I would like to run a new feeder for my house but I definitely don’t need 1/0 wire. I do have about 125 feet of this
 

Attachments

  • 94A8A522-1854-4A59-8A41-8E5BF3D98357.jpg
    94A8A522-1854-4A59-8A41-8E5BF3D98357.jpg
    111.1 KB · Views: 105
Last edited:
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,276
Location
Modesto, CA
I would like to run a new feeder for my house but I definitely don’t need 1/0 wire. I do have about 125 feet of this

That is probably URD. Not permitted for use indoors.

Is there an RHH or RHW writing on the wire?

Where does the current feeder run?

What is the size of the current feeder?
 
To avoid these ads, REGISTER NOW!
OP
G

gayler

Well-known member
Joined
Sep 22, 2011
Messages
3,291
Location
Lakin Kansas
That is probably URD. Not permitted for use indoors.

Is there an RHH or RHW writing on the wire?

Where does the current feeder run?

What is the size of the current feeder?

Not sure of RHH orRHW . I did see use-2. Current feeder comes off the main breaker on the pole next to the house, under the trailer house to the breaker box in the house. Not sure of the current feeder size , but it’s on a 100 amp breaker.
 