Klein receptacle tester

mmelton005

Well-known member
Joined
Dec 16, 2014
Messages
245
Location
West KY
I had finished up installing new receptacles and I was using a klein RT210 tester to go over everything and accidentally hit the "test GFI" button on a non GFI receptacle. Now none of the receptacles in that circuit are working and did not trip the breaker. I've tried resetting the breaker and nothing....any ideas? :headscrat
 
To avoid these ads, REGISTER NOW!

Crazyjake8493

Well-known member
Joined
Sep 26, 2014
Messages
3,977
Location
Upstate NY
The outlet you tested has to be fed by either a GFCI outlet or breaker that you tripped with the reset button. Since you already checked the breaker, there has to be a GFCI outlet upstream somewhere.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,067
Location
Modesto, CA
Ive never investigated the circuitry in my GFCI outlet tester but it will NOT do anything when i push the test button while it is plugged into a circuit that doesnt have a GFCI.

The button doesnt work essentially.

If i plug it into a GFCI circuit or outlet then the test button works..

Would be interesting to know what kind of sensing circuitry it has...
 

malibu101

Well-known member
Joined
Jul 1, 2005
Messages
3,908
Location
Walnutport PA
Ive never investigated the circuitry in my GFCI outlet tester but it will NOT do anything when i push the test button while it is plugged into a circuit that doesnt have a GFCI.

The button doesnt work essentially.

If i plug it into a GFCI circuit or outlet then the test button works..

Would be interesting to know what kind of sensing circuitry it has...

I do not know their internals either.
I'm sure you know that touching ground and neutral together on the load side of the GFI will trip it.
I assumed these testers did that but I have no idea.

Gee thanks. Something else for me to wonder about. :lol_hitti

EDIT- When I plug my Ideal 61-051 into a proper wired non-GFI outlet and press the test button, the lights turn to show as "open ground".
I get no continuity between any combination of prongs no matter if the button is pushed or not.
There must be a mystery circuit in there.
 
Last edited:

JD3020

Well-known member
Joined
May 11, 2016
Messages
91
Location
Dayton, Ohio
Definitely poke around for a GFI. I run into it all the time with lawn irrigation systems and water features/outdoor lights on systems we didn't install. Outlets upstairs will be fed off a GFI downstairs, outlets in the garage or outside fed by a GFI in the basement or a bathroom, etc... Always fun playing "electrician" trying to find a hidden outlet just so i can do my job because somebody else didn't do theres. Labels are important. :thumbup:
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,067
Location
Modesto, CA
I do not know their internals either.
I'm sure you know that touching ground and neutral together on the load side of the GFI will trip it.
I assumed these testers did that but I have no idea.

Gee thanks. Something else for me to wonder about. :lol_hitti

EDIT- When I plug my Ideal 61-051 into a proper wired non-GFI outlet and press the test button, the lights turn to show as "open ground".
I get no continuity between any combination of prongs no matter if the button is pushed or not.
There must be a mystery circuit in there.

lol

yes touching neutral to ground will trip GFCI. The tester either shorts neutral to ground or hot to ground.

EDIT: It just dawned on me that it must short neutral to ground thats why there are no sparks or tripped breakers on non- GFCI circuit.
 

mrjaw14

Well-known member
Joined
May 22, 2012
Messages
1,958
Location
Nashville, TN
maybe there's an internal resistor that protects against sudden amperage flow? Small enough so that the GFCi knows it's there, but large enough so as not to give you a pretty lights show when you press the button?
 
To avoid these ads, REGISTER NOW!

ishiboo

Well-known member
Joined
Oct 27, 2010
Messages
9,481
Location
Oshkosh, WI
lol

yes touching neutral to ground will trip GFCI. The tester either shorts neutral to ground or hot to ground.

EDIT: It just dawned on me that it must short neutral to ground thats why there are no sparks or tripped breakers on non- GFCI circuit.

It's likely just a switch and a current-limiting resistor (perhaps a thermistor too to prevent you from cooking it by holding in the button) which would send X mA to ground.

It would short hot to ground, not neutral... neutral and ground are at the same potential... you couldn't test it that way. (I suppose it would trip IF there was a load on the GFCI-protected circuit AND the path of least resistance was the ground for the moment you hit the switch)
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,067
Location
Modesto, CA
It's likely just a switch and a current-limiting resistor (perhaps a thermistor too to prevent you from cooking it by holding in the button) which would send X mA to ground.

It would short hot to ground, not neutral... neutral and ground are at the same potential... you couldn't test it that way. (I suppose it would trip IF there was a load on the GFCI-protected circuit AND the path of least resistance was the ground for the moment you hit the switch)

Ive been able to trip a GFCI by simpling taking a wire and shorting load neutral to ground.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,034
Location
NJ
I'm thinking it is a resistor from hot to ground.

Shorting neutral to ground could split the load current between the 2 paths creating the sensed imbalance between hot and neutral in the gfci.

However, if there was no connected load and therefor no load current, then there is no current imbalance to be measured.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,771
Location
NW Iowa
GFCI tester uses a resistor between hot and ground. The resistor is sized to flow between 4 and 6 milliamps, which is the range of leakage current that a gfci is required to trip at.

The GFCI needs to be tested at this low current, testing at 1 amp or something ridiculous like that wouldn't do much for safety. It takes only 70 milliamps to stop the heart (less than 1/10 of am amp).
 
Last edited:

ishiboo

Well-known member
Joined
Oct 27, 2010
Messages
9,481
Location
Oshkosh, WI
Ive been able to trip a GFCI by simpling taking a wire and shorting load neutral to ground.

That's possible IF there's a load on the GFCI circuit and greater than whatever the trip current chooses to return from that load on the ground instead of the neutral then. But that wouldn't be a reliable way of testing.
 

tonyciambrone

Well-known member
Joined
Nov 4, 2015
Messages
1,152
Location
Northern Illinois
One time I unplugged a water cooler at work to service it. When I returned the unit to the receptacle nothing happened. I thought maybe the breaker had tripped, tried resetting the GFCI- nothing. Turned out it was backstabbed and the hot wire had finally decided to pop out at that time. The neutral was barely hanging on as well.

Depends on the circuit layout obviously but something like this could have happened to you
 

claymont

Well-known member
Joined
Oct 26, 2010
Messages
435
Location
CLAYMONT, DE
I had finished up installing new receptacles and I was using a klein RT210 tester to go over everything and accidentally hit the "test GFI" button on a non GFI receptacle. Now none of the receptacles in that circuit are working and did not trip the breaker. I've tried resetting the breaker and nothing....any ideas? :headscrat

Have you tried the tester on another circuit?
 