A contractor is fixing my house. He's putting junction boxes inside the ceiling. Is that legal?
The previous owner had house wiring running through a duct from the cooler on the roof. I'm getting new ductwork. The wires were re-routed. But is this code? The wood on the bottom is going to support the new ceiling.
Inside the box is wire nuts. You can just see what he said is a splice above the box.
There is a matching box on the other side of the duct.
rust buster
VA
Not in any states I've lived in. Junction boxes have to be accessible. I'm not an electrician though!! Is there actually a junction or is it just a housing for unused wires that terminate in the box?
Norcal
That pancake box screams hack work, nothing right about any of it. The contractor say they are good at 'lectrician work? :( If it is for a swamp cooler, it works great to have conduit between the cooler & the switch so a selector switch for high cool / low cool/ pump/ high vent/ low vent, can be used, it is a real cluster f to use NM cable "Romex®" in a multi speed application.
N
Nick Danger
Albuquerque
Not for the swamp cooler. That wiring is just passing through. It powers a bedroom.
I told the contractor that I wanted splices instead of the boxes.
TRWham
East Cobb County, Georgia
J box has been discussed.
Exposed NM in a duct/plenum is not allowed (see 300.22). There are several solutions to the problem, but the best is to go around the duct.
N
Nick Danger
Albuquerque
The exposed NM in the duct is what we found when we opened the ceiling. The junction boxes are the contractor's solution for going around the duct.
I don't think he's an electrician.
N
Nick Danger
Albuquerque
They re-routed. This is how it looks now.
He said that he used a 3-conductor splice for the hot, hot, and neutral wires. He used a 1-conductor splice for the ground wire.
N
Nick Danger
Albuquerque
The joys of being at work while someone is remodeling your house. My wife sent me the photo and is doing the face-to-face conversations.
PCustoms
VT
That looks like ****.
If he had to splice on both sides, he should have run a longer jumper and made it look neat.
Also perplexed by your description. Pretty sure the single NM-B (H,N, G) needs to go in 1 splice, and rhe splice should have proper terminals.
mm08822
I don't use those connectors I but thought they were only available for 2 conductor cable (2 conductors + grd).
If you are saying he used 2 connectors at each splice location for a 3 conductor cable - then it is just another hack job.
Also pic not too clear. I don't see 2 connectors on each end. It looks like 14-2 is used between connectors?? If so, where is the 3rd conductor?
N
Nick Danger
Albuquerque
I'm confused too.
A lot of the house is wired with three conductor cable. I thought that is what he said is there. But that's not what it looks like in the picture.
Bert_
NW Iowa
I would rather have a buried j box made up good and tight with wire nuts than those inline splices. I know the code allows them but I wouldn't feel good about using them.
Jazz1
Thunder Bay On.
You might get away burying junction boxes but in the event of a fire that box would void your insurance I would think.
rharman
SoCal
The question is whether the j boxes will be accessable after he’s finished.
Just so I'm clear on this...
If there is attic access, then you're OK with junction boxes in the attic space?
It's only an issue if they end up in an inaccessible space, correct?
This has nothing to do with me.
If the j boxes are accessible no matter where theyre at then its code permissible.
If theyre inaccessible then its an issue as you asked
rharman
SoCal
It was a "royal" "you're". Meaning the homeowner - not directed at you.
Thanks.