what was the COO of the light hehehe
Technically a code violation, as the fixture only has UL approval when completely and properly assembled.
Charles
UL has NOTHING at all to do with code.)
So I can install a fixture in way that violates its UL listing and still comply with code?
Certainly shoddy and the connections are sposed to be in the covered raceway.
90-7 says that if a piece of equipment has been listed by a testing facility, it shall conform to code.
110-2 says the conductors and equipment required or permitted by this code shall be acceptable only if approved. the FPN refers to 90-7 and 110-3.
110-3 (b) installation and use. listed or labeled equipment shall be installed and used in accordance with any instructions included in the listing or labeling.
i know of nothing stating any equipment or luminare has to be listed by a testing facility, however if you chose to install a piece of equipment that is not listed, you are at the mercy of the AHJ who will often reject it.
Exactly. You don't have to have produce a UL certified product, nor do you have to install one (unless there is a local requirement for it).
OK. I was just purely curious. I have never seen that before anywhere. And the place the lady suggested we go eat was a cheap looking Chinese restaurant, LOL.