Hey guys, I'm fairly new here but have read a few good articles on this site. I've been dreaming about adding a garage on the back of my house for some time with a deck on top (aka no roof). I'm looking at a 24x24 ft garage and would like to keep the floor space clear of supports.

I'm an engineer by trade but work with airplanes and metal instead of houses and wood so bare with me as I'm not familiar with what's allowed or standard practice. I was wondering if it's possible to splice some 2"x12"x12' joists together with a 12" spacing to span the 24 feet or would I be forced to use floor trusses or steel I beams for a span this large? If it is too large, could I get away with 20ft or 22ft instead?

If splicing is an option, I can think of tons of ways to splice wood together but what is the appropriate way to do it? Simpson straps, steel plates, bonded wood, nailed wood, bolted wood?

Thanks in advance.
 
To avoid these ads, REGISTER NOW!

Thumper68

Well-known member
Joined
May 16, 2013
Messages
5,134
Location
Duluth MN
I second the I-joist It will be your best bang for the buck. If you call up your supplier (Lumber yard) they will be able to size them for you.
 

kbs2244

Well-known member
Joined
Nov 11, 2006
Messages
14,065
Price competitive with wood "I" joists would be a steel "I" beam down the center with 12 foot joists resting on it.
The shorter span will be stiffer.
 

mharris2007

Well-known member
Joined
Jun 10, 2012
Messages
91
use I-joists

This.

I just built an attic for my garage. My engineer engineered the attic to hold 20,000 pounds or 6 honda civics, lol. There is a beam that spans 24 feet then the ijoists are 14 feet on one side and 8 feet on the other. If you don't plan on it holding anything ultra heavy, ijoists would span 24 ' fine.

When I was deciding between dimensional lumber or ijoists for my attic, you had to buy the best (most expensive) species of lumber for it to be sufficient across 24 feet. This was for attic space mind you 16" on center. Good luck.
 
OP
J

jfw432

Active member
Joined
Dec 30, 2015
Messages
26
Location
Macon, GA

Come on man....seriously? How about explain your original post just a tad better? I wouldn't tell you to make a carbon fiber airplane and show you a picture of dry carbon fiber cloth. I'm just trying to figure out if you're suggesting building one or buying one. It's not like a regular "off the shelf" item at Lowes or Home Depot so I'm here looking for a little bit of clarity. I've done plenty of research but every search ends the same way....lots of specs, no price, no idea who makes them, and no idea how they're assembled.

I've never used a lumber yard before so this is new territory to me. Most specialty shops I've dealt with in the past are in business for other businesses and usually want a license number before even giving me the time of day. Is a wooden I-joist common enough that any lumber yard would have them? Do they custom make them or have them lying around?
 

csp

Well-known member
Joined
Mar 23, 2010
Messages
5,719
Location
Franktown, CO
I second the I-joist It will be your best bang for the buck. If you call up your supplier (Lumber yard) they will be able to size them for you.

Key information here. Call a lumberyard, meaning a real lumberyard, not Home Depot or Lowes.

Chances are you're going to have to have structural engineering drawings for any building permit, so if you're serious go find an engineer that does this sort of work.
 
OP
J

jfw432

Active member
Joined
Dec 30, 2015
Messages
26
Location
Macon, GA
This.

I just built an attic for my garage. My engineer engineered the attic to hold 20,000 pounds or 6 honda civics, lol. There is a beam that spans 24 feet then the ijoists are 14 feet on one side and 8 feet on the other. If you don't plan on it holding anything ultra heavy, ijoists would span 24 ' fine.

When I was deciding between dimensional lumber or ijoists for my attic, you had to buy the best (most expensive) species of lumber for it to be sufficient across 24 feet. This was for attic space mind you 16" on center. Good luck.

I have definitely given this a lot of consideration because I can do the math for a metal I beam. Still need to find one and if it's economical enough, figure out how the heck me and some friends are going to move something like this. I'm guessing around 200-300lbs for one of these without the supports.
 

