Junction box sanity check
Don1357
Palmer, AK
This weekend I'm running two wires to the upstairs of the garage, one for lights, one for outlets. The lights will be on 14 to supply the 3 or so amps for the 40 Watt LED 4' lights will draw. The outlets are 12 wire for 15 amp outlets.
The plan is to run the two wires to a 4" junction box from where the wire for the light is just spliced out, the one for the outlets is spliced into two branches to go left and right. According to what I could research the box is big enough for this? And that there are no problems having the two different wires, which I plan on clearly labeling?
Bonus question: Is it ok to just tie the ground wires together or do they need to keep separate grounds? The plan is to keep them separated but I'm just curious if it is kosher to just merge them.
exranger06
CT
It is impossible to say if the box is big enough or not without knowing the actual volume of it. 4" square boxes are available in many different depths, and therefore many different volumes. Each #14 wire takes 2 cubic inches of volume and each #12 wire takes 2.25 cu in of volume. All of the ground wires count as just one wire, so just add up the volume of all of the hot legs and neutrals, and add another 2.25 for all of the grounds (since #12 is the biggest ground wire, you use the volume of a #12 wire). You just need to make sure the total volume of all conductors doesn't exceed the volume of the box.
Yes, it is perfectly fine to have two different circuits and/or two different gauge wires in the same box.
Code actually REQUIRES you to tie all ground wires together, even when they're on different circuits. And if this is a metal box, don't forget to install a #12 bonding jumper to the box and tie that in to all of the ground wires.
D
Don1357
Palmer, AK
even at an inch deep that's 16 square inches, so I would be stuffing at worst 6.25 square inches. Heck my box is 2 inches deep, I cannot imagine putting enough cables there to take up the full allowance.
Thank you for taking the time to respond, most appreciated.
exranger06
CT
No, you're not calculating properly. When you take two wires and splice them together with a wire nut, that counts as TWO wires. You said you're taking three #12 cables and splicing them all together, and splicing two #14 cables together. Each cable has a hot leg and a neutral, so you have a total of six #12 wires, and four #14 wires. Then you add in one more #12 wire for the ground wires, so basically seven #12s and four #14s. That comes out to (2.25 x 7) + (2.0 x 4) = 23.75 cu in.
u2slow
BC
IMHO, do a lighting JB, and another JB for receptacles.
75gmck25
Alexandria, VA
Using two junction boxes makes it easier in the future when you want to add one more receptacle or one more light. And that 2nd junction box probably only costs less than $5, so its not a cost consideration. Unless you have a space issue (nowhere to put the 2nd box), I don't understand why you would not use two.
Bruce
D
Don1357
Palmer, AK
Thank you! I would have never caught that if I didn't bring it up!
I love being proved wrong, it guarantees I learn something :D
Bruce
Oh, trust me; I'm putting an obnoxious number of outlets from the get go, and that doesn't even count all the other receptacles dedicated to machines that will be running from the breaker box. If by any chance I were to need another outlet I would run it from the nearest existing outlet, not this box.
Same thing with the lights; these are for the overhead lights, a total of 8 x 4' LED lights. If I needed to add another set of 4 they would run off the existing wiring coming out of the box. I see it as a safety thing not to share the wiring for the shop lights with anything else; the last thing you want is to be working on a hand-eating machine and have the lights go out because somebody else tripped something.
Skiff Builder
Southern NJ Coast
Live it up ( if you have the space). Get 2 each of these, pleasure to splice in with all the room.
I use thes for my outlets too- just add a mud ring.
M-Petrik
Attached to my home
Why are you over sizing your wire for the 15a receptacles? You only need #14 for 15a.
sparky 1971
Central Iowa
15 amp receptacles can be installed on a 20 amp circuit. He does not state that is what he's doing, but it's more than likely what is happening.
OP, if you haven't done the project already, I would suggest just using a regular 4X4 box with an extension box on it.