Lighting plan for 28x28....opinions?

69charged

Well-known member
Joined
Sep 20, 2007
Messages
469
Location
carberry, manitoba
Good morning all. I am going to be wiring my unfinished garage as soon as I pass inspection on the panel. I also want to order my lights so they get here when i need them. I am going with the Hyperlite Hero series lights so I decided to get a lighting plan done by them to see what they say. They came back with 4- 150w lights 7' in from each corner for my 28' x 28' garage with 12.5' ceilings. I'm no expert by any means, but it doesn't seem enough does it? Originally I was just going to buy 9- 100w hero lights in a 5000k color, and put up 6 of them and have three spares. Then have all 6 on the same circuit and a 1-10v dimmer. So to go down to 4 seems like I would have hot spots in the middle and dark at the edges. I will use the garage for everything from detailing vehicles to dimming the lights and having people over for beers and bbq's . What are your thoughts?? lighting sim2.png

lighting sim1.png

lighting sim.png

I should add that the walls with be finished in painted drywall. Thinking something like a real light gray, or possibly white. The ceiling will be old barnboard. These lights will be wired with plugins so its easier to change one out if needed.

Thank you very much for your time with this.
Clarence
 
Last edited:
To avoid these ads, REGISTER NOW!

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
5,987
Location
NJ
Without knowing what obstacles will be part of the ultimate floor plan and where you would be detailing cars, I would suggest installing 3 rows of 3.
Definitely do the dimmer.

2x2 is enough for storage IMO.
 

Shiftless

Well-known member
Joined
Mar 9, 2014
Messages
14,553
Location
East Bay SFO
2x2 is enough for storage IMO.
That’s more than adequate for most uses.
Each one is good for 21,000 lumens.
Four of them will light up that 28x28 just fine. Too much glare for my personal taste but plenty of light. My little 20x20 is lit up with 9 twin tube four foot long LED fixtures. And some extra separately switched floodlights over one of the workbenches and aimed downward at the shelving on one wall. No dimmers.
 
Last edited:
OP
6

69charged

Well-known member
Joined
Sep 20, 2007
Messages
469
Location
carberry, manitoba
Thanks all. I had originally planned for 3 rows of 3 of the 100w lamps.
There are 2 8x9 overhead doors, and the cabinetry and work bench will be in an L shape along the west and north wall. So for reference that would be the left wall and top wall in the layout diagrams above. The 2 garage doors are on the bottom wall in the diagrams. I would pull a vehicle in one of the doors, and park it pretty much in the middle. Anything I work on would most often be pulled into the middle.
I had also thought on running the 3x3 on two circuits so I wouldn't HAVE to have them all on. The amount of money any extra wiring and switches would cost to do that are pretty minimal in the grand scheme of things. But, not sure I see a scenario where I would need that if I also install a dimmer. My son thinks I'm crazy to put a dimmer in and all these lights! But I painted him a picture of him and his buddies all sitting around havin a few beers till 1 in the morning with music blaring. No need for it to look like a surgery room with it dark outside and the big doors open. Set the mood and dim the lights!! He came around to my style of thinking!! :)
 

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,599
Location
BC
I have added lights to the walls, edges of built-in shelving, and under portions of mezzanine. Puts light closer to what I'm working on, and avoids a lot of shadows. I knew i would have to add this in addition to ceiling light, so i did it first, Lol. My ceiling is still not finished.
 
OP
6

69charged

Well-known member
Joined
Sep 20, 2007
Messages
469
Location
carberry, manitoba
Thinking about the glare part of this.....i did some quick reading on it. Definitely something to think about. Will it be a huge concern if my ceilings are that high? At work we have some new LED linear lights mounted on the walls. They have no diffuser or and shading or anything. You can see the bare LED chips. They are extremely annoying because they are just above head height. So no matter where you look they are always in your face. Mine will be 6-7 feet above your head. Thoughts???
 

cybrdyke

Well-known member
Joined
Sep 9, 2014
Messages
3,449
Location
USA
The diffuser is a good accessory because it helps a little with glare and also evens out your f-c min/max figures. Plus, they look nicer. Your light level with 4 fixtures is more than adequate. For reference, we shoot for 40fc in a school classroom. You're at 75, in theory, but you'll fall short of that by a bit because of obstacles, barnwood, etc. You can put all four on one dimmer for about $200 without running wire down the walls. Use a Lutron Vive Powpak and a Pico (or two).
Good luck,
CD
 

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,599
Location
BC
7' above your head is definitely NOT suitable for highbay fixtures. I'd be looking for single tube/strip lights with a good diffuser.
 
