Is this up to code / done by professional installer

CHEBANSE

Well-known member
Joined
Feb 2, 2012
Messages
49
Location
Illinois
I just contracted my local plumbing and heater contractor to do the connections for my Beacon Morris 45K btu heater. Is this safe or proper for a house I plan on living in at least 20 years.

No exhaust T pipe

No gas line drip pipe

Flex Gas Line

Not shown electrical light in water heater closet falling out of drywall/ceiling because of electrical connections.

Thank you
 

Attachments

  • gas line and vent install 001.jpg
    gas line and vent install 001.jpg
    144 KB · Views: 527
  • gas line and vent install 004.jpg
    gas line and vent install 004.jpg
    128.8 KB · Views: 481
  • gas line and vent install 003.jpg
    gas line and vent install 003.jpg
    139.7 KB · Views: 499
Last edited:
To avoid these ads, REGISTER NOW!

NorthCountry

Banned
Joined
Apr 22, 2012
Messages
155
Location
WhiteHall NY
Here in NY there should be at least an 8" drip leg on any gas appliance and that hot water heart has no shut off to the appliance only the drip leg. And yes there should be a t on that chimney. Professional no up to code definatly no


Sent from my iPhone using Tapatalk - now Free
 
Joined
Aug 25, 2013
Messages
21
Location
NE Massachusetts
The gas comes up through the floor near the water heater, right? You defiantly can't use one shut off for 2 appliances, plus the things already mentioned. I don't know the codes in your area, but it isn't an acceptable professional installation.
 

mygarageone

Well-known member
Joined
Oct 16, 2013
Messages
2,691
Location
Munising , Mich
All gas equip is required to have drips legs. As far as the flex gas piping , it depends on your state or county code requirements.
You also mention the electric fixture , unless he's lic to do elec work , you have him there too.!
did he pull a permit ? I suspect not based on what I see.

There are no requirements for exhaust t's at least I haven't put on in for decades. They are no longer required unless you over size the B Vent and then the inspector would catch it. As the PP stated you can not use 1 shut off for 2 units.

The other thing I noticed , he used Teflon tape , we never use it anymore . Pipe dope only.
Reason , it gets into the gas controls and then you have bigger problems.
 
Last edited:

mygarageone

Well-known member
Joined
Oct 16, 2013
Messages
2,691
Location
Munising , Mich
Here in NY there should be at least an 8" drip leg on any gas appliance and that hot water heart has no shut off to the appliance only the drip leg. And yes there should be a t on that chimney. Professional no up to code definatly no


Sent from my iPhone using Tapatalk - now Free

The T serves no purpose , they were once used for clean outs which is pass a anymore.

But New York is a different situation.
 

mygarageone

Well-known member
Joined
Oct 16, 2013
Messages
2,691
Location
Munising , Mich
Why no drip tee or drain trap to catch the flue/exhaust condensation??[/QUOTE

Not required anymore . There was a big issue with condensation when furnaces were way over sized , like years ago but that's not the case anymore.
However I do see them installed on 80%

But they still are not required . but then the manufacture will call for one and then you have to have it . the manufactures now days determine whats happening with there equip.
 

NorthCountry

Banned
Joined
Apr 22, 2012
Messages
155
Location
WhiteHall NY
Mygarageone you are right up here in NY we have the gustapo watching over us which in my eyes keeps the Hacks out of the trades which keeps my per hour labor rate nice and comfy!!


Sent from my iPhone using Tapatalk - now Free
 

mygarageone

Well-known member
Joined
Oct 16, 2013
Messages
2,691
Location
Munising , Mich
Mygarageone you are right up here in NY we have the gustapo watching over us which in my eyes keeps the Hacks out of the trades which keeps my per hour labor rate nice and comfy!!


Sent from my iPhone using Tapatalk - now Free

Well Chicago is even worse , especially Cook country . They still require Cast Iron Pipe for most plumbing Jobs ! It's mostly to protect the unions . Not many people know anything about Cast Iron , nor have the tools to install it .
 

HoosierBuddy

Well-known member
Joined
May 9, 2006
Messages
2,918
Location
Southern Indiana
I don't see a bond wire. CSST is supposed to be electrically contiguous and bonded to the main electrical ground for the home. Since this wasn't done, it makes me wonder if the installer was properly certified by the pipe manufacturer to install the CSST in the first place. The installer should have documentation that he has been certified to use that brand of CSST.

In this case, I really would have wanted to see black pipe.

Phil
 

mygarageone

Well-known member
Joined
Oct 16, 2013
Messages
2,691
Location
Munising , Mich
I don't see a bond wire. CSST is supposed to be electrically contiguous and bonded to the main electrical ground for the home. Since this wasn't done, it makes me wonder if the installer was properly certified by the pipe manufacturer to install the CSST in the first place. The installer should have documentation that he has been certified to use that brand of CSST.

In this case, I really would have wanted to see black pipe.

Phil

The problem is you can buy this stuff at Menards , lowes, home depot , etc. with out any certs.
Looking at it , it looks like the box store stuff.
When we first started using this stuff , there was no grounding required and we did have to be certified by the manufacture. It has it's place but we mostly use it on very short connections were it would take lots of 90's or cutting and fitting and never concealed.
 
Last edited:

HoosierBuddy

Well-known member
Joined
May 9, 2006
Messages
2,918
Location
Southern Indiana
The problem is you can buy this stuff at Menards , lowes, home depot , etc. with out any certs.
Looking at it , it looks like the box store stuff.
When we first started using this stuff , there was no grounding required and we did have to be certified by the manufacture. It has it's place but we mostly use it on very short connections were it would take lots of 90's or cutting and fitting and never concealed.

