Hi all,

So I am mounting a NEMA 3R enclosure on the outside of my attached garage.
This is where my main power 2/0 aluminum XHHW from the detached will transition to 1/0 copper to go to my panels, which are on the other side of the wall (behind the meter box). This is in the 2.5" conduit.
The other 2 conduits are for future plans (screen porch and possible pool). The thought is to put them in the trench and under the house in the crawlspace so I don't have to dig this area up again.
My inspector said to transition to 1/0 copper SER in the enclosure and run that into the panel. (I will be cutting a section of drywall out in the garage to run the wire). The plan is to use some polaris connectors in the enclosure.

My questions:
Is there a minimum/maximum height from the ground of the enclosure?

Are there spacing requirements of the holes for the conduits coming up from the ground?

Are there any spacing/size requirements of the holes in the back that will go to the panel? Any special fittings required?

Thanks!
 

Attachments

  • enclosure wall.jpg
    enclosure wall.jpg
    150.4 KB · Views: 50
To avoid these ads, REGISTER NOW!
OP
J

jpcjguy

Well-known member
Joined
Jan 6, 2014
Messages
1,486
Location
Richmond, VA
I am using 2/0 aluminum to the junction box from the detached garage. The 125A breaker will only fit a 1/0 wire. So I am transitioning to SER to run in the walls, and was recommended to transition to copper in 1/0 to keep the same "size rating" as the 2/0 aluminum XHHW...
 
OP
J

jpcjguy

Well-known member
Joined
Jan 6, 2014
Messages
1,486
Location
Richmond, VA
How far is the short wire? The reason its upsized is for distance, its less of an issue on short sections.

3-5 feet range. See the attached pics. The new junction box will go where the current phone line box is. The inside panels are on the other side of the meter.
 

Attachments

  • meter-outside.jpg
    meter-outside.jpg
    116.1 KB · Views: 18
  • panel-inside.jpg
    panel-inside.jpg
    71.1 KB · Views: 19
To avoid these ads, REGISTER NOW!

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,920
Location
NW Iowa
What size are the other conduits? Just the 2.5" conduit it's going to require a pretty large box. I think 18"x18" is the closest common size that is large enough.

Can you come right into the back of the panel and eliminate the pull box?
I don't think I've seen a 125A breaker that doesn't take 2/0.
 
Last edited:
OP
J

jpcjguy

Well-known member
Joined
Jan 6, 2014
Messages
1,486
Location
Richmond, VA
What size are the other conduits? Just the 2.5" conduit it's going to require a pretty large box. I think 18"x18" is the closest common size that is large enough.

Can you come right into the back of the panel and eliminate the pull box?
I don't think I've seen a 125A breaker that doesn't take 2/0.

Inspector told me 18x18x6 box. Sticker right on the side of the 125A breaker says "1/0 MAX"
 
OP
J

jpcjguy

Well-known member
Joined
Jan 6, 2014
Messages
1,486
Location
Richmond, VA
So I am ready to mount the box. There will be the following conduit going to it:
2.5"
2"
1"

In the picture, the yellow line is the bottom of the panels inside. I was planning on mounting the junction box so the top is a couple inches below that line.
This way when I go out the back of the box, I make a right turn and then I am under the panels and go up.

As you can see there will be two 90 degree turns up to the junction box. I will be pulling the wire from the garage. Should I assemble all the PVC and pull the wire all the way? or should I pull the wire to the first 90 (corner of the building) and then assemble the last 5 feet or so over the wire?
I am hoping that three 2/0 and one #4 (aluminum XHHW) should not be too bad to pull in 2.5" conduit....
Looking for any tips, suggestions! Never pulled this size wire 215 feet before!
 