Legal to Punch Another Knockout in Strip Light?

bad_idea

Well-known member
Joined
Jun 11, 2011
Messages
4,338
Location
Pasquotank, NC
My long winded title pretty well says it. I bought (20) 2 Bulb 48" T8 LED strip lights I plan to mount directly to the bottom of the trusses (no ceiling). If I mount the lights centered on the truss (parallel to the truss) it blocks the factory knock outs in the light housing. Is it code compliant to make a new hole off center in the housing? That would allow me to mount the lights down the center of the truss, cable down the side of the truss and dropped into the top of the light. At some time in the distant future I plan to install a ceiling and would like all of the wiring in the attic space.
 
Last edited:
To avoid these ads, REGISTER NOW!

markhm

Well-known member
Joined
Mar 4, 2017
Messages
265
Location
NY
Punching a new hole in the fixture voids the UL listing. Code requires fixtures be (UL) listed.

In reality, it is done often. It doesn't sound like a safety issue assuming it is properly done. But if you have an electrical inspection at some point, an inspector would be allowed to say you have an unlisted fixture and reject you.
 
OP
B

bad_idea

Well-known member
Joined
Jun 11, 2011
Messages
4,338
Location
Pasquotank, NC
I built the garage last summer and am finally getting around to running the electrical (time and money deficit). I am going to pull an electrical permit. Considering the money I have invested in the lights, I don't want to take the risk of getting rejected. So, what other options are there to mount these lights to the bottom of the truss with the wiring entering through the top of the fixture?
 

OccupantRJ

Well-known member
Joined
May 15, 2009
Messages
11,460
Location
Eastern North Carolina
You could mount them across trusses instead of parallel to allow the knockouts to be used. On mine, I just popped holes where I needed them. Government, stay off my lawn!
 

markhm

Well-known member
Joined
Mar 4, 2017
Messages
265
Location
NY
Suspend them below truss and wire thru factory k/o. Get your inspection.

Then you can raise them, plug the k/o holes and put new holes where it works for you.
 

Platonic Solid

Well-known member
Joined
Nov 29, 2014
Messages
3,587
Location
CT-USA
This is done all the time in the field with a greenlee punch. If you do it neatly, no inspector would ever know or care. Many strip light housings come with knockouts on the back, side and ends. Since LED retrofit bulb strip light housings have no internal components and only house the wires, I can't think of any UL issues with adding a 7/8" dia. hole at a location that's convenient for your installation. Just use common sense with respect to hole location so there's enough clearance for the nut of the cable connector (or whatever device you're installing) and you're not diminishing the structural integrity of the housing or interfering with installed housing parts.

Note: Using the 3.32" width of the Maxlite 4ft retrofit housing, you don't have enough room to do what you're stating. 3.32" - 1.5" truss = 1.82" / 2 = 0.91". This puts the edge of the 7/8" hole right at the housing bend line - offering no clearance for the cable connector nut.
 
Last edited:

Jim greengo

Well-known member
Joined
Sep 3, 2018
Messages
7,415
Location
Behind my house
Punching a new hole in the fixture voids the UL listing. Code requires fixtures be (UL) listed.

In reality, it is done often. It doesn't sound like a safety issue assuming it is properly done. But if you have an electrical inspection at some point, an inspector would be allowed to say you have an unlisted fixture and reject you.

As long as it lands under the cover that protects wires I dont see an inspector complaining about it myself anyway.
 

nsula_country

Well-known member
Joined
May 23, 2013
Messages
1,534
Location
Northwestern Louisiana
Greenlee or hole saw KO where needed (correct size). Use proper cable or conduit fitting with a locknut. If existing KO have been knocked out, install a filler plug (no tape!). Done.

CT
 

ard

Well-known member
Joined
Feb 16, 2015
Messages
4,391
Location
Sierra Foothills... California
lol. Legal? Who cares?

If it is inspected, ask the inspector. Otherwise doesnt matter (unless you are a licensed contractor.)

(Edit: not saying to go and violated codes....just that there seems to be an obsession with 'to code' in some very very minor and arcane points. Moving a KO a few inches in an otherwise open wiring channel is one of them.....)
 
