Nailing in boxes and so on and this is the startup plan. Any comments or suggestions welcome.

Have three gooseneck lamps for outside so will have boxes for those and a few other undereave lamps (not shown)

How many outlets per circuit are good for a garage. Keeping in mind there is only one of me operating equipment.

Using a 100 a subpanel. 150 feet of 1.5" conduit buried from the house (nothing pulled yet) Do I need ground rods or run it back to house (read lots of threads but nothing seemed conclusive. I plan to do most of the rough in myself and have an electrician to the final tie ins.

electric001.jpg



Included my build link so you can see the actual structure as it sits now.

http://www.garagejournal.com/forum/showthread.php?t=106028

Cheers,
 
Last edited:
To avoid these ads, REGISTER NOW!

scrape53

Member
Joined
Mar 5, 2010
Messages
9
the plan looks good...as far as the ground goes it depends. if you fall under 2008nec you need both if not just rods at the building
 
To avoid these ads, REGISTER NOW!

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
In the US you would run four wires, two hots, a neutral, and a ground (if supplied from your house panel) and you also would need two ground rods at the garage. Ground and neutral circuit are separated from each other. Not sure if Canada is the same or not.