JasonF
Well-known member
Was just hoping you guys could look over my plans to run service to my new pole building that is approx 200ft from my house.
Plan is to put a 100A sub panel in the new garage and feed it with #4 copper THHN wire buried in conduit. Power will be supplied from a 90A breaker inside my homes panel. I plan on running 4 wires (3) #4 & (1) #8 ground) inside 2" sched 40 conduit 18-24" underground along with a grounding rod at the garage. I then would like to bury the conduit in 6" of dirt and then run my Cat/5 wire in 1" conduit along with my natural gas service.
Does this look ok? I will be pulling a permit and contacting the local inspector, just want to sound like I know what I'm doing first.
Couple questions I have are:
Can my (3) #4 wires coming from the house all be black and then taped at the ends with colored tape?
Does the Sched 40 PVC need to run all the way to each electrical box or does it only have to feed wires into the wall of each structure were they then can be run without conduit?
Plan is to put a 100A sub panel in the new garage and feed it with #4 copper THHN wire buried in conduit. Power will be supplied from a 90A breaker inside my homes panel. I plan on running 4 wires (3) #4 & (1) #8 ground) inside 2" sched 40 conduit 18-24" underground along with a grounding rod at the garage. I then would like to bury the conduit in 6" of dirt and then run my Cat/5 wire in 1" conduit along with my natural gas service.
Does this look ok? I will be pulling a permit and contacting the local inspector, just want to sound like I know what I'm doing first.
Couple questions I have are:
Can my (3) #4 wires coming from the house all be black and then taped at the ends with colored tape?
Does the Sched 40 PVC need to run all the way to each electrical box or does it only have to feed wires into the wall of each structure were they then can be run without conduit?
Last edited:
Those conductors will pretty much walk themselves in.
, don't think I could do that with a clear conscience. Will probably do the electrical 2-3ft down with the gas at 18".