Last edited:

dledinger

Well-known member
Joined
Apr 14, 2009
Messages
345
Most inspectors around here wouldn’t know one hole from a hole in the ground...if you get what I’m saying.
 

teamextreme

Well-known member
Joined
Aug 10, 2013
Messages
867
Location
Lakewood, CO
This is done all the time in the field with a greenlee punch. If you do it neatly, no inspector would ever know or care. Many strip light housings come with knockouts on the back, side and ends. Since LED retrofit bulb strip light housings have no internal components and only house the wires, I can't think of any UL issues with adding a 7/8" dia. hole at a location that's convenient for your installation. Just use common sense with respect to hole location so there's enough clearance for the nut of the cable connector (or whatever device you're installing) and you're not diminishing the structural integrity of the housing or interfering with installed housing parts.

Note: Using the 3.32" width of the Maxlite 4ft retrofit housing, you don't have enough room to do what you're stating. 3.32" - 1.5" truss = 1.82" / 2 = 0.91". This puts the edge of the 7/8" hole right at the housing bend line - offering no clearance for the cable connector nut.

^This. Particularly the second paragraph. You would have to mount the fixtures off-of-center on the truss to provide enough room on the back of the fixture for a new KO.
 
OP
B

bad_idea

Well-known member
Joined
Jun 11, 2011
Messages
4,338
Location
Pasquotank, NC
If you have an inspector digging that deep, you are going to fail anyway

I hear you on that one. I just want to avoid getting failed for an item that will cost me a fortune.

I appreciate you all's confidence in punching a new hole not being a big deal. Unfortunately I am that guy that will get popped for dumb stuff. This is a 'Risk vs. Reward' deal for me - I risk having an inspector tell me all of my light housings are garbage for the reward of an easier install. I'll sort a good solution that follows code, or at least can be easily reversed if I get popped.
 

ard

Well-known member
Joined
Feb 16, 2015
Messages
4,391
Location
Sierra Foothills... California
I hear you on that one. I just want to avoid getting failed for an item that will cost me a fortune.

I appreciate you all's confidence in punching a new hole not being a big deal. Unfortunately I am that guy that will get popped for dumb stuff. This is a 'Risk vs. Reward' deal for me - I risk having an inspector tell me all of my light housings are garbage for the reward of an easier install. I'll sort a good solution that follows code, or at least can be easily reversed if I get popped.

Ask the inspector. You will then have your ducks in a row.


Or OP is just being OCD and needs it to 'be to code' for whatever reason.

Cant ask an inspector if there actually is no inspector....
 
To avoid these ads, REGISTER NOW!

Platonic Solid

Well-known member
Joined
Nov 29, 2014
Messages
3,587
Location
CT-USA

Innovate1

Well-known member
Joined
Jul 28, 2014
Messages
4,323
Location
Illinois near St. Louis, Missouri
I can't imagine it being a problem to punch another hole as long as there are no other issues (wires pinched, things like that). They make electrical boxes with no holes that you have to punch holes in so how can that be wrong? And how would the inspector ever know that the hole wasn't a knockout. Once the fitting is in place there is no way to tell.

But the added wood sounds easier.
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,596
Location
Fullerton, CA
More about the listings thing....
Some jobs for municipalities I've worked on specified for a minimum conduit size of 3/4".
The light fixtures that they specified only came with 1/2" KOs.
I guess by knocking them out to 3/4" I violated the listing requirements?
:wtf::headscrat
 

Falcon67

Well-known member
Joined
Jun 11, 2009
Messages
18,371
Location
Merkel, TX
If I was going to put up rows of 4' fixtures, I'd also consider tying them together with conduit end for end and raising the whole mess as a unit to the joist, then coming out of one end with the feed.

Also done the spacer block thing - see the light at the far distance in the pic

S2Ceiling8.jpg
 

NUTTSGT

Super Moderator
Staff member
Joined
Sep 14, 2009
Messages
51,407
Location
Northern Central Ohio
I can't imagine the inspector would have issue with it. They make junction boxes with out knockouts so you can place them where you need them.
 

BD1

Well-known member
Joined
Mar 18, 2007
Messages
4,602
Location
north side
What about wiring light with a cord and plug end. Mount cord up against trust and plug into receptacle.


Sent from my iPhone using Tapatalk
 

MattT

Well-known member
Joined
Feb 20, 2010
Messages
3,201
What he said.

What y'all said:bounce:

I've been told that to maintain a UL listing whatever you stick in the hole must also be UL listed. This was for enclosures so maybe there are different rules for light fixtures...................................
 