Less then Neat Wire Termination under Terminal

Spudland_Dave

Well-known member
Joined
Mar 12, 2010
Messages
3,025
Location
Maine
I know...vague as hell title....last night I wired up my Sub-Sub Panel using the 4ga THHN, my question is on the Neutral and 2 Hot lugs in my panel, the wire once I tightened down the lugs is quite smooshed and some of the strands are not under the lug. I attribute that to the lug being so large and cable relatively small. On the "Feed End" where that 4ga THHN goes into the 60A Breaker its beautiful and perfect. I tried a couple times, outcome the same. Lugs are rated for 4ga, so no technical/code problem there. Being a little OCD, it looked less then perfect so I figured I'd ask about it.
 
To avoid these ads, REGISTER NOW!

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,620
Location
SE MI
If twisting tightly with linesman pliers doesn't help, you could try "tinning" the end with solder, but unless you have a really old fashioned heavy duty iron, you will likely get a cold joint.
 

SiGmA_X

Well-known member
Joined
Aug 13, 2005
Messages
1,111
Location
Portland, OR
I'd re-twist with your linesman pliers and see what happens. I've only installed a couple runs of 3-4ga before but it all fit under the terminals completely.
 
OP
S

Spudland_Dave

Well-known member
Joined
Mar 12, 2010
Messages
3,025
Location
Maine
I'd re-twist with your linesman pliers and see what happens. I've only installed a couple runs of 3-4ga before but it all fit under the terminals completely.

I did that on the worst one...what ends up happening is because there is no "Side Support" for the wire (1/4" wire diameter in a 1/2" lug hole) the wire just smashes down quite a bit under the set screw...Even as twisted tight I could get it. Now I'm at the point where I'd hate to damage the end.
 
To avoid these ads, REGISTER NOW!

Rob_b

Well-known member
Joined
Jul 28, 2009
Messages
209
Location
Ontario Canada
You could always use a ferrell (sp) on the wire end before putting under the lug. It sounds as if the lug is rated for minimum of #2 or larger if its spreading out that badly. Short of that, go with tinning it up. That will also keep it from over-heating on a large load.
 

SiGmA_X

Well-known member
Joined
Aug 13, 2005
Messages
1,111
Location
Portland, OR
If Aceman says its OK, I think its probably fine. The man quotes NEC like its his job (I think it is ;)).

Maybe post up a picture so someone can give some feedback based directly on what they see vs a description of it?
 
OP
S

Spudland_Dave

Well-known member
Joined
Mar 12, 2010
Messages
3,025
Location
Maine
If Aceman says its OK, I think its probably fine. The man quotes NEC like its his job (I think it is ;)).

Maybe post up a picture so someone can give some feedback based directly on what they see vs a description of it?

Here ya guys go...I was thinking the same thing, by the time I/we got the kids to bed, I get out into the shop, etc you beat me to it :D

As you can see...I took the neutral off the lug tonight and put it directly on the Neutral bar...fits like a Glove there.

Main & Neutral Lugs are rated #6-1 on the panel sticker. Ground & Neutral Bars are #4-??
 

Attachments

  • black.jpg
    black.jpg
    95.3 KB · Views: 47
  • red.jpg
    red.jpg
    90.8 KB · Views: 44
  • panel.jpg
    panel.jpg
    94.2 KB · Views: 47