Agree. My point is it impossible for someone that is not certified to install CSST properly according to the national fuel code...because the first requirement of the code is any CSST installer has to be certified. If they aren't, then it doesn't matter what the piping looks like...it doesn't meet code.

Phil
 

mygarageone

Well-known member
Joined
Oct 16, 2013
Messages
2,691
Location
Munising , Mich
Agree. My point is it impossible for someone that is not certified to install CSST properly according to the national fuel code...because the first requirement of the code is any CSST installer has to be certified. If they aren't, then it doesn't matter what the piping looks like...it doesn't meet code.

Phil

Well the home owner has an alternative , call the Mechanical Inspections dept for his state or county. They will get involved and make sure it complies with code.
 
To avoid these ads, REGISTER NOW!
OP
C

CHEBANSE

Well-known member
Joined
Feb 2, 2012
Messages
49
Location
Illinois
I finally got the HVAC guy to come back and upgrade per code. I was told that he did his and his dads garage the way he originally did mine. Appearently the exhaust T is not required today in my area.
 

Attachments

  • heat upgrade 001.jpg
    heat upgrade 001.jpg
    144.3 KB · Views: 212
  • heat upgrade 003.jpg
    heat upgrade 003.jpg
    126.8 KB · Views: 194
  • heat upgrade 002.jpg
    heat upgrade 002.jpg
    42.4 KB · Views: 379

NorthCountry

Banned
Joined
Apr 22, 2012
Messages
155
Location
WhiteHall NY
I finally got the HVAC guy to come back and upgrade per code. I was told that he did his and his dads garage the way he originally did mine. Appearently the exhaust T is not required today in my area.

Not to sound like a negative nancy but there is still no drip leg on the water heater! Sorry I have OCD!!! Looks a hell of alot better tho


Sent from my iPhone using Tapatalk - now Free
 
OP
C

CHEBANSE

Well-known member
Joined
Feb 2, 2012
Messages
49
Location
Illinois
I noticed that too. Also no shut off on the water heater. I am tired of fighting them. Definately will look elsewhere in the future.
 

mygarageone

Well-known member
Joined
Oct 16, 2013
Messages
2,691
Location
Munising , Mich
I noticed that too. Also no shut off on the water heater. I am tired of fighting them. Definately will look elsewhere in the future.

You do have a recourse , contact the local code authorities and they will make sure this is done proper and no cost to you. This guy could get his Hinny in big trouble for this.

Trust me , there would be no fighting after they get involved.
 

alpinewhite

Well-known member
Joined
Aug 4, 2012
Messages
1,315
Location
Orange County, California, USA
attachment.php
Here in (earthquake-zoned) California, we are required to have flex to the water heater.
 

mygarageone

Well-known member
Joined
Oct 16, 2013
Messages
2,691
Location
Munising , Mich
I saw that but technically you could isolate water hear with the two valves in place


Sent from my iPhone using Tapatalk - now Free

Every state is different , some require a shut off exclusively for the appliance . There may be a national code that they all follow but most times each state will add or delete things they want for there jurisdiction.
 

volaredon

Well-known member
Joined
Oct 7, 2012
Messages
1,617
Location
IL
Hey Chebanse... is your username based on the town you are in? In Illinois? If so youre <10 miles from me, and im the guy that had the rant about HVAC parts places not selling to anyone "not in the trade" I was able to get what I need just by asking from a place right in that town, if youre from there youre probably familiar with them.... hopefully these aren't the guys that did your install.
 

Walty

Member
Joined
Feb 18, 2011
Messages
19
Besides the other stuff, I would take a closer look at the exhaust vent for the heater. My beacon Morris 75k instructions say that the vent needs to go out a foot horizontal before going vertical.
 

charged355

Well-known member
Joined
Jan 27, 2011
Messages
171
Location
Cottage Grove, MN
Besides the other stuff, I would take a closer look at the exhaust vent for the heater. My beacon Morris 75k instructions say that the vent needs to go out a foot horizontal before going vertical.

I'm installing the a 75k beacon morris right now also. I believe that it just states you need a minimum of 1/4" slope per horizontal foot. No requirement of running any horizontal length. I think the 90 is just fine.
 

Walty

Member
Joined
Feb 18, 2011
Messages
19
Looked at the instructions again. Thought it was specifying a 1 foot horizontal run cause I saw the 5' vertical minimum, but after rereading, looks like your right.

Thanks, saves me some trouble.
 

ksj9393

Well-known member
Joined
Jul 5, 2011
Messages
162
Location
Minnesota
Not to sound like a negative nancy but there is still no drip leg on the water heater! Sorry I have OCD!!! Looks a hell of alot better tho


Sent from my iPhone using Tapatalk - now Free

Drip legs are an anachronism, from the bygone era of "manufactured gas" which was notoriously dirty. In most places today, natural gas is so clean as to render the drip leg obsolete. Yet, codes are slow to keep up, and in my estimation, left on the books way too long just to give nit-picky inspectors something to do. At least, that's how things have been for me. I put the drip leg on only after the inspector caught my "mistake".
 

CNGsaves

Well-known member
Joined
Sep 26, 2012
Messages
13,233
Location
KS and OK
Drip legs are ALWAYS a good idea as they not only catch crud in the gas flow like rust specs, but they also serve as water collection point.

Some areas of country have much wetter natural gas than others . . . . even though it's considered "pipeline quality" per se.

Guy in Ohio has his own NG compressor outside garage to fuel his bi-fuel vehicles, and his monopoly-provided NG from local gas company is so wet that it was damaging his expensive Fuelmaker NG compressor. He installed his own dessicant dryer and now has perfectly dry NG.

Do not skimp on drip legs . . . . they are cheap insurance.
 