OP
6

69charged

Well-known member
Joined
Sep 20, 2007
Messages
469
Location
carberry, manitoba
7' above your head is definitely NOT suitable for highbay fixtures. I'd be looking for single tube/strip lights with a good diffuser.
I was under the impression anything about 12' and higher would be suitable? I'm at 12.5' so right at the threshold, hence why I thought about the 100w ones.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
5,987
Location
NJ
That’s more than adequate for most uses.
Each one is good for 21,000 lumens.
Four of them will light up that 28x28 just fine. Too much glare for my personal taste but plenty of light. My little 20x20 is lit up with 9 twin tube four foot long LED fixtures. And some extra separately switched floodlights over one of the workbenches and aimed downward at the shelving on one wall. No dimmers.
My point is more fixtures, each at a lower lumen output to lower the intensity of each point source and the glare it creates.

Personally, I prefer linear fixtures inside to smooth out the lighting level even further. I hate working in shadows. I would put more effort into the installation so my daily use from then on meets all my needs.

Detail work is a different need than just storage.
 
OP
6

69charged

Well-known member
Joined
Sep 20, 2007
Messages
469
Location
carberry, manitoba
So here is a 300w light I “borrowed” from work a couple weeks ago just to see what I was wanting and looking for. I will admit I was a little disappointed compared to what I thought it would look like. I know it’s only 1, and the shadowing was real bad, so that’s what kind of led me to think more than 4 100w ones. I think I’d like better coverage in all areas than what I “imagine” 4 will get me.


IMG_3122.jpeg
It’s like 42,000 lumens or something crazy.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
5,987
Location
NJ
If I found the same fixture family on Amazon, only the 150w version has a diffuser. The others are open LEDs. I would stay away from non-diffused versions.

The specs state 12-16' mounting height. You're just within that range.

The specs also indicate "Control Method: Remote" Not sure that implies 0-10v control. It could simply mean turn off the circuit "elseware" as in via switch or cb. If fixtures are dimmable it is usually a clearly stated feature. Where did you find any mention or 0-10v control?
 
OP
6

69charged

Well-known member
Joined
Sep 20, 2007
Messages
469
Location
carberry, manitoba
The picture I posted with the diffuser was taken from Amazon. They sell the diffuser separately so that does add to the cost. Currently it shows the diffusers are out of stock, but they can be bought later and added on real easy it looks like.

This screen shot is from their website.


IMG_3238.png
I would end up running a 1-10v separate control wire. It is easier to just use a dimmer without to control the dimming, but if ever I change fixtures for whatever reason, I want that wire there so I’m never limited on what I can install. As I said earlier these will be plugged in so can be swapped out easy if needed.

Thanks all for the help so far. I appreciate the discussion and learning that comes from back and forth!
Clarence
 

Criss

ALLIANCE MEMBER
Joined
Apr 21, 2012
Messages
262
Location
Western PA
I see hyperlite has an available 60 degree frosted diffuser available for those hero lights. Could that be an option to help glare?


IMG_3237.png
I have that 150w with diffuser light that I use as an additional overhead work light in one garage bay. I mounted this Hyperlite on a trolley that runs in a strut/track along the garage door opener track. This allows me to slide it overhead where I need it. It's 9'-1/2" from the floor. I have 63, 6" (120W equivalent)5000k led flush can lights in my 30X60 and I still never seem to have the light where I need it. I run mine on three separate dimmer switches. I usually need more light not less.
 

Shiftless

Well-known member
Joined
Mar 9, 2014
Messages
14,553
Location
East Bay SFO
I have 63, 6" (120W equivalent)5000k led flush can lights in my 30X60 and I still never seem to have the light where I need it.
I bet that took a lot of time to wire up 63 fixtures. Sorry it’s still disappointing.
I assume each fixture is good for what…1500 lumens?
63 x 1500 = close to 100,000 lumens
I guess that’s not enough. Plus, those low lumen flush lights probably have too wide a beam spread so the light bounces around off the walls which might not be very reflective. Not the greatest for high ceilings.
 
