviced out here have had everything right next to the casing so I didnt think of a divorced setup

Don't get me wrong there are some like that here but you either need a pit 5-6' in the ground or a shed with a heater to keep it from freezing.

Used to be real common with dug or early drilled wells to have a pit 5-6' deep with all the equipment in it and the well would be in the bottom. Now the well head needs to be above ground to prevent ground water contamination.
 

walrus

Well-known member
Joined
Nov 12, 2008
Messages
11,679
Location
Maine
The well is about 135 foot deep, it is about 70 Ft from my home, The Pressure tank and switch are in the basement.

Just like 99% of wells in Maine, the guys in warm climates don't have to worry about freezing water but in the Northeast...........
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,756
Just like 99% of wells in Maine, the guys in warm climates don't have to worry about freezing water but in the Northeast...........

Yup, the people who live in god forsaken country have to worry about that, my tank is sitting outdoors but back in 1990-91 there were temps in the single digits that caused a lot of water damage here, the 1/4” galvanized ****** under the pressure switch froze causing the rental to run out of water.
 
OP
J

JOE.G

Well-known member
Joined
Feb 4, 2013
Messages
765
Location
Eastern ( Catskills ) NY
Around here almost all set ups are like mine, Tank and switch in basement or some where in the home. Funny how some thing you think is normal and the same everywhere is not.
 

Blk88GT

Well-known member
Joined
Mar 16, 2009
Messages
1,075
Location
Manitoba
The only thing I don't care for in the pictures are the lack of loops on the wire ends to get a positive wrap around the screws.
 

Arne73

Well-known member
Joined
Mar 20, 2010
Messages
1,477
Just had to replace the line from my pressure tank on Tuesday. Galvanized pipe sprung a leak, replaced it all with schedule 80 PVC.
Here's my switch~SQ-D, no low pressure shut off. 20200214_075317.jpeg

Sent from my SAMSUNG-SM-G930A using The Garage Journal mobile app
 

Junkman

Well-known member
Joined
Dec 18, 2006
Messages
6,626
Location
Northeastern CT
This is my low cut off switch. I had to replace it last year, because the one that was installed 30+ years ago, had clogged up with rust. Where I live, we have something in the water called "iron bacteria", which gets as thick as chocolate pudding in the filters. There are only 2 ways to get rid of it... filters or chlorinating the well and letting it sit for a few weeks with chlorine in it, which isn't going to happen. Last time I did that, was when we were going away for 2 weeks. When I came back, the iron bacteria was gone, but the water smelled of chlorine for a couple of months afterward.
This switch came from Lowes, and is branded "Everbilt". I also keep spare parts in the event my well gets struck by lightning. It was a problem for a number of years, but for some unknown reason, it hasn't happened in the last 10 or 15 years. Before that, it was every 2 or 3 years, lightning would blow out the well pump and the control. It happened enough times that I kept spare parts including the 2 HP well pump on hand.
It has a place in the box for an optional run capacitor, but it was never installed, and I often wonder if it might be of some value to add it?
 

Attachments

  • MVC-012L.JPG
    MVC-012L.JPG
    108.8 KB · Views: 21
  • MVC-013L.JPG
    MVC-013L.JPG
    110.2 KB · Views: 19
  • MVC-016L.JPG
    MVC-016L.JPG
    86.6 KB · Views: 19
  • MVC-017L.JPG
    MVC-017L.JPG
    83 KB · Views: 16
  • MVC-018L.JPG
    MVC-018L.JPG
    65.7 KB · Views: 17
Last edited:

850xpeps

Well-known member
Joined
Aug 6, 2017
Messages
1,365
All wells I have seen have a pump house and everything is near the casing.



Interesting setup. Haven't seen a divorced setup before.



CT



Everything here is a deivorced setup. Sometimes older houses that had jet pumps had the at the well. But any submersible I’ve seen has everything in the house. And a bulldog or snappie or whatever you wanna call it about 6-8’ down to stop from freezing and that’s where the water line connects to go to house
 

JRC3

Well-known member
Joined
Jun 30, 2014
Messages
12,481
Location
Southwestern OH
The wiring is fine, not how I'd do it. Luckily electric current/phase is colorblind.

My only suggestion is to change out your switch for a new Square D switch with low pressure cut off. If you left your home, and a pipe broke, the pump would shut off because the broken pipe would be pulling more water out of the tank than the pump could recover. We had a ruptured water hose on the washing machine, that started flooding the laundry room, until the pump shut down.
They sell in the $25 range at Home Depot.. Cheap Insurance....
That only happened by chance. Most plumbing is restricted enough so the pressure wouldn't drop below the 30psi or whatever the pump saver switch is set to cut-off? I mean a tub or hos bib should deliver pretty much the full flow of any pipe feeding it. Do most well saver pumps trip when either of those high flow faucets are used? Nope.
 

JRC3

Well-known member
Joined
Jun 30, 2014
Messages
12,481
Location
Southwestern OH
I'd guess the Romex is 12/3 and someone discovered they didn't need the common for the well application. If so, I'd used the red instead of the white for the other hot.
 
OP
J

JOE.G

Well-known member
Joined
Feb 4, 2013
Messages
765
Location
Eastern ( Catskills ) NY
Wires are wrapped and hooked up correctly now, this was a before shot. Yes the red was from a 12/3 and it is tapped off, Why would you use the red just because of color? Both have bare grounds which are grounded to switch ground screws.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,733
Location
NW Iowa
Wires are wrapped and hooked up correctly now, this was a before shot. Yes the red was from a 12/3 and it is tapped off, Why would you use the red just because of color? Both have bare grounds which are grounded to switch ground screws.

You are putting way to much thought into this whole thing. They used 12/3 for some reason (doesn't matter) and capped the extra wire. None of the colors matter because it's 240v single phase.

All that matters is that the pump gets power when the pressure switch calls for it. The two hot wires can be flipped back and forth and they could be black, red, purple, blue, ect. It just doesn't matter.

The only thing wrong is the white wire should be marked black, or any color other than white, gray or green. But that is a very minor detail.
 

JRC3

Well-known member
Joined
Jun 30, 2014
Messages
12,481
Location
Southwestern OH
Yes the red was from a 12/3 and it is tapped off, Why would you use the red just because of color?
The only thing wrong is the white wire should be marked black, or any color other than white, gray or green. But that is a very minor detail.
And that's why I'd use the red instead of the white. Red and black mean hot. But the pump don't care, it is color blind.
 

SGKent

Banned
Joined
Feb 12, 2010
Messages
1,959
Location
Citrus Heights CA
IMHO - to me it is just the whole reason for this thread - someone looks at it and instead of having a pretty good idea what has been done, the first thing that goes thru their mind is, "what have they done here?" I hope the rest of the wiring on this property is more standard. The way the wires were jammed into that switch doesn't speak highly of whomever did/maintained the wiring on that property.

I'd probably turn the breaker off and verify that a white and a black were used, use a sharpie to put a bold black stripe on the white, then do the same at the relay, and make the sides so that black/black is one side and white/blk / white/blk is the other. My guess is that this won't be the only wiring on the property that could use some tuning. The red may be too short to use, and using it instead of white would require changes at the pump. If the pump wiring connection is above ground then use the black sharpie there too and make sure the connection is solid.
 
Last edited: