Just got a mig welder, need some help

automotive stud

Well-known member
Joined
Apr 3, 2006
Messages
83
Location
NJ
I just got a new millermatic 180, it's 230v, and I have two garages I would like to use it in. Both garages have a 220 outlet for the air compressors that are in them. One is even on it's own breaker. But neither plug matches the plug on my new welder. What do I need to do to get it working safely and correctly?
 
To avoid these ads, REGISTER NOW!

Red Green

Well-known member
Joined
Dec 5, 2007
Messages
1,905
Location
South Central Michigan
Are the plugs in each shop the same? if so I would just make an extension cord with a female end that matches your welded and and the male end that matches you plugs.
 
OP
A

automotive stud

Well-known member
Joined
Apr 3, 2006
Messages
83
Location
NJ
I thought of that, but is it safe? I assume if I used heavy enough cable it would be. Where would I get the ends?
 

DuckusCrapus

Member
Joined
Jan 23, 2008
Messages
7
Location
Claremore, OK
A standard 220 household outlet is something like what you would find on an electric clothes dryer. It is rated at 30 amps. The plug on your welder is mot likley a 50 amp plug. You can run an adapter like mentioned above, but for your welder to work at it's full potential. I would add a proper plug in with the right breaker. You can get all this stuff at a local hardware store and be up and running for less than $50.


I did this with my welder and have never had a problem.



DuckusCrapus
 

Slonaker

Active member
Joined
May 30, 2006
Messages
40
Location
Marion, TX
The guys on the welding boards like the 50 foot ($50) and 100 foot ($97) 10/3 120v extension cords sold by Lowes and Home Depot. They just cut the ends off and replace them with the appropriate 240v plugs. Another popular one is the 30 foot ($30) RV extension cord sold by Wal-Mart. I have priced the bulk wire at Lowes and HD, and the extension cords are cheaper.

In the link below, they say that a 12/3 is sufficient for a Hobart Handler 187. IT might work for yours as well. I have an HH 187, and plan to go with a 50 foot 10/3 extension cord in the next few days.

http://www.hobartwelders.com/weldtalk/showthread.php?t=28725

Slonaker
 
OP
A

automotive stud

Well-known member
Joined
Apr 3, 2006
Messages
83
Location
NJ
that's a good idea guys. I don't recall what breaker is in the shops right now, but I remember they were pretty hefty knowing there would be a welder in the future. I know the compressor is 30, and the welder draws about 21.5 in operation, so I think that should be fine.
 
To avoid these ads, REGISTER NOW!

MXtras

Well-known member
Joined
Aug 17, 2005
Messages
1,356
Location
On the Right Coast
You would be fine on a 25A breaker.

Here's the spec sheet on your machine - just for others to reference:
http://www.millerwelds.com/pdf/spec_sheets/DC12-44.pdf

What does the receptacle on the wall look like? Does it have three or four prongs?

If it has three prongs, you are fine. If four, you have to use caution - four prong plugs have a neutral which will not be used for your welder. If it's for a dryer, it's likely three prongs, but I thought I'd ask.

Scott
 
OP
A

automotive stud

Well-known member
Joined
Apr 3, 2006
Messages
83
Location
NJ
You would be fine on a 25A breaker.

Here's the spec sheet on your machine - just for others to reference:
http://www.millerwelds.com/pdf/spec_sheets/DC12-44.pdf

What does the receptacle on the wall look like? Does it have three or four prongs?

If it has three prongs, you are fine. If four, you have to use caution - four prong plugs have a neutral which will not be used for your welder. If it's for a dryer, it's likely three prongs, but I thought I'd ask.

Scott

Both my shop and the welder have a 3 prong plug. The shop has one horizontal plug and one verticle, although one takes both. The one on the welder looks like an overgrown 120 plug. Is there an adapter that would plug right into the wall maybe?
 

dxdexter

Well-known member
Joined
Aug 1, 2006
Messages
1,923
I have the older Millermatic 175 version (essentially the same machine) for the last three years. I replaced the standard 220V welder plug with a Leviton 220V twist lock type plug (20Amp).The plug and receptacle is redly available from most hardware stores. The receptacle is fed from a 20Amp breaker. I have never once tripped the breaker and frequently use the machine at its greatest output.

Prior to replacing the standard plug with twist lock , I called the seller (Air Liquide Canada) and they inturn contacted the Miller rep who stated the warranty would not be violated. I suggest you do the same if you intend to alter anything within the warranty period.
 