Thumper68

Well-known member
Joined
May 16, 2013
Messages
5,134
Location
Duluth MN
Come on man....seriously? How about explain your original post just a tad better? I wouldn't tell you to make a carbon fiber airplane and show you a picture of dry carbon fiber cloth. I'm just trying to figure out if you're suggesting building one or buying one. It's not like a regular "off the shelf" item at Lowes or Home Depot so I'm here looking for a little bit of clarity. I've done plenty of research but every search ends the same way....lots of specs, no price, no idea who makes them, and no idea how they're assembled.

I've never used a lumber yard before so this is new territory to me. Most specialty shops I've dealt with in the past are in business for other businesses and usually want a license number before even giving me the time of day. Is a wooden I-joist common enough that any lumber yard would have them? Do they custom make them or have them lying around?

If you call a real lumber yard, they will be able to spec and order the I-joists that you need. They usually do not have a engineer on staff and will contact the manufacturer and they will do the load calc, it usually takes a week or so to get the specs and a few weeks to deliver after the order.
 

Thumper68

Well-known member
Joined
May 16, 2013
Messages
5,134
Location
Duluth MN
Have to add:

Depending on your AHJ you might need stamped prints to get the permit. to get those you will have to pay a engineer to go over any plans and stamp them. I had drew up some for a customer a few years back and had to take them to a engineer for a stamp, they charged me $350.00 with no changes. Of course the stamp also comes with them accepting liability for the specs as well.
 
To avoid these ads, REGISTER NOW!
OP
J

jfw432

Active member
Joined
Dec 30, 2015
Messages
26
Location
Macon, GA
If you call a real lumber yard, they will be able to spec and order the I-joists that you need. They usually do not have a engineer on staff and will contact the manufacturer and they will do the load calc, it usually takes a week or so to get the specs and a few weeks to deliver after the order.

Thanks!
 

Dustball

Well-known member
Joined
Jun 25, 2011
Messages
2,081
Location
Hudson, WI
My house is a raised ranch meaning my living space is entirely over the garage. In order to have a clear span of 28 feet depth in the garage, 22" tall open web floor trusses were specified at 19.2" spacing. Seeing how houses and decks both need to meet 40PSF live load, you're probably looking at close to the same truss dimensions except you're four feet shorter. Keep in mind you have to also accommodate the weight of your roofing material and decking material.
 

gpflepsen

Well-known member
Joined
Sep 5, 2013
Messages
105
Location
NE
C'mon man! I like your *****. :}


Engineered lumber used according to the manufacturers span table often precludes the need for an engineered stamp. The design is already done and incorporated into the product literature. You need to understand where your inspector will be coming from and his requirements on this.

I would definitely look at the live loads and deflection that you're comfortable with. Having a bouncy deck would **** in my book. This would probably force you to upsize the joist to lessen the deflection. I'd explore the I-beam solution already mentioned for cost and buildability. Larger I-joist are easily manageable, but the I-beam will take some muscle.
 

dfiler2

Well-known member
Joined
Dec 15, 2014
Messages
2,858
Location
NW Minnesota
My shop is 26' wide 14" I-joists 16"OC w/ 3/4" T&G decking and Its very solid. You can also use metal bridging to take out the bounce.
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,077
Location
SE MI
First you need to know what the load is. This is going to be difficult because you want a deck on top, plus you have the "live load" of people walking on it. Once you know the dead and live load, there are tables you can look at for the proper joist size.

Likely you will have to go with a wooden I-beam or, worst case, a parallel chord floor truss.
 

6t7gto

Well-known member
Joined
Dec 6, 2005
Messages
522
Location
bedford,ohio
Come on man....seriously? How about explain your original post just a tad better? I wouldn't tell you to make a carbon fiber airplane and show you a picture of dry carbon fiber cloth. I'm just trying to figure out if you're suggesting building one or buying one. It's not like a regular "off the shelf" item at Lowes or Home Depot so I'm here looking for a little bit of clarity. I've done plenty of research but every search ends the same way....lots of specs, no price, no idea who makes them, and no idea how they're assembled.

