Kind of overkill for 2 wires.![]()
The table above is referencing "current carrying conductors". Be sure that you understand that the table above is for conduit or raceways, not open air or studs. The code is very specific and does not leave much room for interpretation.....

Be sure that you understand that the table above is for conduit or raceways, not open air or studs. The code is very specific and does not leave much room for interpretation.....
You are talking about deration, not fastening...
You need to make sure we are taking into account that 2 of the 3 wires in the cable are current carrying. But as far as the table, I wouldn't use it for deciding how many Romex wires I can fasten together...
Ok. It may go hand in hand, but one is different than the other. And the table above does not answer the op question, it tells what percentage to derate, therefore is not applicable to the question.
Is this ok? One staple for 2 nm
I've never had an inspector complain about 2 wires under a staple.
Are the staples listed for 2 pieces of NM? Most are from what I know but the inspector could be a **** and say show me
Nope,I'd tell him to show me where I can't do it.
I've been doing this a long time,inspectors don't get to make up rules with me.
I keep the chief electrical inspector/chief plumbing inspector and chief mechanical inspectors phone number on my phone for every town I do work in.
It is applicable. If more than 3 wires are bundled together they must be derated.
He is bundling 2 wires. Therefore it is ok-as-is.