ForceFed70
Well-known member
I've still got it UPDATE - Furnace broke again!
Came home today to the wife saying it's cold in the house and the furnace isn't turning on. She had the thermostat cranked but it was only 60* inside
Checked the basic's (breaker, cycled power on/off, turned thermostat on/off) but nothing. Couldn't even get the fan to run in "fan only" mode. So I bust out the DMM and the tools and start pulling the access panels off. Furnace is 20 years old.
I have no HVAC repair knowledge. I went to college 12 years ago for Electronics Engineering Technology however I've been employed with computers ever since I graduated and have forgoten a lot of what I learnt.
I noted that when power was applied to the furnace nothing really happened. I could hear 1 relay "click" but that was all that would happen.
1st I checked that power was making it's way into the mainboard - OK
2nd I checked that the Transformer was working and got 27VAC according to the DMM - OK
I didn't really know where to go from there so I started studying the diagrams on the back of the service panel:
- I noticed that the relay I heard clicking was the fan relay. But the fan wasn't turning on. So I measured voltage to the blower/fan. Nothing. So I thought maybe the relay was bad. Spent a bunch of time looking at the relay and wishing it wasn't soldered to the control board only to realize that it's marked NC (Normally Closed) the clicking I heard was the contacts opening to prevent operation of the fan... so not likely the relay.
- After a bunch more poking around, I was about to give up and call a professional when I decided that it seemed like the furnace wasn't even trying to light. That made me wonder about the thermostat. I had ignored the thermostat earlier because I couldn'd even get the fan to run but decided to take another look. Then I noticed that there was no wire on the thermostat terminal for "fan only" it would never have worked. I measured voltage across the R and W terminals and it said 24V... according to the diagram this connection should be closed when the thermostat is calling for heat which would mean I should be measuring 0 volts. So I put a jumper between the terminals and powered up the furnace. VOILA... she lit up right away.
I'll pick up a new thermostat tomorrow.
A pro probably would have diagnosed this problem in just a couple of minutes, but I'm still proud of myself for figuring it out.
Came home today to the wife saying it's cold in the house and the furnace isn't turning on. She had the thermostat cranked but it was only 60* inside
Checked the basic's (breaker, cycled power on/off, turned thermostat on/off) but nothing. Couldn't even get the fan to run in "fan only" mode. So I bust out the DMM and the tools and start pulling the access panels off. Furnace is 20 years old.
I have no HVAC repair knowledge. I went to college 12 years ago for Electronics Engineering Technology however I've been employed with computers ever since I graduated and have forgoten a lot of what I learnt.
I noted that when power was applied to the furnace nothing really happened. I could hear 1 relay "click" but that was all that would happen.
1st I checked that power was making it's way into the mainboard - OK
2nd I checked that the Transformer was working and got 27VAC according to the DMM - OK
I didn't really know where to go from there so I started studying the diagrams on the back of the service panel:
- I noticed that the relay I heard clicking was the fan relay. But the fan wasn't turning on. So I measured voltage to the blower/fan. Nothing. So I thought maybe the relay was bad. Spent a bunch of time looking at the relay and wishing it wasn't soldered to the control board only to realize that it's marked NC (Normally Closed) the clicking I heard was the contacts opening to prevent operation of the fan... so not likely the relay.
- After a bunch more poking around, I was about to give up and call a professional when I decided that it seemed like the furnace wasn't even trying to light. That made me wonder about the thermostat. I had ignored the thermostat earlier because I couldn'd even get the fan to run but decided to take another look. Then I noticed that there was no wire on the thermostat terminal for "fan only" it would never have worked. I measured voltage across the R and W terminals and it said 24V... according to the diagram this connection should be closed when the thermostat is calling for heat which would mean I should be measuring 0 volts. So I put a jumper between the terminals and powered up the furnace. VOILA... she lit up right away.
I'll pick up a new thermostat tomorrow.
A pro probably would have diagnosed this problem in just a couple of minutes, but I'm still proud of myself for figuring it out.
Last edited: