Is anyone on the forum familiar with Lennox defrost circuits on heat pump?
My house has a HPXA12 heatpump. Recently it seemed like after a defrost cycle the outdoor fan no longer works when I request heat or AC. This started on a below freezing day when defrosting would have been needed. I noticed the HP was supposed to be running but no heat was coming and the outside fan was off. The unit was well defrosted. As an expedient I setup the system to just use backup heat.
Today I tried to look into the thing and found the following.
1. The outside fan works if I manually press the compressor contactor. I've also verified the capacitors are good. So I do not believe my issue is with the fan itself.
2. Today was warm enough to try both heat and AC modes. In both cases the pump turned on but the fan didn't.
3. Looking at the defrost control board there are status LEDs. The whole time they indicated either ready or short cycle delay (just after I turned the system off).
4. I don't see obvious damage on the defrost control board. Replacements appear to be $200 so affordable but I don't want to guess and check just yet.
Is there anything else I should check?
Are these boards known to fail? I see that Lennox has a new board that supersedes mine.
Any suggestions?
My house has a HPXA12 heatpump. Recently it seemed like after a defrost cycle the outdoor fan no longer works when I request heat or AC. This started on a below freezing day when defrosting would have been needed. I noticed the HP was supposed to be running but no heat was coming and the outside fan was off. The unit was well defrosted. As an expedient I setup the system to just use backup heat.
Today I tried to look into the thing and found the following.
1. The outside fan works if I manually press the compressor contactor. I've also verified the capacitors are good. So I do not believe my issue is with the fan itself.
2. Today was warm enough to try both heat and AC modes. In both cases the pump turned on but the fan didn't.
3. Looking at the defrost control board there are status LEDs. The whole time they indicated either ready or short cycle delay (just after I turned the system off).
4. I don't see obvious damage on the defrost control board. Replacements appear to be $200 so affordable but I don't want to guess and check just yet.
Is there anything else I should check?
Are these boards known to fail? I see that Lennox has a new board that supersedes mine.
Any suggestions?