Last edited:

cybrdyke

Well-known member
Joined
Sep 9, 2014
Messages
3,449
Location
USA
That spec sheet indicates 1-10V dimming. This is not the same as 0-10V dimming, which is the industry standard. That would be a deal breaker for me because most controls, like Lutron (the most common), operate a 0-10 protocol and wont work properly with a 1-10V driver. Really dumb of this manufacturer to use a 1-10V driver.
CD
 
To avoid these ads, REGISTER NOW!
OP
6

69charged

Well-known member
Joined
Sep 20, 2007
Messages
469
Location
carberry, manitoba
That spec sheet indicates 1-10V dimming. This is not the same as 0-10V dimming, which is the industry standard. That would be a deal breaker for me because most controls, like Lutron (the most common), operate a 0-10 protocol and wont work properly with a 1-10V driver. Really dumb of this manufacturer to use a 1-10V driver.
CD
I started reading up on the difference. Had no idea. They offer their own dimmer on the site. I could just order one with the lights I guess. I was hoping to use the Lutron Casetta series switches. I've used them in the past and really like the mobility of them.
Looking online, it is kind of hard to find a 1-10v dimmer.
 

cybrdyke

Well-known member
Joined
Sep 9, 2014
Messages
3,449
Location
USA
I started reading up on the difference. Had no idea. They offer their own dimmer on the site. I could just order one with the lights I guess. I was hoping to use the Lutron Casetta series switches. I've used them in the past and really like the mobility of them.
Looking online, it is kind of hard to find a 1-10v dimmer.
Easier to find a similar UFO that's 0-10V. There's millions of them out there....
CD
 

billconner

Well-known member
Joined
Jul 20, 2021
Messages
6,970
Location
Thousand Islands NYS
That spec sheet indicates 1-10V dimming. This is not the same as 0-10V dimming, which is the industry standard. That would be a deal breaker for me because most controls, like Lutron (the most common), operate a 0-10 protocol and wont work properly with a 1-10V driver. Really dumb of this manufacturer to use a 1-10V driver.
CD
Are you sure? This from manual. Seems like it does both. "The main difference between 0-10V and 1-10V is the direction of the current between dimmer and driver. 0-10V is a current source system, which means that the dimmer provides the power for the 0-10V signals – a mains connection to the dimmer is necessary. 1-10V is a current sink system."
Screenshot_20240418-142341.png
 

Criss

ALLIANCE MEMBER
Joined
Apr 21, 2012
Messages
262
Location
Western PA
I bet that took a lot of time to wire up 63 fixtures. Sorry it’s still disappointing.
I assume each fixture is good for what…1500 lumens?
63 x 1500 = close to 100,000 lumens
I guess that’s not enough. Plus, those low lumen flush lights probably have too wide a beam spread so the light bounces around off the walls which might not be very reflective. Not the greatest for high ceilings.
Only 1050 lumen per fixture. Ceiling is 9'-1/2" 110° beam. I decided to order 4 more High bay that I will put on 9' tripods and use them as auxiliary work lights. Cans lights look fancy, but aren't practical.
 
OP
6

69charged

Well-known member
Joined
Sep 20, 2007
Messages
469
Location
carberry, manitoba
So say I decide to go with something else. I like the look of a 2x4 flat panel light, I think. They go all the way down to 30w up to 72w. What would the layout pattern look like then? They are pretty big. As in they take up ceiling real estate. It wouldn't really matter, but it really wasn't the look I was going for. Not sure how they would look with a barn board ceiling. I see there are surface mount kits for them as well.
Would it be better to run these at full brightness all the time I'm in there or have the UFO's and have them dimmed down? Life expectancy wise. Or, am I overthinking everything? Which I tend to do!! :D
 

cybrdyke

Well-known member
Joined
Sep 9, 2014
Messages
3,449
Location
USA
Are you sure? This from manual. Seems like it does both. "The main difference between 0-10V and 1-10V is the direction of the current between dimmer and driver. 0-10V is a current source system, which means that the dimmer provides the power for the 0-10V signals – a mains connection to the dimmer is necessary. 1-10V is a current sink system."
Here's what I'm sure of...
  • 0-10 and 1-10 systems are different and there will be issues if you try to dim a 1-10 driver with a 0-10 control.
  • The spec sheet says the driver is 1-10.
  • The comments above in red are incorrect. The dimmer doesn't provide power for the 0-10 signals. The driver does.
  • The Chinglish attempt at trying to explain a wiring diagram makes it even more complicated and confusing.
Now, back in the day, in entertainment lighting, there were products that used the control to provide the 0-10V signal. Maybe that's where you got this info. But that was a while ago. For general illumination, the driver creates the control signal. Always has.
1-10V systems can only dim to 10%. 0-10V systems can dim lower, sometimes to OFF (this can be a point of contention, too). But the dimming curves are different and thus the misbehavior can begin when you try to mix and match these systems.
As technology advances, this will start to become less of an issue. Consensus has already chosen 0-10 as the protocol.
CD
 

