Hey guys,

I'm a bit of a rule follower, and want to make sure when I'm adding breakers to my panel, that is done up to code and in a professional manner.

My house was built in 2013 and a standard Square D panel was installed (similar to this: http://www.homedepot.com/p/Square-D-Homeline-200-Amp-30-Space-60-Circuit-Indoor-Main-Plug-On-Neutral-Breaker-Load-Center-with-Cover-Value-Pack-HOM3060M200PCVP/204836369). All wire was ran through the top of the panel, with 2 wires running out of each knockout, utilizing button connectors ( http://www.homedepot.com/p/Arlington-Industries-3-8-in-Plastic-Push-In-Button-Connectors-10-Pack-NM94-10/100186858?keyword=button+connector ).

My question is, if I can physically get a third 12/2 NM cable through the button connector/knock out, is it allowed? Each button connector currently has 2 wires through it. I wasn't sure if they did this out of convenience for themselves, or if there is some code limiting that. Please advise. Thanks!

Edit: I just noticed that the link for the button connectors mentions that 2 cables per connector. I know I can fit 3, is that allowed? Or do I have to follow the listing of the connector?
 
Last edited:
To avoid these ads, REGISTER NOW!

Rock knocker

Well-known member
Joined
Aug 14, 2014
Messages
704
I just noticed that the link for the button connectors mentions that 2 cables per connector. I know I can fit 3, is that allowed? Or do I have to follow the listing of the connector?

What do you think?

Follow the listing and don't ask questions hoping you'll get an anonymous exemption to the NEC over the net
 

JACDes

Well-known member
Joined
Dec 23, 2014
Messages
204
Location
IL
romex... bah.. with conduit you could have many more circuits in a pipe, meaning fewer homerun connections to the panel meaning fewer knock out connections.

I get why people like and use romex, Most cities in IL you can't for new work so we stick to EMT & rigid conduit.
 

Orionrising

Well-known member
Joined
Nov 16, 2012
Messages
960
Location
Western Maine
and depending on the size of the knockout/ clamp it may already be in violation, last small ones I used were labled 2/14 1/12 if I recall.
 
OP
C

cagullett1

Well-known member
Joined
Sep 29, 2013
Messages
2,203
Location
North Texas
What do you think?

Follow the listing and don't ask questions hoping you'll get an anonymous exemption to the NEC over the net

That was my question though, is there a NEC code that makes you follow the listing on the bag of these little connectors, or is that just a manufacturing thing?
 
To avoid these ads, REGISTER NOW!
OP
C

cagullett1

Well-known member
Joined
Sep 29, 2013
Messages
2,203
Location
North Texas
romex... bah.. with conduit you could have many more circuits in a pipe, meaning fewer homerun connections to the panel meaning fewer knock out connections.

I get why people like and use romex, Most cities in IL you can't for new work so we stick to EMT & rigid conduit.

Everything new here in TX is done with romex. In fact, I don't recall ever seeing conduit ran to a panel.
 

slow

Well-known member
Joined
Feb 26, 2006
Messages
2,596
Location
near Orlando
it is code in cities like Chicago to put everything in conduit, gotta love the unions.

Ryan
 

hammlm

Well-known member
Joined
Jun 21, 2005
Messages
676
Location
SE PA
Yes, code says you have to use a listed device in the manner (and capacity) it is listed.

2 cables in the connector if that's what the bag says. Use another knock-out or make a new hole.
 

JohnX14

Well-known member
Joined
Jun 2, 2014
Messages
557
Location
Boston 'burbs
Everyone here is spot on. Plus I highly doubt you will get a third NM cable in one of those without damaging it.
 
OP
C

cagullett1

Well-known member
Joined
Sep 29, 2013
Messages
2,203
Location
North Texas
Yes, code says you have to use a listed device in the manner (and capacity) it is listed.

2 cables in the connector if that's what the bag says. Use another knock-out or make a new hole.

I guess this is what I was looking for. I searched online and couldn't really tell... maybe because it's such a stupid question lol

Everyone here is spot on. Plus I highly doubt you will get a third NM cable in one of those without damaging it.

3 12/2 romex cables fit without any damage.... it's definitely tight though!
 

JACDes

Well-known member
Joined
Dec 23, 2014
Messages
204
Location
IL
it is code in cities like Chicago to put everything in conduit, gotta love the unions.

Ryan

Actually I prefer it in pipe for many reasons.

The system has a direct/permanent ground path, (metal pipe, fittings, and boxes) so no need to install additional ground wires.

with proper planning you only need a handful of conduit home-runs to the panel

You don't have to worry about damaging it with a drywall screw.

You actually need some skill to bend conduit, for a concealed system no one appreciates the quality of the electrical rough in but it is a better/safer installation.

For a garage / shop you can do an exposed system (if you like that look) and not have to worry about cables getting damaged.
 