I have a lighting circuit running 2 fixtures using 2 3-way switches. All of a sudden neither of lights works. The sequence is POWER to 3-way to 3-way to FIXTURE to FIXTURE.

Checked power = good. Power to 2nd 3-way = good Power to first fixture = good.

Tested with basic noncontact tester.

Removed one fixture and replaced it with a basic ceramic keyless lamp holder = no light.

So my next thought is open neutral somewhere (at either switch). God forbid it's a mouse related problem.

Thoughts?
 
To avoid these ads, REGISTER NOW!

Shiftless

Well-known member
Joined
Mar 9, 2014
Messages
14,474
Location
East Bay SFO
You mentioned mice...
If you’ve checked the bulbs I can’t see any other explanation.
anybody else have an idea?
 

bigmike989

Member
Joined
Feb 5, 2016
Messages
23
Make sure both switches are to their extreme position. I've had a 3-way stop in the "middle" with no connection. It just needed to be bumped.
 

Shiftless

Well-known member
Joined
Mar 9, 2014
Messages
14,474
Location
East Bay SFO
Here’s your wiring, right? (Second fixture added in parallel to the one here on the right)

You said this “ Checked power = good. Power to 2nd 3-way = good Power to first fixture = good.”

That implies that there is power to first fixture so that one works OK??

If so, you’ve got an open somewhere between the 2 lights.
 

Attachments

  • CE77FCA2-34B1-4F8F-9546-C098F620C106.jpeg
    CE77FCA2-34B1-4F8F-9546-C098F620C106.jpeg
    133.1 KB · Views: 43

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
22,308
Location
VT
Get a real tester.

Those non contact tester are prone to false voltage readings
 

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
Get a meter that reads voltage, that non contact tester will not tell you if you lost a neutral and alot of times when it tests hot, it might not be 120 volts. Remember, all white wires in a 3-way switch circuit are not neutrals
 
Last edited:

nadogail

Well-known member
Joined
Jan 23, 2009
Messages
31,906
Location
Coronado, CA
IMHO, Non contact testers have limited value in trouble shooting; but they can help you stay alive.

You now need a "Real" multimeter.
 
OP
B

Bunchgrass

Well-known member
Joined
Dec 8, 2013
Messages
236
Location
North Idaho
So if I have an open btwn the 1st and 2nd fixture why wouldn't the first one work? The neutral (common) should complete the circuit from that fixture back to the panel, no?

Note -- there was nothing done to this circuit before the failure. It just stopped working one AM.


More info --- there are other outlets between the panel and the first 3-way switch. They are both fine. Also another switch in the first box with the 3-way and tying into the same common as the 3-way. IMO --- this indicates a problem somewhere between the 1st 3-way and the fixtures
 
Last edited:

yatg

Well-known member
Joined
Aug 16, 2019
Messages
2,749
Location
Southern Oregon
Check all connections, including the neutrals wire-nutted.

Backstabs to the switches are bad.

Check for 120v between hot/neutral at your first switch, second switch, first light. That will tell you more.
 

Shiftless

Well-known member
Joined
Mar 9, 2014
Messages
14,474
Location
East Bay SFO
So if I have an open btwn the 1st and 2nd fixture why wouldn’t the first one work? The neutral (common) should complete the circuit from that fixture back to the panel, no?

Note -- there was nothing done to this circuit before the failure. It just stopped working one AM.


More info --- there are other outlets between the panel and the first 3-way switch. They are both fine. Also another switch in the first box with the 3-way and tying into the same common as the 3-way. IMO --- this indicates a problem somewhere between the 1st 3-way and the fixtures

I thought you said in your first post that you had power to the first light fixture?

“Power to first fixture = good”
 
OP
B

Bunchgrass

Well-known member
Joined
Dec 8, 2013
Messages
236
Location
North Idaho
Maybe I was unclear, sorry.

I do have POWER to the first fixture. Checked the hot. Installed a cheap ceramic keyhole lamp holder and ..... no light.

More and more this seems to indicate and issue between this fixture and the power coming into the 1 st 3-way.
 
OP
B

Bunchgrass

Well-known member
Joined
Dec 8, 2013
Messages
236
Location
North Idaho
Checked neutral/common connections -- look good/solid tight.

Using my meter ==

Checked power at fixture box (probe to hot and white common) -- 120V
Installed keyhole lamp holder and tested socket ( probe to threaded portion and tab in base) --- 120V
Put functioning light bulb into lamp holder --- nothing.

I'm totally lost now. How I can have 120V and not get a bulb to light is .... confusing?
 

larry4406

Well-known member
Joined
Jan 27, 2006
Messages
19,024
Location
Northern Virginia
Turn breaker off.

Reach into keyless socket and pull the brass tab at the bottom of the socket up so it makes contact with the bulb. Insert known good bulb.

Turn breaker on. Let there be light.

I have had several light bulbs that didn't seem to thread enough into the socket to engage the brass tab at the bottom.
 

Yankeefarmer

Well-known member
Joined
Jul 25, 2011
Messages
1,169
Location
Connecticut
Checked neutral/common connections -- look good/solid tight.

Using my meter ==

Checked power at fixture box (probe to hot and white common) -- 120V
Installed keyhole lamp holder and tested socket ( probe to threaded portion and tab in base) --- 120V
Put functioning light bulb into lamp holder --- nothing.

I'm totally lost now. How I can have 120V and not get a bulb to light is .... confusing?

Very carefully, with the lampholder hanging out of the wall or ceiling, and a known good bulb in it, use a meter to measure voltage across the lampholder. If you have a bad connection or almost severed wire, it’ll cause high resistance such that you can measure 120 v with no load, and 0 volt with a load.
 
OP
B

Bunchgrass

Well-known member
Joined
Dec 8, 2013
Messages
236
Location
North Idaho
More troubleshooting.

