Is this against common practice?

roosh725

Well-known member
Joined
Feb 16, 2015
Messages
83
Let me preface this- I understand what the code is in my area. But I’m asking in the sense of general electrical safety.

I am in the process of finishing my basement and I plan on putting drywall on my ceiling. I have about 10 of these junction boxes with lights on them. The boxes are too deep 1-1/2 for my drywall plans so I found these from Garvin which are 1-1/4 deep and would work. So w plus it be ok to removed the lights, replace the boxes with the thinner ones, cap off or remove the unused wires that went to the lights, and placed a cover on them. Then Drywall right over. I don’t plan on needing to access these ever. They just go to outlets on the main floor.

Thank you in advance.

42de12ed4d3e5cafba56413b059d2e84.jpg
94ffa57dabb64c4561f2bf4d27517d56.jpg


Sent from my iPhone using Tapatalk
 

Attachments

  • 42de12ed4d3e5cafba56413b059d2e84.jpg
    42de12ed4d3e5cafba56413b059d2e84.jpg
    61.8 KB · Views: 0
  • 94ffa57dabb64c4561f2bf4d27517d56.jpg
    94ffa57dabb64c4561f2bf4d27517d56.jpg
    45.9 KB · Views: 0
Last edited:
To avoid these ads, REGISTER NOW!

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
If its got a junction in it cant be covered. Here is something to consider. It dont gotta be the way it was. You can reroute the other wire etc? Even go so far as to pull a new longer wire if I had to and get rid of it all if you dont need it.
 
Last edited:

Shiftless

Well-known member
Joined
Mar 9, 2014
Messages
14,495
Location
East Bay SFO
So could the O.P. pull all of the wires out of the conduit and replace with continuous runs serving only the receptacles on the main floor. Then put covers on the 4x4 boxes and drywall over them?

I wouldn’t do it that way, but since there would not be any wire connections in those 10 boxes, wouldn’t it be “legal” to cover them?

That sounds like more work than simply ripping all of that out and starting over again.
If it’s gonna be finished, just run NM cable through holes drilled in the joists and be done with it.


.
 
Last edited:

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
That sounds like more work than simply ripping all of that out and starting over again.
If it’s gonna be finished, just run NM cable through holes drilled in the joists and be done with it.
This is what I am saying to do, re route/replace some wire and tear that out.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
I would tend to think it would be a sleeve for protection if the wire was continuous, the steel would need to be grounded. If I was doing the wall or ceiling and the finish removal of all I could might be worth it.
 

grounded-b

Well-known member
Joined
Oct 23, 2012
Messages
285
Location
Milwaukee, WI
No, It would not be legal and would not be "common practice" to cover any electrical box with drywall, or any other "non-removable" surface.

NEC 314.29 Boxes, conduit bodies and handhole enclosures to be accessible

Even if the wire is pull through the box, without splices, it needs to be accessible. Think how hard it would be, if someone in the future, pulled out those wires, not knowing there was a J-Box in the run, and tried to push a fishtape back into the conduit. It would be nearly impossible to get the fishtape to hit the other conduit, once it got to the box.

Here's an idea - replace the boxes with your 1 1/4" deep, 4" squares. Install a square to round plaster ring, matching the thickness of your drywall, and then once the ceiling is finsished, install round blank covers. I believe Arlington makes a nice plastic one, which has no exposed screws and can be painted to match. it's number CP-3540

http://www.aifittings.com/catalog/miscellaneous/ceiling-box-cover/CP3540

Steve
 
Last edited:

grounded-b

Well-known member
Joined
Oct 23, 2012
Messages
285
Location
Milwaukee, WI
So could the O.P. pull all of the wires out of the conduit and replace with continuous runs serving only the receptacles on the main floor. Then put covers on the 4x4 boxes and drywall over them?

I wouldn’t do it that way, but since there would not be any wire connections in those 10 boxes, wouldn’t it be “legal” to cover them?

.

No, even if there are no splices, it is still a box, and can not be buried behind drywall, or other non-removable surface

Steve
 

Shiftless

Well-known member
Joined
Mar 9, 2014
Messages
14,495
Location
East Bay SFO
No, even if there are no splices, it is still a box, and can not be buried behind drywall, or other non-removable surface

Steve

Thanks
Then definitely tear it all out.
The extra work of swapping for thinner boxes, untwisting and retwisting a hundred connections, cutting holes in the drywall for all of those rings and then just capping them off with blank covers, even good looking ones, seems like a losing proposition.
 
To avoid these ads, REGISTER NOW!
OP
R

roosh725

Well-known member
Joined
Feb 16, 2015
Messages
83
Thank you all for the suggestions! A great help!


Sent from my iPhone using Tapatalk
 

mcbane

Well-known member
Joined
Jul 23, 2017
Messages
794
Location
California
I like doing things the hard way so if I wanted the lights I would just remove the screws that hold up the conduit and boxes. Do only one portion at a time and use a sheet rock lift the slide the Sheetrock between the conduit and the joists. Reinstall the mounting straps and box screws and proceed to next section. Not really as hard as it sounds.


Sent from my iPhone using The Garage Journal mobile app
 
OP
R

roosh725

Well-known member
Joined
Feb 16, 2015
Messages
83
I like doing things the hard way so if I wanted the lights I would just remove the screws that hold up the conduit and boxes. Do only one portion at a time and use a sheet rock lift the slide the Sheetrock between the conduit and the joists. Reinstall the mounting straps and box screws and proceed to next section. Not really as hard as it sounds.


Sent from my iPhone using The Garage Journal mobile app


My whole idea is to hide all the above behind the Sheetrock. I want the basement to feel like any other room in the house as much as possible.


Sent from my iPhone using Tapatalk
 

teamextreme

Well-known member
Joined
Aug 10, 2013
Messages
867
Location
Lakewood, CO
Every basement finish I do involves demoing all the existing wiring. As Wylies mentioned, not sure why there's EMT there, rip it out and run romex, unless you're in Chicago.
 

MrSurly

Well-known member
Joined
Jan 15, 2014
Messages
1,671
Location
East Texas
The so-far unmentioned option: remove the boxes, replace with EMT and two couplings, pull the (continuous) wire back in, cover it up with drywall, no issues.
 
Last edited:

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,994
Location
Modesto, CA
The so-far unmentioned option: remove the boxes, replace with EMT and two couplings, pull the (continuous) wire back in, cover it up with drywall, no issues.

He would have to rerun all the EMT as well since it is surface mounted on the joists and he wants to put up sheetrock.
 