Is PVC conduit available in threaded *******?

gamp945

Well-known member
Joined
Jun 4, 2014
Messages
1,550
Hi all,

Probably a beginner question - but I can't find anything from a google search.

I am working with PVC conduit for my outbuilding's service entrance. I know that there are threaded male adapters available for PVC conduit. But I am trying to connect the panel on the inside straight through to two different boxes on the outside (LB conduit body and an AC disconnect). The distance between the panel and the outside wall is, obviously, very short. If I use two male terminal adapters then the length of the conduit won't allow me to mount the conduit body and disconnect flush to the outside wall.

I know that with EMT you can use short threaded *******, and this seems like it would solve the problem I am having. But are threaded ******* available in PVC?

I found these, but although they are sch 80 and grey, I don't think they are UL listed for conduit (but maybe I'm wrong?):
https://www.supplyhouse.com/Spears-884-025-1-x-2-1-2-PVC-Sch-80-Threaded-******#product-overview

Sorry if I'm being dense, but what is the solution here? Should I just use EMT conduit for the service entrance instead so that I can use the threaded *******?

Thanks for reading :beer:
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,257
Location
Modesto, CA
Just use some chase ******* and be done with it

The conduit you linked to appears to be sprinkler pipe and not for electrical use
 
OP
G

gamp945

Well-known member
Joined
Jun 4, 2014
Messages
1,550
Chase ******* are metal, correct? So you are suggesting to get rid of the PVC conduit/fittings and LB and use all metal instead?
 
OP
G

gamp945

Well-known member
Joined
Jun 4, 2014
Messages
1,550
yatg: got it - so use two PVC box adapters and PVC conduit instead of the male terminal adapters + locknut and bushing - correct?
 
To avoid these ads, REGISTER NOW!

yatg

Well-known member
Joined
Aug 16, 2019
Messages
2,918
Location
Southern Oregon
yatg: got it - so use two PVC box adapters and PVC conduit instead of the male terminal adapters + locknut and bushing - correct?

Not quite. The box adapter o.d. is the same size as the pipe and glues into a female fitting.

If the LB is back to back with the panel, glue the box adapter into the LB through the panel.
Or put a stub of PVC into the LB, add a coupling, and glue the box adapter to the coupling through the panel.

BELOW DOES NOT WORK
The OD of the reducer is the same as the OD of the adapter...
Thanks Innovate1 for pointing that out

Another option, depending on what size of fitting or pipe you're using, is to use the next size up box adapter and a reducer. The reducer is about half the length of a coupling.
Example, 1/2 conduit -> 1/2 to 3/4 reducer -> panel -> 3/4 box adapter
This provides no sandwiching (locknut or shoulder) support to the panel, so it would need to be fitted up tight.

https://www.homedepot.com/p/Carlon-3-4-in-x-1-2-in-PVC-Reducer-Bushing-E950ED-CTN/100404103
 
Last edited:
OP
G

gamp945

Well-known member
Joined
Jun 4, 2014
Messages
1,550
I picked up some PVC box adapters last night and they might work for both the LB and the disconnect. The thickness of the sheathing, rainscreen, siding, and standoffs is about 1.25 - 1.5", so in both cases I don't think I'll be able to fully insert the box adapter into the mating piece, but there should be enough surface area for the PVC cement to do its job.

Thanks for the help!
 

Innovate1

Well-known member
Joined
Jul 28, 2014
Messages
4,330
Location
Illinois near St. Louis, Missouri
Another option, depending on what size of fitting or pipe you're using, is to use the next size up box adapter and a reducer. The reducer is about half the length of a coupling.
Example, 1/2 conduit -> 1/2 to 3/4 reducer -> panel -> 3/4 box adapter
This provides no sandwiching (locknut or shoulder) support to the panel, so it would need to be fitted up tight.

https://www.homedepot.com/p/Carlon-3-4-in-x-1-2-in-PVC-Reducer-Bushing-E950ED-CTN/100404103

The box adapters look slick and reduce the extension into the box quite a bit. Have a few places I will do that. Seems like generally less work and parts to do that than the male adapter, locknut, and bushing.

But I am not following the other option. The OD of the reducer and box adapter seem to be the same so how are those connected?
 

yatg

Well-known member
Joined
Aug 16, 2019
Messages
2,918
Location
Southern Oregon
The box adapters look slick and reduce the extension into the box quite a bit. Have a few places I will do that. Seems like generally less work and parts to do that than the male adapter, locknut, and bushing.

But I am not following the other option. The OD of the reducer and box adapter seem to be the same so how are those connected?

Ugh. You are correct.
Was thinking the electrical reducer was like a plumbing reducer coupling.
 
Last edited: