Light Fixture Grounding

dfiler2

Well-known member
Joined
Dec 15, 2014
Messages
2,858
Location
NW Minnesota
Hi guys, I have two questions. I installed 9- 8’ T8 w/4 4’ bulbs in each fixture. There are three rows of three fixtures each. I am using surface mounted EMT and have connected the fixtures in each row with a short piece of conduit. My question is, do I need to run the ground wire to each fixture? I ran the ground wire to the first fixture in each row, I used a twist on wire connector on those connections so running the ground to each fixture would be easy if I need to.

My second question is do I need to have a ground wire connected in every box? I have a couple of boxes where there are no connections made, just used them for pulling the wire.

Thanks in advance
 
To avoid these ads, REGISTER NOW!

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
Yes you need to ground a metal Jbox and the conduit is fine for the fixtures. I double check a bit before I put the covers on o make sure the nuts are tight. I probably would not add a wire if I piped.
 

coyote54

Well-known member
Joined
Dec 31, 2011
Messages
62
Location
Eastern Washington State
I'm doing this very exact thing in my shop today except I'm daisy chaining 8 4' 2 bulb T5 fixtures together with 30" lengths of 1/2" EMT between the fixtures (fixtures are plastic housings). Ran the green to each fixture and also bonded each individual piece of EMT with a bonding locknut. Since fixtures are attached to a tin ceiling, electrician said to bond the EMT's together.
 

laser3kw

Well-known member
Joined
Nov 17, 2012
Messages
7,276
Location
northen IL
My shop has three rows, 3 fixtures each row, conduit between rows, fixtures butted end to end in each row,
I ran a green from the panel and pig tailed to each fixture ground screw (green screw in fixture housing) and each row.
I did not want to rely on conduit and nut connections for grounding over that area. They could rattle loose over time.
 
To avoid these ads, REGISTER NOW!

Rookie2

Well-known member
Joined
Feb 27, 2013
Messages
1,925
Location
Western Pa.
You won't believe this but somewhere I read (balast company) that the fixture needs to be grounded for proper lamp operation. I have replaced U tube T-12 lamps that have a foil stip taped to the lamp and connects to the lamp base at each end.

anyone else older than dirt remember this ?
 

cybrdyke

Well-known member
Joined
Sep 9, 2014
Messages
3,442
Location
USA
Those strips are there to help with the ignition of the lamps. They help pull the arc around the bend.
CD
 

rlitman

Well-known member
Joined
Oct 18, 2010
Messages
24,591
Location
Long Island
You won't believe this but somewhere I read (balast company) that the fixture needs to be grounded for proper lamp operation...

anyone else older than dirt remember this ?

That was more of an issue in T12. I don't think it is necessary for T8 with solid state ballasts. Still, grounding of metal is required for safety.
 