I've never used a lumber yard before so this is new territory to me. Most specialty shops I've dealt with in the past are in business for other businesses and usually want a license number before even giving me the time of day. Is a wooden I-joist common enough that any lumber yard would have them? Do they custom make them or have them lying around?

http://www.menards.com/main/building-materials/engineered-products/i-joists/c-5662.htm

You're the "engineer", now all you have to do is figure out your live load and dead load.
 
Last edited:

rburke65

Well-known member
Joined
Nov 10, 2007
Messages
12,349
Location
Canfield, Ohio
I-joist....picture a wooden "I" beam with the center web of plywood and the upper and lower flange being a 2"x4" and you will have a rough visual. They have been in use for years.....invented in 1969. Good luck and keep us posted.
 
Last edited:

larry4406

Well-known member
Joined
Jan 27, 2006
Messages
19,039
Location
Northern Virginia
I would look into open web floor trusses. They span long distances. Then build a sleeper system on top to pitch the roof below the deck. Coat the roof with EPDM rubber to seal it. Then your deck bears on the EPDM (dead weight, no punctures).
 

kbs2244

Well-known member
Joined
Nov 11, 2006
Messages
14,065
Everybody has been ignoring the issue of "stiffness" in the floor above.
Open web, and even some solid wood web "I" jousts have fallen out of favor because they just do not have a "sold" feel.
They do meet all the load bearing specs but people feel a flex or "spring" when walking over them.
Around here the steel "I" beam and 12 foot span 2x12 is back in favor because of this.
 

csp

Well-known member
Joined
Mar 23, 2010
Messages
5,719
Location
Franktown, CO
Thanks. I saw those and I wish I had a Menards somewhere even remotely close to me so I could price those out and compare it to the other options.

If your location was listed in your profile someone reading this may be able to point to where you could look locally.
 

b4z

Well-known member
Joined
Dec 31, 2008
Messages
82
I have just modified our garage to remove a center support post and beef up the attic above.
It was 2 2x8s spanning 22' with a center support into the concrete floor and 2x6 floor/ceiling joists supporting the garage plaster ceiling and decking above for attic storage.
It is now 3 2x18" LVLs nailed together($1126) and the original 2x6s sitting on a 2x8 ledgers. When I sister 2x10s to the 2x6s for strength on the attic floor they will sit flush with the top of 2x18 LVLs. It will be super strong.
I'm going to agree with the other posters who have said that it is better to have a strong center spine and 2x10s or 12s off of that. I think it will be less expensive as well.
I am in charleston sc where will build for wind uplift and seismic. Mine was done by a engineer because it was required yours can probably be designed by the lumber yard.

BTW the plaster ceiling is so heavy the 11' 2x6s had deflected over a inch.
 
Last edited:

b4z

Well-known member
Joined
Dec 31, 2008
Messages
82
Everybody has been ignoring the issue of "stiffness" in the floor above.
Open web, and even some solid wood web "I" jousts have fallen out of favor because they just do not have a "sold" feel.
They do meet all the load bearing specs but people feel a flex or "spring" when walking over them.
Around here the steel "I" beam and 12 foot span 2x12 is back in favor because of this.
Agreed!
 

Jon_E

Well-known member
Joined
Aug 19, 2015
Messages
575
Location
Southwestern Vermont
Open span in my 24' x 36' garage. I used (2) W14x30 spanning the full 24', between each garage bay, and each 12' bay has roughsawn (full dimension) 2x10 pine at 16" on center. According to my calculations it can handle 100 psf live load. I was going to use I-joists but they are really "bouncy" for a long span. I also considered floor trusses and the cost was prohibitive.
 