It would work- but is it permitted by code?

CoogarXR

Well-known member
Joined
Jan 11, 2016
Messages
6,858
Location
Ohio
At my new place, I have a small attached 1.5 car garage that has two 120v circuits fed by a 10/3. The 10/3 has a 30A 240v breaker in the house, and it terminates in the garage with a 2-slot breaker box with 2 15A branches for the garage interior.

Forgive me if this is a dumb idea, but I have a 240v submersible pump that I would like to run occasionally. Could I put a 240v outlet BEFORE the small subpabel? The 10/3 would go to the 240v socket first (still protected by the 30a breaker in the house), and then another piece of 10/3 would continue to the existing subpanel?

I'm not worried about overloading the line, the pump is only like 5A and the two 120v circuits have no existing load on them at all. Just empty receptacles and a few overhead LED lights.

I know it would work functionally, but is it allowed?
 
To avoid these ads, REGISTER NOW!

MovingAlong

Well-known member
Joined
Aug 17, 2013
Messages
1,227
Do you know who your AHJ (authority having jurisdiction) is? (City, county, etc..) Call and ask for the permit office, talk with an inspector about what you have planned. They'll let you know. :thumbup:
 

dcg9381

Well-known member
Joined
Jun 20, 2018
Messages
11,778
Location
Austin, TX
Can you do this with only a 10/3 feed?
Sure you can feed a sub panel with 30A and outputs might be more than the sum of the upstream breaker.

I do not think you can "branch" a 30A @ 240V feed. Nor are 240V outlets made for input/output.
 

larry_g

Well-known member
Joined
Apr 28, 2007
Messages
16,885
Location
oregon
Alrighty then, looks like I'll just buy a bigger panel (like a 6/8 slot or so) and just add a breaker for the 240v outlet.

Thanks dudes.
It seems to me I remember that a 6 slot does not require a master breaker but more than 6 does? Check me on this.

lg
no neat sig line
 

The Cobbler

Super Moderator
Staff member
Joined
Oct 24, 2013
Messages
25,920
Location
Niagara Region, Ontario, Canada
It seems to me I remember that a 6 slot does not require a master breaker but more than 6 does? Check me on this.

lg
no neat sig line
if that's required, he can always use the 2 slot existing box and install a 30 amp breaker . in fact without knowing the situation, it may be easier to leave it in and add a panel to that. ( and maybe not a bad idea in any event)
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,025
Location
Modesto, CA
At my new place, I have a small attached 1.5 car garage that has two 120v circuits fed by a 10/3. The 10/3 has a 30A 240v breaker in the house, and it terminates in the garage with a 2-slot breaker box with 2 15A branches for the garage interior.

Forgive me if this is a dumb idea, but I have a 240v submersible pump that I would like to run occasionally. Could I put a 240v outlet BEFORE the small subpabel? The 10/3 would go to the 240v socket first (still protected by the 30a breaker in the house), and then another piece of 10/3 would continue to the existing subpanel?

I'm not worried about overloading the line, the pump is only like 5A and the two 120v circuits have no existing load on them at all. Just empty receptacles and a few overhead LED lights.

I know it would work functionally, but is it allowed?
why not just swap in a larger subpanel instead of running the current thru the junction box of the receptacle? more points of failure instead of less

that pump may also need to be protected by a breaker smaller than 30a
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,025
Location
Modesto, CA
Sure you can feed a sub panel with 30A and outputs might be more than the sum of the upstream breaker.

I do not think you can "branch" a 30A @ 240V feed. Nor are 240V outlets made for input/output.
there is no prohibition on that and the 240v receptacle would not only not have a way to connect more than 1 wire per terminal but #10 probably wont fit either, so he would have to splice it all in a j box. solid #10 is not fun to work with or splice in a small j box either
 
Last edited:
To avoid these ads, REGISTER NOW!

dcg9381

Well-known member
Joined
Jun 20, 2018
Messages
11,778
Location
Austin, TX
there is no prohibition on that and the 240v receptacle would not have a way to connect more than 1 wire per terminal so he would have to splice it all in a j box. solid #10 is not fun to work with or splice in a small j box
Thanks.. I think I was confusing branching at the out.
 

AA/FC

Well-known member
Joined
Dec 9, 2010
Messages
2,080
My local city electrical inspector told me that he actually enjoys it when home owners call and ask for advice. He said that is part of his job.... He also said it's a different story for electrical contractors, they are supposed to already know the answers.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,025
Location
Modesto, CA
My local city electrical inspector told me that he actually enjoys it when home owners call and ask for advice. He said that is part of his job.... He also said it's a different story for electrical contractors, they are supposed to already know the answers.
that is rare
 

driftpin

Well-known member
Joined
Dec 22, 2016
Messages
11,268
Location
Miami-Dade/Broward Co. Florida
My local city electrical inspector told me that he actually enjoys it when home owners call and ask for advice. He said that is part of his job.... He also said it's a different story for electrical contractors, they are supposed to already know the answers.
I think that is dependent on the workload of the plans examiner.

If they're short staffed and under pressure to reduce the size of the backlog of permits for review then they probably are not going to be teaching the code to a novice. In the jurisdiction of where I worked if something failed twice for the same reason the qualifier would be required to come in and sit with the Chief Inspector for that discipline and possibly the Chief Building official. They would review the plans and settle any issues so that the person pulling the permit would know what direction they needed to go.
 

Jimmyrace

Member
Joined
Oct 28, 2024
Messages
12
It seems to me I remember that a 6 slot does not require a master breaker but more than 6 does? Check me on this.

lg
no neat sig line
quite actually, if it is more of a separate building issue than the size of the panel - if it is a seperate bldng. then it should have a local "disconnect", which could just be another 2p/30A breaker in the panel (backfed), which technically should be held down w/ a screw-kit, but in some instances i think you can zip-tie that breaker in place if no set.screw location exists ... and i have not seen any 30A breakers w/ a hole for that set-up anyway.
 

Jimmyrace

Member
Joined
Oct 28, 2024
Messages
12
please ignore my replies - everybody already answered your Q's ... guess i should read the whole thread before replying next time lol.

Lotta Good Knowledge here! - Take Care Y'all !
 

AA/FC

Well-known member
Joined
Dec 9, 2010
Messages
2,080
that is rare
Yeah, not every electrical inspector is an *******. This particular city inspector was also one of the electrical instructors at the local tech college for 18 years. He enjoys explaining things to people who ask questions.
 