billconner

Well-known member
Joined
Jul 20, 2021
Messages
6,970
Location
Thousand Islands NYS
Here's what I'm sure of...
  • 0-10 and 1-10 systems are different and there will be issues if you try to dim a 1-10 driver with a 0-10 control.
  • The spec sheet says the driver is 1-10.
  • The comments above in red are incorrect. The dimmer doesn't provide power for the 0-10 signals. The driver does.
  • The Chinglish attempt at trying to explain a wiring diagram makes it even more complicated and confusing.
Now, back in the day, in entertainment lighting, there were products that used the control to provide the 0-10V signal. Maybe that's where you got this info. But that was a while ago. For general illumination, the driver creates the control signal. Always has.
1-10V systems can only dim to 10%. 0-10V systems can dim lower, sometimes to OFF (this can be a point of contention, too). But the dimming curves are different and thus the misbehavior can begin when you try to mix and match these systems.
As technology advances, this will start to become less of an issue. Consensus has already chosen 0-10 as the protocol.
CD
So you're saying the fixture installation sheet is not possible? No one could design a driver to work on both 0-10 sinking current and a 0-10 vdc supply?

Pretty thorough article on 0-10 sinking current *******.
 

Attachments

  • 0-10VLEDDrivers_WhitePaper_revC.pdf
    261 KB · Views: 2

cybrdyke

Well-known member
Joined
Sep 9, 2014
Messages
3,449
Location
USA
So you're saying the fixture installation sheet is not possible? No one could design a driver to work on both 0-10 sinking current and a 1-10 vdc supply?

Pretty thorough article on 0-10 sinking current *******.
The spec sheet is likely wrong, but who am I to say for sure? The installation instructions are ridiculous to read. Its anyone's guess what they're trying to say.
I'm not sure I understand your second question. Did you mean to say 1-10VDC supply? I know of drivers that work on multiple dimming protocols. They work on both line voltage dimming, low voltage dimming (0-10) and even DALI. But I dont know of one that does both 0-10 and 1-10. Sure, someone could invent that. Wouldn't surprise me if someone already has. But I dont see any benefit to it. Like I said earlier, the consensus has made 0-10 the standard protocol, so why spend R&D money on a dinosaur. Plus, it would be expensive. Besides, if someone did make such a thing, it wouldn't be a no-name internet gutter-dweller like Hyperlite.
CD
 
OP
6

69charged

Well-known member
Joined
Sep 20, 2007
Messages
469
Location
carberry, manitoba
So….if they are like a interwebs dumpster fire type light, what brand should I be looking at? I say that with genuine intentions. There is just so much to sift through. I have bought from superbrightleds before as well, but suspect that’s in the same boat as these?
Not looking to spend 300 per fixture either.
Honestly my original plan was to put up 9 of these. But buy 12 or so to have 3 spares in case they failed. But…..now what?
 

cybrdyke

Well-known member
Joined
Sep 9, 2014
Messages
3,449
Location
USA
69- I didn't mean to dissuade you from using them. I'm sure they're fine. Please understand that there's a difference between DIY garage lighting and professional stuff that old stuck-up lighting nerds like me will use. My comment simply means that these generic fixtures are built and engineered to a price point, and then the internet seller also has very little stake in the process. He simply handles the order with no liability. Those things combined make for a low-end product with no discernable features. (It also allows for the Chinglish instructions. You would think that someone would at least take a minute to clean those up).
The pro brands do cost more. We know who's drivers are in there, who's diode arrays are being used, who's casting, etc. The product claims are verified, tested and documented. There is a giant difference in performance and life.
There are mid-range brands that are legitimate. RAB, Eiko, Keystone, ETI and more are actual manufacturers that you should be able to find from the internet sellers. Try Green Lighting Wholesale. They carry good stuff.
CD
 