1) Removed 3 way switch nearest the fixture. Attached hot and common from a separate circuit to the switch leg. Works. So apparently not a switch leg/fixture issue.

2) Tried a single pole (all I had in the toolbox) using one hot lead from 3-way circuit and switch leg black --- commons tied. Nothing.

3) Checked voltage at both red and black of this 3 way -- 113V when touching the isolated common. When the common was connected to the switch leg that number rose to 122V. What IS that?

One step further --- connected hot to black switchleg directly (wirenut). Nothing. Same with red. IMO this all seems to point to a problem with the common but I can see nowhere for there to be an issue (either of the boxes). Any ideas at all?
 
OP
B

Bunchgrass

Well-known member
Joined
Dec 8, 2013
Messages
236
Location
North Idaho
Latest --- I took some 12g wire and jumped from the common at the first 3way box to the light switch leg bypassing the common between the switches and we had light. So clearly the issue is the common in that run. Next question. How to remedy. I will check the run under the house but it's very possible this is in the wall between the switch box (either one) and the floor. Pull a whole new piece of 12-3?
 
To avoid these ads, REGISTER NOW!

cybrdyke

Well-known member
Joined
Sep 9, 2014
Messages
3,442
Location
USA
this is why I chuckle when I hear folks put down wireless switches. All the extra aggravation of pulling wires, figuring out which wires go where, and then at the end, they still dont work right. And then fixing them is even more of a headache.
Yeah, wireless switches are more expensive. But install them in 10 minutes and they work.
They're not voodoo. They've been around for 10 years with millions of satisfied customers.
www.casetawireless.com

Good luck,
CD
 
OP
B

Bunchgrass

Well-known member
Joined
Dec 8, 2013
Messages
236
Location
North Idaho
But wait. There's more. At the switch box and in the cavity leading to the switch box.:sad:
 

Attachments

  • IMG_1160.jpg
    IMG_1160.jpg
    89.9 KB · Views: 89
  • IMG_1162.jpg
    IMG_1162.jpg
    95.9 KB · Views: 87

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,698
Location
NW Iowa
Ouch, looks like you've got a bit of a mouse problem. I don't know why they like wires so much.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,698
Location
NW Iowa
this is why I chuckle when I hear folks put down wireless switches. All the extra aggravation of pulling wires, figuring out which wires go where, and then at the end, they still dont work right. And then fixing them is even more of a headache.
Yeah, wireless switches are more expensive. But install them in 10 minutes and they work.
They're not voodoo. They've been around for 10 years with millions of satisfied customers.
www.casetawireless.com

Good luck,
CD

They've got a place sure, but I don't want them everywhere. You've still got to run wire for a wireless switch, maybe to only one location but it's not immune to these problems.

I've got a few original switches in my house. Got to be 100 years old. When wireless switches have that kind of track record we can talk.
 
OP
B

Bunchgrass

Well-known member
Joined
Dec 8, 2013
Messages
236
Location
North Idaho
Mice are a serious issue here. We farm and have a constant battle with mice. They get in any rigs not being used for more than 7 days. Sometimes even if they are being used. Get in the cabin air filter/fan etc. You can trap or poison as much as you like --- it's like clone wars. They just keep coming.
 

Shiftless

Well-known member
Joined
Mar 9, 2014
Messages
14,474
Location
East Bay SFO
I’m afraid that unless you get that mouse problem under control quickly, you’ll have more and more problems.

Not to mention the careless people who nailed on the sheathing.
 

Attachments

  • 45094AAF-E422-4CED-B04D-CEC1578279D3.jpeg
    45094AAF-E422-4CED-B04D-CEC1578279D3.jpeg
    105.2 KB · Views: 67
OP
B

Bunchgrass

Well-known member
Joined
Dec 8, 2013
Messages
236
Location
North Idaho
Yep -- give a monkey a nail gun and see what you get.

Probably going to use a j-box to connect the other good end of this run to new wire going i to replace this mess. Then foam with steel wool in the hole.
 

Shiftless

Well-known member
Joined
Mar 9, 2014
Messages
14,474
Location
East Bay SFO
Yep -- give a monkey a nail gun and see what you get.

Probably going to use a j-box to connect the other good end of this run to new wire going i to replace this mess. Then foam with steel wool in the hole.

Rats are quite damaging. I have fought them in my house. One of them chewed through half inch Sheetrock. Another attacked a 36 pack of water bottles and apparently got an adequate water supply to continue his carnage.
I used the steel wool/expanding foam to seal entry cracks in our 70 year old house crawl space. Sheet metal glued onto holes with Liquid Nails or PL Premium works very well.
I set a couple of electronic rat zapper traps baited with dry dog food.
It’s a war. You have to go to battle.
 
Last edited:

MatBirch

Well-known member
Joined
Oct 10, 2013
Messages
419
Location
Filer, Idaho
Ouch, looks like you've got a bit of a mouse problem. I don't know why they like wires so much.

Don’t know about new house wire, but with automotive stuff, many newer wire insulation’s are made with soy. Rodents love a free snack!
 

Milton Shaw

Well-known member
Joined
Feb 11, 2011
Messages
4,835
From what I understand the soy insulation is so good tasting to termites that that is what is used in the bait stations for determining termite infestations. This was first discovered by electricians finding underground wire completely stripped of insulation by the termites. A friend who is an exterminator told me this.
 
OP
B

Bunchgrass

Well-known member
Joined
Dec 8, 2013
Messages
236
Location
North Idaho
We have a car wandering around. She wanders back and forth to the food bowl and only snags a mouse when they've reached epidemic levels.

CAT not car.:lol_hitti
 
Last edited:
To avoid these ads, REGISTER NOW!
Top Bottom