I'm putting in a 100 amp sub panel to free up space in my main panel (kitchen is all electric)
What I have right now:
200A Main panel -> 2" FMC -> 16"x16"x4" box in the crawl space
What I would like to do for the feed is run 1G wire from the main to the 16" box, run 1.5" FMC from the 16" box to the subpanel
For all the appliance feeds (currently in 1/2" or 3/4" FMC conduits to main panel) I want to run 2" FMC from the sub panel to a pull box directly under it (in the crawl space) than tie in all the appliances to the new pull box to feed up to the sub panel. This way I can move over each appliance as time allows and have room for expansion later on that is easy to add.
What size does the new pull box need to be? I was thinking about using a 6"x6"x12" raceway box, but I would need to run the 2" FMC conduit to the 6"x6" face to allow for the 8x conduit size straight section. But since the pull box can be mounted directly under the sub panel, I think it would be cleaner/neater to mount the box directly under the sub panel and avoid a bend in the conduit, but than I only have a 6" straight section in front of the 2" conduit fittings. Is that ok since I am only running max size 6G wire in the 2" FMC?
www.mcmaster.com
Edit:
So I just learned about derating wires when multiple current carrying conductors are in the same conduit so my plan to run everything through a 2" up to the sub panel may not work without upsizing every wire due to needing to be derated to 45-50% according to table 310.15(B)(3)(a)
Now my concern falls on the 2" from the main to the existing 16"x16" box, which will have (All THHN):
Table 310.15(B)(16)
2 6G on a 50A Breaker, wire run is ~40'
3 4G on a 70A Breaker, wire run is ~55'
3 1G on a 100A Breaker, wire run is ~20'
1 8G Ground
That's 8 CCCs that will need to be derated to 70%
6G rated for 75A derates to 52.5A
4G rated for 95A derates to 66.5A
1G rated for 145A derates to 101.5A
So everything is good except the 4G on the 70amp breaker, it will need to be either upsized to 3G or a 60A breaker installed
Does my math check out or is there anything else I'm missing?
What I have right now:
200A Main panel -> 2" FMC -> 16"x16"x4" box in the crawl space
What I would like to do for the feed is run 1G wire from the main to the 16" box, run 1.5" FMC from the 16" box to the subpanel
For all the appliance feeds (currently in 1/2" or 3/4" FMC conduits to main panel) I want to run 2" FMC from the sub panel to a pull box directly under it (in the crawl space) than tie in all the appliances to the new pull box to feed up to the sub panel. This way I can move over each appliance as time allows and have room for expansion later on that is easy to add.
What size does the new pull box need to be? I was thinking about using a 6"x6"x12" raceway box, but I would need to run the 2" FMC conduit to the 6"x6" face to allow for the 8x conduit size straight section. But since the pull box can be mounted directly under the sub panel, I think it would be cleaner/neater to mount the box directly under the sub panel and avoid a bend in the conduit, but than I only have a 6" straight section in front of the 2" conduit fittings. Is that ok since I am only running max size 6G wire in the 2" FMC?
McMaster-Carr
McMaster-Carr is the complete source for your plant with over 595,000 products. 98% of products ordered ship from stock and deliver same or next day.
Edit:
So I just learned about derating wires when multiple current carrying conductors are in the same conduit so my plan to run everything through a 2" up to the sub panel may not work without upsizing every wire due to needing to be derated to 45-50% according to table 310.15(B)(3)(a)
Now my concern falls on the 2" from the main to the existing 16"x16" box, which will have (All THHN):
Table 310.15(B)(16)
2 6G on a 50A Breaker, wire run is ~40'
3 4G on a 70A Breaker, wire run is ~55'
3 1G on a 100A Breaker, wire run is ~20'
1 8G Ground
That's 8 CCCs that will need to be derated to 70%
6G rated for 75A derates to 52.5A
4G rated for 95A derates to 66.5A
1G rated for 145A derates to 101.5A
So everything is good except the 4G on the 70amp breaker, it will need to be either upsized to 3G or a 60A breaker installed
Does my math check out or is there anything else I'm missing?
Attachments
Last edited: