I bought a used 15" Jet planer today, I tried the unit out and it works great. I got home and downloaded the manual and it says it should be connected to a dedicated minimum 30 amp circuit. The cord, which looks like it came with the unit, has a 20 amp 240 volt plug and is 12-3. I am going to run a dedicated 30 amp circuit and put a 30 amp plug on, but, do I need to replace the cord?

I'm going to build a different base for it, I just built the dolly to get it off the trailer.

Thanks
 

Attachments

  • planer.jpg
    planer.jpg
    136.5 KB · Views: 58
  • planerplug.jpg
    planerplug.jpg
    129.5 KB · Views: 44
To avoid these ads, REGISTER NOW!
OP
D

dfiler2

Well-known member
Joined
Dec 15, 2014
Messages
2,858
Location
NW Minnesota
This is what has me confused, I'm almost certain the unit came with a 12-3 cord. The grommets/strain reliefs are specific to the cord and it doesn't make sense that someone would change it to something lighter. I assume that if it's on a 30 amp circuit as the manual suggests, it should be 10-3, right?
 

404

Well-known member
Joined
Aug 23, 2014
Messages
3,463
Location
Mass
The breaker size protects the wire in the building, not what is plugged into it.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
If the manual says 30A circuit doesn't necessarily mean that the planer came with a #10 cord. But it will need a 30A rated plug on the cord if you put it on a 30A circuit. You are not to put a 20A outlet on a 30A circuit to use the existing 20A plug that's on the cord. If the cord is getting really warm to the touch when using the planer then up it to a #10 for the peace of mind.

Edit: I looked at a couple of manuals and it appears that the cord comes installed on the planer and you need to add the correct plug if a plug is used. In this case it's a 6-30P.


*
 
Last edited:
OP
D

dfiler2

Well-known member
Joined
Dec 15, 2014
Messages
2,858
Location
NW Minnesota
Right, I would not use the plug that's on the machine on a 30 amp circuit, my question was can I use the 12-3 cord and it sounds like if it does not get warm I should be ok.

Thanks
 

shoot summ

Well-known member
Joined
Jun 8, 2010
Messages
2,959
In the manual I found for the 15" planer there is a table that shows for 30a you should be using 10ga cord...
 
To avoid these ads, REGISTER NOW!
OP
D

dfiler2

Well-known member
Joined
Dec 15, 2014
Messages
2,858
Location
NW Minnesota
hmm... I've got the manual for the machine I have and there is no table, do you have a link to what you found, thanks.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
In the manual I found for the 15" planer there is a table that shows for 30a you should be using 10ga cord...

That table is for extension cords, not the installed cord on the planer.


I'm looking at manual for newer 15" Jet planer on the Jet site.


*
 
Last edited:

simpler=better

Well-known member
Joined
Oct 6, 2015
Messages
499
Location
Baltimore, Maryland
You're probably fine.

My best guess: They tell you to run a 30A circuit so that the 20A planer won't be using 100% of a 20A circuit when in use, it will be using 66% of a 30A circuit when in use.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
It came with the 12 cord. I believe it has its own thermal.
The breaker size protects the wire in the building, not what is plugged into it.
Yes and no and sort of. The cord needs to be adequate for the load and sized for short circuit protection to 30A. There is a limit the machine can be plugged on to.
 