  • Like
Reactions: Max
OP
6

69charged

Well-known member
Joined
Sep 20, 2007
Messages
469
Location
carberry, manitoba
69- I didn't mean to dissuade you from using them. I'm sure they're fine. Please understand that there's a difference between DIY garage lighting and professional stuff that old stuck-up lighting nerds like me will use. My comment simply means that these generic fixtures are built and engineered to a price point, and then the internet seller also has very little stake in the process. He simply handles the order with no liability. Those things combined make for a low-end product with no discernable features. (It also allows for the Chinglish instructions. You would think that someone would at least take a minute to clean those up).
The pro brands do cost more. We know who's drivers are in there, who's diode arrays are being used, who's casting, etc. The product claims are verified, tested and documented. There is a giant difference in performance and life.
There are mid-range brands that are legitimate. RAB, Eiko, Keystone, ETI and more are actual manufacturers that you should be able to find from the internet sellers. Try Green Lighting Wholesale. They carry good stuff.
CD
Ok. Thanks. I will look into those brands. I recognize the RAB name as I have a few of those lights for my yard site. The electrical contractor my son works for sells those. 👍
 

dave*99

Well-known member
Joined
May 5, 2009
Messages
4,269
Location
Coastal NJ
So say I decide to go with something else. I like the look of a 2x4 flat panel light, I think. They go all the way down to 30w up to 72w. What would the layout pattern look like then? They are pretty big. As in they take up ceiling real estate. It wouldn't really matter, but it really wasn't the look I was going for. Not sure how they would look with a barn board ceiling. I see there are surface mount kits for them as well.
Would it be better to run these at full brightness all the time I'm in there or have the UFO's and have them dimmed down? Life expectancy wise. Or, am I overthinking everything? Which I tend to do!! :D
Considering 2x4? Perhaps my journey will provide some insight.

 

4x4Pete

Well-known member
Joined
Aug 26, 2019
Messages
791
Location
Stroud
In my 30'x32'x 12.5', I used 12 4' led units. 4400 lumens I think, it's been a few years. It's bright enough and the light is even with no glare. I didn't do a calculation, I just guesstimated it. For the layout I made 3 rows of 4 lights evenly spaced and set them on two switches, front and back. For the work bench I put a switched plug mounted high with a similar plug in type fixture hanging above the bench. Here is a pic during construction.
20200409_164934.jpg
 
OP
6

69charged

Well-known member
Joined
Sep 20, 2007
Messages
469
Location
carberry, manitoba
Considering 2x4? Perhaps my journey will provide some insight.

Thanks. So after having them
Considering 2x4? Perhaps my journey will provide some insight.

Thanks.
So after having them all this time, how have they been? I had looked at doing a 2x4 panel in my old garage with 9’ ceilings. I thought I should look for something brighter for 12.5’ ceilings. But I do like how smooth they are. Smooth as in not hot spots and easier to look at.
How were they mounted in your particular install, and how far down do they sit?
 

BLUE72CAMARO

Well-known member
Joined
Jan 1, 2014
Messages
911
Location
IL
Here is my install of 150W hero series lights in 36x48 area of my back pole barn.

These are the switches I used on mine and they work perfectly.
 
Last edited:
OP
6

69charged

Well-known member
Joined
Sep 20, 2007
Messages
469
Location
carberry, manitoba
Here is my install of 150W hero series lights in 36x48 area of my back pole barn.

These are the switches I used on mine and they work perfectly.
Nice. Thank you for that. Pretty much what I had in mind. I think I will order one 100w light and see what I think. Its free shipping in Canada, so if I end up not using them, I'll put it under my eaves or something.
 

dave*99

Well-known member
Joined
May 5, 2009
Messages
4,269
Location
Coastal NJ
Thanks. So after having them

Thanks.
So after having them all this time, how have they been? I had looked at doing a 2x4 panel in my old garage with 9’ ceilings. I thought I should look for something brighter for 12.5’ ceilings. But I do like how smooth they are. Smooth as in not hot spots and easier to look at.
How were they mounted in your particular install, and how far down do they sit?
They are perfect. No glare no shadows. And the design program correctly predicted the illumination level.

Consider this…. I have 64 sq ft of light surface area (the 2x4 panels times 8) on 700 sq ft of floor. I’m not sure if that is the perfect way to look at it.

You can also consider 3 tube 4 ft LED ready fixtures with frosted tubes for your application.
 
OP
6

69charged

Well-known member
Joined
Sep 20, 2007
Messages
469
Location
carberry, manitoba
They are perfect. No glare no shadows. And the design program correctly predicted the illumination level.

Consider this…. I have 64 sq ft of light surface area (the 2x4 panels times 8) on 700 sq ft of floor. I’m not sure if that is the perfect way to look at it.

You can also consider 3 tube 4 ft LED ready fixtures with frosted tubes for your application.
I would either go flat panel, or the UFO’s. The look I’m going for when it’s all done would suit the UFO’s better. Like a factory or warehouse type look.
 