I looked.....maybe I don't know what to call it when searching, the closest I can find is talk about "abandoned" electrical on forums with some references to the NEC.....

If you're installing a subpanel and running emt and boxes, what's the word on leaving a box unused? Specifically, my plans call for a lift. That lift will be hard-wired with a dedicated 30a breaker in the new subpanel. That lift won't be installed until after this subpanel install is done.

Can I go ahead and branch off of my emt run (it's headed that direction anyway) and run the wires to a box that will be used in the future? Is it ok to run the wire but not connect them in the subpanel? Can I cap them with wire nuts in the subpanel and in the box until I'm ready to wire up the lift? Should I instead run the emt and place the box, but not put any wires in until the lift is in, then call out the inspector on a new permit? What might an inspector say about an empty box that's obviously gonna be used for something in the future?

Thanks.....This is Hillsborough County Florida, Tampa suburbs, they use the 2011 NEC here.
 
To avoid these ads, REGISTER NOW!

mrVanagon

Well-known member
Joined
Jul 21, 2015
Messages
107
Location
Belleville, IL, USA
There shouldn't be any problem with a future-use box. Just cap the wires in the j-box and put a blank cover on it. In the panel I like to either cap the wires or connect them to their breaker and leave it off. Can even label that breaker "future use". I've done this sort of thing before.
 

vavet

Well-known member
Joined
Mar 6, 2012
Messages
5,363
Location
Ashland, VA
They ran a dedicated circuit to my bathroom when we built the house. It's to be used for a heated tile floor at some point.
 
OP
J

jtbinvalrico

Well-known member
Joined
Jan 2, 2010
Messages
1,375
Location
Tampa FL
They ran a dedicated circuit to my bathroom when we built the house. It's to be used for a heated tile floor at some point.

Did they connect it to a turned off breaker and label it as suggested above? Or did they cap the wires in the panel and tuck them to the side?
 

Falcon67

Well-known member
Joined
Jun 11, 2009
Messages
18,371
Location
Merkel, TX
They ran a dedicated circuit to my bathroom when we built the house. It's to be used for a heated tile floor at some point.

They ran wire for a 2nd plug in our master bath. Apparently the sheet rocker's covered it anyway. Found the box 2 years ago when I cut a hole for a second plug on the vanity - proximity tester says the wires buried in there are hot. One day I'll have to dig it out.
 

APEowner

Well-known member
Joined
Oct 2, 2009
Messages
4,170
Location
Sunny, New Mexico
There shouldn't be any problem with a future-use box. Just cap the wires in the j-box and put a blank cover on it. In the panel I like to either cap the wires or connect them to their breaker and leave it off. Can even label that breaker "future use". I've done this sort of thing before.

I prefer to connect the wires to the breaker but I don't know why.

They ran wire for a 2nd plug in our master bath. Apparently the sheet rocker's covered it anyway. Found the box 2 years ago when I cut a hole for a second plug on the vanity - proximity tester says the wires buried in there are hot. One day I'll have to dig it out.

That, is not cool.
 

6768rogues

Banned
Joined
Nov 28, 2007
Messages
4,524
Location
Western NY
When I did inspections, I accepted wires terminated by being safely capped and covered with a blank cover, without regard to whether they were connected at the other end to a breaker.
 

prostreetamx

Well-known member
Joined
Dec 19, 2016
Messages
222
Location
Las Vegas
You can have empty boxes as long as they are covered but dead end pipe runs are not allowed without some form of plug or cap on them. This prevents you from putting a fish tape into the pipe and ending up in a hot panel without some extra effort.
 
To avoid these ads, REGISTER NOW!

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,596
Location
Fullerton, CA
Spares are good things !!

NEC 90.8 Wiring Planning.
(A) Future Expansion and Convenience. Plans and specifications that provide ample space in raceways, spare raceways, and additional spaces allow for future increases in electric power and communications circuits.......
 

tyme2par4

Well-known member
Joined
May 16, 2016
Messages
571
Location
NH
I believe proper practice is to tie the hot and neutral together with a wire nut in the box. That way if anyone ever ties to power up that circuit, it will immediately trip the breaker. If you just cap each line individually, you end up with hot wires that aren't attached to anything.
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,596
Location
Fullerton, CA
I believe proper practice is to tie the hot and neutral together with a wire nut in the box. If you just cap each line individually, you end up with hot wires that aren't attached to anything.

And what's wrong with hot wires that aren't attached to anything in a box? :confused:

You should ALWAYS test to see if they're dead
 

AntonLargiader

Well-known member
Joined
Nov 20, 2016
Messages
1,372
Location
Charlottesville, VA
I believe proper practice is to tie the hot and neutral together with a wire nut in the box. That way if anyone ever ties to power up that circuit, it will immediately trip the breaker. If you just cap each line individually, you end up with hot wires that aren't attached to anything.

I'm having a hard time believing that's any kind pf proper practice. What's so wrong with a hot and neutral sitting in a box waiting to be used? Why add the complexity of a deliberate short that needs to be troubleshot and repaired before you can get on with what you're doing?
 

OH_Varmntr

Well-known member
Joined
Apr 2, 2017
Messages
320
Location
Ohio
I believe proper practice is to tie the hot and neutral together with a wire nut in the box. That way if anyone ever ties to power up that circuit, it will immediately trip the breaker. If you just cap each line individually, you end up with hot wires that aren't attached to anything.



Proper practice by whom?!
 

reader2580

Well-known member
Joined
Dec 31, 2014
Messages
14,628
Location
Minneapolis, MN
My electrical inspector didn't like having a currently unused line still attached to a breaker. His concern was someone turning the breaker on and then someone working on the circuit later without checking the breaker. (Pretty stupid if you don't check breaker first.) He didn't fail me for this, but he said I should remove wire from breaker until needed.

I don't currently have a dishwasher, but I have a space for one. The unused line is for the dishwasher when I do get around to buying another one. I ran low on money during kitchen remodel so I skipped the dishwasher since I used the one in my other house maybe once a year.
 

mrVanagon

Well-known member
Joined
Jul 21, 2015
Messages
107
Location
Belleville, IL, USA
A box behind a future dishwasher is easy. Put a single plug receptacle in the box and connect it to the breaker on the other end. When you add the dishwasher put a cord set on it and plug it in.
 