I just wired in 5 vintage porcelain lights with 16-2 plus ground. Ended up putting 200W bulbs in each and now am questioning my wire size. Am I OK or do I need to up wire size or go to LED lights? Breaker size OK?
 

Attachments

  • IMG_4067.JPG
    IMG_4067.JPG
    96.4 KB · Views: 69
  • Lites 2.jpg
    Lites 2.jpg
    59.1 KB · Views: 70
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,002
Location
Modesto, CA
You used 16/2 + grnd?

What type of wire did u use? Sounds like you used cordage.

Smallest gauge building wire available is #14.

Either way, on a 20a breaker, you shouldve used #12. 16 and 14 are too small.

Tear it out and use 12/2...

BTW in cordage the ground is counted so hot neutral and ground is counted as 16/3.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,754
Flexible cord is not permitted to be a substitute for the fixed wiring of a structure, see 400.8(1), it would be easier to use 14/2 NM & replace the 20A breaker W/ a 15A.
 

zmaxmotorsports

Well-known member
Joined
Jan 11, 2013
Messages
11,948
Location
South of omaha
You used 16/2 + grnd?

What type of wire did u use? Sounds like you used cordage.

Smallest gauge building wire available is #14.

Either way, on a 20a breaker, you shouldve used #12. 16 and 14 are too small.

Tear it out and use 12/2...

BTW in cordage the ground is counted so hot neutral and ground is counted as 16/3.
:thumbup::thumbup::thumbup::thumbup:
 

nsula_country

Well-known member
Joined
May 23, 2013
Messages
1,534
Location
Northwestern Louisiana
Is the cord orange?

Did it at one time have male and female plugs on each end of it?

I agree that pulling 1000 watts of incandescent, it needs minimum of 14 ga wire. 12 ga wire if you would like to keep the 20 amp breaker.

CT
 

American Locomotive

Well-known member
Joined
Jan 8, 2017
Messages
10,953
Location
Rhode Island
As mentioned, the 16 gauge cord is not appropriate for fixed wiring, neither is the 20 amp breaker on 16 gauge wire. Go to a 15 amp breaker and 14-2 romex, or keep the 20a and go 12-2

Also, you should go to LED anyways, since blowing 1KW of power to light the front of your garage up is just insane.
 

nsula_country

Well-known member
Joined
May 23, 2013
Messages
1,534
Location
Northwestern Louisiana
They do look period correct though! I like vintage lighting.

We have 30's-40's era Holophane Acorn Industrial fixtures in our kitchen and on the porches. Cut glass globes are second to none for light distribution. We are using 75 watt equivalent LED bulbs in them.

CT
 
Last edited:
OP
Y

Youngfd

Well-known member
Joined
Dec 9, 2014
Messages
189
Location
Maltby, WA
I was wrong. Wiring is 14/2 w ground Romex. I changed breaker to a 15 AMP.
 

Attachments

  • IMG_4098.JPG
    IMG_4098.JPG
    142.8 KB · Views: 20
To avoid these ads, REGISTER NOW!

ddawg16

Well-known member
Joined
Jul 11, 2008
Messages
21,005
Location
S. California
Lighting looks great.....but...200W?

What kind of bulbs did you use?

I would really suggest looking for LED bulbs....a fraction of the energy and will last a LOT longer
 
OP
Y

Youngfd

Well-known member
Joined
Dec 9, 2014
Messages
189
Location
Maltby, WA
Yes, I am looking into LED lights to replace the 200W. I have a 200 Amp panel that I am going to have replaced with a Square D 200 Amp.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,717
Location
NW Iowa
Most of the LED options look terrible in these style of lights. Few of them throw enough light to the side and the reflector will look dark, completely ruins the look of these fixtures.

There are some "filament" LED bulbs that throw light 360*, but I think the largest I've seen those is 6.5W. I think that is in the neighborhood of a 60W incandescent. But that may still produce enough light depending on what your trying to achieve.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,717
Location
NW Iowa
Bert....I disagree. I have one of those fixtures and I have an LED bulb in it....and it great

I'll believe it when I see it...

In the few I have seen the LED was too directional sending most of the light straight down instead to shining on the reflector and letting the reflector do it's job of redirecting the light.

If a filament led lamp of suitable wattage can be found then I think that would be the nicest solution

Feel free to show a picture and prove me wrong, I'm just basing my opinion on what I have seen.
 
OP
Y

Youngfd

Well-known member
Joined
Dec 9, 2014
Messages
189
Location
Maltby, WA
Soffit will all be enclosed so wiring will be high and dry. I will have to experiment with LED lights as you do want the right look with the lights on.
 

JohnnyK81

Well-known member
Joined
Jul 6, 2016
Messages
142
Bert....I disagree. I have one of those fixtures and I have an LED bulb in it....and it great

I think Bert has a little bias against LED's from what I've been reading in multiple threads, so his mind is made up! :D
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,717
Location
NW Iowa
I think Bert has a little bias against LED's from what I've been reading in multiple threads, so his mind is made up! :D

I just try to even the playing field. LED's have been marketed as so superior when in fact they can be matched in efficiency and many other parameters by several other light sources. I just want all the facts to be heard.

I guess if no one else was promoting LED's then I would say more good things about them since there ARE many good things about them.
In fact I do like LED's in many applications. I put in some LED wraps just the other day and I was very happy with them. I will definitely recommend them again in the right situation. But they weren't cheap costco or feit fixtures.

Now I guess I will have to admit you are somewhat correct about my "bias". But to be truthful my bias is more towards old magnetic ballasted gear, HID and fluorescent. I love 'em they last and last, often just takes a few lamp changes to keep them going. My favorite fixtures in my garage are some "shop light" style F40T12 fixtures from the late 40's that I saved and use regularly, They all original including ballasts. Hard to beat 70 years of service with nothing other than new lamps and starters.


Back on topic, I would definitely try some LED's in those fixtures. I personally have a similar fixture, mine is an old incandescent yard light that mounts by an arm, and I use a 6.5W filament LED lamp in it. But if the OP wants the same amount of light as those 200w lamps provide then those filament LED's aren't an option. I am just worried that standard LED lamps will not be aesthetically pleasing.
 