Was watching a youtube video this afternoon that someone sent to me to ask if it was correct. Starting at 4:40... Yes or no???

 
To avoid these ads, REGISTER NOW!

TRWham

Well-known member
Joined
Aug 11, 2017
Messages
1,961
Location
East Cobb County, Georgia
Yes. It's called a multi-wire branch circuit (MWBC). Perfectly acceptable, though I am skeptical it makes fiscal sense given the cost of 12/2 vs 12/3 cable.
 

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
The first example where he was wiring the 240 volt circuit is not a MWBC. There is no neutral, just 2 hots and a ground. He is just sharing one 240 volt circuit for two machines. I will say, I have never seen a NM-B cable with just a black, red and ground, it is still just a 12/2. The second example is a MWBC, since it has a neutral which carries the unbalanced load from two different 120 volt circuits from different legs. he used a 12/3 or 14/3
 
Last edited:

thammel

Well-known member
Joined
Oct 3, 2005
Messages
2,245
Location
Maryland
My house has a few MWBCs and I hate them. For one, you can't put arc fault or ground fault breakers on them. Just the cheap way of doing things. When I can, I run a separate wire and get rid of the MWBC.
 
To avoid these ads, REGISTER NOW!

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,765
The first example where he was wiring the 240 volt circuit is not a MWBC. There is no neutral, just 2 hots and a ground. He is just sharing one 240 volt circuit for two machines. I will say, I have never seen a NM-B cable with just a black, red and ground, it is still just a 12/2. The second example is a MWBC, since it has a neutral which carries the unbalanced load from two different 120 volt circuits from different legs. he used a 12/3 or 14/3

I have not watched the video but by chance is the poster from Canada? That product seems to be a Canadian thing.
 

frankush

Well-known member
Joined
Oct 23, 2011
Messages
1,156
Location
IL
The video is correct, at least at the 4:40 mark. He does not get twice as much juice at that point. All he gets is a separate circuit. A two wire circuit is one circuit. A three wire circuit, in this case provides for two circuits. MWBC's are the most common method of wiring, in anything other than residential wiring. The biggest problem you find with them is when neutrals from other MWBC's get wired where they don't belong.
 
Last edited:

exranger06

Well-known member
Joined
Aug 9, 2015
Messages
1,686
Location
CT
My house has a few MWBCs and I hate them. For one, you can't put arc fault or ground fault breakers on them. Just the cheap way of doing things. When I can, I run a separate wire and get rid of the MWBC.

You can use arc fault and ground fault breakers on MWBCs. You just have to use a double pole breaker.
 