Can I use this box and distribution block to lengthen a three phase run? This will power my air compressor. 8 ga wire.
 

Attachments

  • 20220504_132647.jpg
    20220504_132647.jpg
    318.5 KB · Views: 47
  • 20220504_132720.jpg
    20220504_132720.jpg
    246.2 KB · Views: 44
  • 20220504_132744.jpg
    20220504_132744.jpg
    334.6 KB · Views: 41
Last edited:
To avoid these ads, REGISTER NOW!
To avoid these ads, REGISTER NOW!
OP
9

930dreamer

Super Moderator
Staff member
Joined
Oct 7, 2009
Messages
23,088
Location
Amarillo,TX and Stinnett,TX
What about using a surplus ITE three phase panel, digging electrical items out of deep storage.
 

Attachments

  • 20220504_164704.jpg
    20220504_164704.jpg
    356.6 KB · Views: 27
  • 20220504_164750.jpg
    20220504_164750.jpg
    343.4 KB · Views: 22
  • 20220504_164808.jpg
    20220504_164808.jpg
    383.6 KB · Views: 30

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,792
What about using a surplus ITE three phase panel, digging electrical items out of deep storage.
If you need breakers, better consider wearing a adult brief, :D before looking at the prices, E2,E4,E6 breakers are not cheap, & would be more economical if were BQ, or BL, breakers. The ITE brand was discarded quite a while ago, in favor of Siemens.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,250
Location
Modesto, CA
oh this is a 3Ø motor? why are you using #8 wire? thats way overkill

FLC for 230v 5HP 3Ø motor is 15.2a which means 19a rated wire. so you really only need #14 THWN in pipe.

Also, why bother adding a point of failure to the mix? if the wires are too short, just run some new ones. but if you must, just use wire nuts in a j box. not sure why you want to throw a breaker panel in the mix

also if this is further than 50' form and not within sight of the breaker panel, then you will need a local disconnect
 
OP
9

930dreamer

Super Moderator
Staff member
Joined
Oct 7, 2009
Messages
23,088
Location
Amarillo,TX and Stinnett,TX
oh this is a 3Ø motor? why are you using #8 wire? thats way overkill

FLC for 230v 5HP 3Ø motor is 15.2a which means 19a rated wire. so you really only need #14 THWN in pipe.

Also, why bother adding a point of failure to the mix? if the wires are too short, just run some new ones. but if you must, just use wire nuts in a j box. not sure why you want to throw a breaker panel in the mix

also if this is further than 50' form and not within sight of the breaker panel, then you will need a local disconnect
I had/have multiple spools of 8ga wire so that's what I used. I'm reusing wire/conduit that I had from my old shop powering the same machines.